I modelled a house with comfort controlled thermostat and ideal air system. Results for heating demand seemed plausible at first. Yet, when I change the design flow rate from 0.5 air changes per hour to 1 air change per hour, I get an unexpectedly high differential.
I would have assumed something in the order of ventilated volume * ac/h *  specific heat capacity of air * degree hours, but my differences are nearly double what I'd expect from this approximation.
Does anyone have an idea how this magnitude of a difference comes about, or where I make a mistake in my model that leads to this outcome? All hints appreciated!

!-Generator IDFEditor 1.43
!-Option OriginalOrderTop UseSpecialFormat

!-NOTE: All comments with '!-' are ignored by the IDFEditor and are generated automatically.
!-      Use '!' comments if they need to be retained when using the IDFEditor.

ZoneVentilation:WindandStackOpenArea,
    InfilRoof,               !- Name
    Attic,                   !- Zone Name
    1,                       !- Opening Area {m2}
    AlwaysOn,                !- Opening Area Fraction Schedule Name
    1,                       !- Opening Effectiveness {dimensionless}
    ,                        !- Effective Angle {deg}
    0,                       !- Height Difference {m}
    autocalculate,           !- Discharge Coefficient for Opening
    -100,                    !- Minimum Indoor Temperature {C}
    AlwaysOn,                !- Minimum Indoor Temperature Schedule Name
    100,                     !- Maximum Indoor Temperature {C}
    ,                        !- Maximum Indoor Temperature Schedule Name
    -100,                    !- Delta Temperature {deltaC}
    ,                        !- Delta Temperature Schedule Name
    -100,                    !- Minimum Outdoor Temperature {C}
    ,                        !- Minimum Outdoor Temperature Schedule Name
    100,                     !- Maximum Outdoor Temperature {C}
    ,                        !- Maximum Outdoor Temperature Schedule Name
    40;                      !- Maximum Wind Speed {m/s}

Output:Variable,*,People Total Heat Gain ,Annual;
Output:Variable,*,People Total Heat Gain Rate ,Annual;

ElectricEquipment,
    IGains,                  !- Name
    AllControlledZones,      !- Zone or ZoneList Name
    AlwaysOn,                !- Schedule Name
    Watts/Area,              !- Design Level Calculation Method
    2.8,                     !- Design Level {W}
    ,                        !- Watts per Zone Floor Area {W/m2}
    ,                        !- Watts per Person {W/person}
    ,                        !- Fraction Latent
    ,                        !- Fraction Radiant
    ,                        !- Fraction Lost
    General;                 !- End-Use Subcategory

Schedule:Compact,
    AlwaysOn,                !- Name
    Fraction,                !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00, 1;         !- Field 4

Output:Variable,*,Ideal Loads Total Heating Energy ,Annual;
Output:Variable,*,Ideal Loads Total Cooling Energy ,Annual;

WindowProperty:FrameAndDivider,
    AluFrame,                !- Name
    0.06,                    !- Frame Width {m}
    0.06,                    !- Frame Outside Projection {m}
    0.06,                    !- Frame Inside Projection {m}
    5.86,                    !- Frame Conductance {W/m2-K}
    1,                       !- Ratio of Frame-Edge Glass Conductance to Center-Of-Glass Conductance
    0.9,                     !- Frame Solar Absorptance
    0.7,                     !- Frame Visible Absorptance
    0.2,                     !- Frame Thermal Hemispherical Emissivity
    DividedLite,             !- Divider Type
    ,                        !- Divider Width {m}
    ,                        !- Number of Horizontal Dividers
    ,                        !- Number of Vertical Dividers
    ,                        !- Divider Outside Projection {m}
    ,                        !- Divider Inside Projection {m}
    ,                        !- Divider Conductance {W/m2-K}
    1,                       !- Ratio of Divider-Edge Glass Conductance to Center-Of-Glass Conductance
    ,                        !- Divider Solar Absorptance
    ,                        !- Divider Visible Absorptance
    0.9;                     !- Divider Thermal Hemispherical Emissivity

BuildingSurface:Detailed,
    RoofW1,                  !- Name
    Roof,                    !- Surface Type
    Exterior Roof,           !- Construction Name
    Attic,                   !- Zone Name
    Outdoors,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    ,                        !- View Factor to Ground
    3,                       !- Number of Vertices
    11.050000000000, 6.6, 3.500000000000,
                                        !- X,Y,Z  1 {m}
    7.6, 6.6, 2.4,                      !- X,Y,Z  2 {m}
    11.05, 3.3, 3.5;                    !- X,Y,Z  3 {m}

