Re: [EnergyPlus_Support] VRF Error



It means the VRF system turned off since the outdoor temperature is 
above 20C (the maximum OA temp that allows operation).

You can either increase the input for Heating Maximum Outdoor Dry-Bulb 
Temperature from 20C to 25C and assume the performance is unaffected by 
this change from manufacturers recommendations, or include a backup 
system to condition the zone when the VRF system is off.


On 2/28/2013 7:06 AM, zenithshahir wrote:
> Dear all
>   While modelling VRF system i am getting warning.
> VRF Heat Pump Min/Max Outdoor Temperature in Heating Mode Limits have been exceeded and VRF system is disabled.
> ... Outdoor Dry-Bulb Temperature                 = 24.362
> ... Heating Minimum Outdoor Dry-Bulb Temperature = -20.000
> ... Heating Maximum Outdoor Dry-Bulb Temperature = 20.000
> ... Check VRF Heat Pump Min/Max Outdoor Temperature in Heating Mode limits.
>   
> is this means VRF system is not working. can i ignore this warning
>   
>
>
>
>
> ------------------------------------
>
> Primary EnergyPlus support is found at:
> http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/