BuildingSurface:Detailed,
    RoofW,                   !- Name
    Roof,                    !- Surface Type
    Exterior Roof,           !- Construction Name
    Attic,                   !- Zone Name
    Outdoors,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    ,                        !- View Factor to Ground
    4,                       !- Number of Vertices
    11.050000000000, 7.800000000000, 3.500000000000,
                                        !- X,Y,Z  1 {m}
    10.900000000000, 7.800000000000, 3.452173913043,
                                        !- X,Y,Z  2 {m}
    10.900000000000, 6.600000000000, 3.452173913043,
                                        !- X,Y,Z  3 {m}
    11.05, 6.600000000000, 3.5;         !- X,Y,Z  4 {m}

People,
    PeopleElse,              !- Name
    ElseZone,                !- Zone or ZoneList Name
    Else occ,                !- Number of People Schedule Name
    People,                  !- Number of People Calculation Method
    1,                       !- Number of People
    ,                        !- People per Zone Floor Area {person/m2}
    ,                        !- Zone Floor Area per Person {m2/person}
    0.3,                     !- Fraction Radiant
    autocalculate,           !- Sensible Heat Fraction
    Activity Sch,            !- Activity Level Schedule Name
    0.0000000382,            !- Carbon Dioxide Generation Rate {m3/s-W}
    ,                        !- Enable ASHRAE 55 Comfort Warnings
    ZoneAveraged,            !- Mean Radiant Temperature Calculation Type
    ,                        !- Surface Name/Angle Factor List Name
    Work Eff Sch,            !- Work Efficiency Schedule Name
    Clothing Sch,            !- Clothing Insulation Schedule Name
    Air Velo Sch,            !- Air Velocity Schedule Name
    Fanger;                  !- Thermal Comfort Model 1 Type

ZoneList,
    ElseZone,                !- Name
    Z3ENT,                   !- Zone 1 Name
    Z9COR;                   !- Zone 2 Name

Schedule:Compact,
    Else occ,                !- Name
    Fraction,                !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 07:00, 0,         !- Field 4
    Until: 21:00, .01,       !- Field 6
    Until: 24:00, 0;         !- Field 8

ZoneControl:Thermostat:ThermalComfort,
    AllButLivTC,             !- Name
    AllButLIV,               !- Zone or ZoneList Name
    PeopleAverage,           !- Averaging Method
    ,                        !- Specific People Name
    0,                       !- Minimum Dry-Bulb Temperature Setpoint {C}
    50,                      !- Maximum Dry-Bulb Temperature Setpoint {C}
    ZONE CONTROL TYPE SCHEDULE,  !- Thermal Comfort Control Type Schedule Name
    ThermostatSetpoint:ThermalComfort:Fanger:DualSetpoint,  !- Thermal Comfort Control 1 Object Type
    AllButLIV DUAL COMFORT SETPOINTS;  !- Thermal Comfort Control 1 Name

ZoneControl:Thermostat:ThermalComfort,
    Z1_LIVTC,                !- Name
    Z1LIV,                   !- Zone or ZoneList Name
    ObjectAverage,           !- Averaging Method
    ,                        !- Specific People Name
    0,                       !- Minimum Dry-Bulb Temperature Setpoint {C}
    50,                      !- Maximum Dry-Bulb Temperature Setpoint {C}
    ZONE CONTROL TYPE SCHEDULE,  !- Thermal Comfort Control Type Schedule Name
    ThermostatSetpoint:ThermalComfort:Fanger:DualSetpoint,  !- Thermal Comfort Control 1 Object Type
    Z1_LIV DUAL COMFORT SETPOINTS;  !- Thermal Comfort Control 1 Name

RunPeriod,
    Year,                    !- Name
    1,                       !- Begin Month
    1,                       !- Begin Day of Month
    12,                      !- End Month
    31,                      !- End Day of Month
    UseWeatherFile,          !- Day of Week for Start Day
    Yes,                     !- Use Weather File Holidays and Special Days
    Yes,                     !- Use Weather File Daylight Saving Period
    No,                      !- Apply Weekend Holiday Rule
    Yes,                     !- Use Weather File Rain Indicators
    Yes;                     !- Use Weather File Snow Indicators

GroundHeatTransfer:Slab:Materials,
    2,                       !- NMAT: Number of materials
    0.158,                   !- ALBEDO: Surface Albedo: No Snow
    0.379,                   !- ALBEDO: Surface Albedo: Snow
    0.9,                     !- EPSLW: Surface Emissivity: No Snow
    0.9,                     !- EPSLW: Surface Emissivity: Snow
    0.75,                    !- Z0: Surface Roughness: No Snow {cm}
    0.03,                    !- Z0: Surface Roughness: Snow {cm}
    6.13,                    !- HIN: Indoor HConv: Downward Flow {W/m2-K}
    9.26;                    !- HIN: Indoor HConv: Upward {W/m2-K}

GroundHeatTransfer:Slab:MatlProps,
    2300,                    !- RHO: Slab Material density {kg/m3}
    1200,                    !- RHO: Soil Density {kg/m3}
    653,                     !- CP: Slab CP {J/kg-K}
    1200,                    !- CP: Soil CP {J/kg-K}
    0.93,                    !- TCON: Slab k {W/m-K}
    1;                       !- TCON: Soil k {W/m-K}

GroundHeatTransfer:Slab:BoundConds,
    TRUE,                    !- EVTR: Is surface evapotranspiration modeled
    TRUE,                    !- FIXBC: is the lower boundary at a fixed temperature
    10,                      !- TDEEPin {C}
    FALSE;                   !- USRHflag: Is the ground surface h specified by the user?

GroundHeatTransfer:Slab:BldgProps,
    5,                       !- IYRS: Number of years to iterate
    0,                       !- Shape: Slab shape
    4,                       !- HBLDG: Building height {m}
    22,                      !- TIN1: January Indoor Average Temperature Setpoint {C}
    22,                      !- TIN2: February Indoor Average Temperature Setpoint {C}
    22,                      !- TIN3: March Indoor Average Temperature Setpoint {C}
    18,                      !- TIN4: April Indoor Average Temperature Setpoint {C}
    18,                      !- TIN5: May Indoor Average Temperature Setpoint {C}
    18,                      !- TIN6: June Indoor Average Temperature Setpoint {C}
    18,                      !- TIN7: July Indoor Average Temperature Setpoint {C}
    18,                      !- TIN8: August Indoor Average Temperature Setpoint {C}
    18,                      !- TIN9: September Indoor Average Temperature Setpoint {C}
    18,                      !- TIN10: October Indoor Average Temperature Setpoint {C}
    20,                      !- TIN11: November Indoor Average Temperature Setpoint {C}
    22,                      !- TIN12: December Indoor Average Temperature Setpoint {C}
    0,                       !- TINAmp: Daily Indoor sine wave variation amplitude {deltaC}
    0.10;                    !- ConvTol: Convergence Tolerance

GroundHeatTransfer:Slab:Insulation,
    0.526315789,             !- RINS: R value of under slab insulation {m2-K/W}
    0.6,                     !- DINS: Width of strip of under slab insulation {m}
    0,                       !- RVINS: R value of vertical insulation {m2-K/W}
    0,                       !- ZVINS: Depth of vertical insulation {m}
    0;                       !- IVINS: Flag: Is there vertical insulation

GroundHeatTransfer:Slab:EquivalentSlab,
    2.08,                    !- APRatio: The area to perimeter ratio for this slab {m}
    0.13,                    !- SLABDEPTH: Thickness of slab on grade {m}
    15.,                     !- CLEARANCE: Distance from edge of slab to domain edge {m}
    15.;                     !- ZCLEARANCE: Distance from bottom of slab to domain bottom {m}

Version,7.2;

ZoneHVAC:IdealLoadsAirSystem,
    Z5_BAT Ideal Loads,      !- Name
    ,                        !- Availability Schedule Name
    Z5 Supply Inlets,        !- Zone Supply Air Node Name
    ,                        !- Zone Exhaust Air Node Name
    50,                      !- Maximum Heating Supply Air Temperature {C}
    13,                      !- Minimum Cooling Supply Air Temperature {C}
    0.015,                   !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir}
    0.01,                    !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir}
    NoLimit,                 !- Heating Limit
    autosize,                !- Maximum Heating Air Flow Rate {m3/s}
    ,                        !- Maximum Sensible Heating Capacity {W}
    NoLimit,                 !- Cooling Limit
    autosize,                !- Maximum Cooling Air Flow Rate {m3/s}
    ,                        !- Maximum Total Cooling Capacity {W}
    ,                        !- Heating Availability Schedule Name
    ,                        !- Cooling Availability Schedule Name
    ConstantSupplyHumidityRatio,  !- Dehumidification Control Type
    ,                        !- Cooling Sensible Heat Ratio {dimensionless}
    ConstantSupplyHumidityRatio,  !- Humidification Control Type
    ,                        !- Design Specification Outdoor Air Object Name
    ,                        !- Outdoor Air Inlet Node Name
    ,                        !- Demand Controlled Ventilation Type
    ,                        !- Outdoor Air Economizer Type
    ,                        !- Heat Recovery Type
    ,                        !- Sensible Heat Recovery Effectiveness {dimensionless}
    ;                        !- Latent Heat Recovery Effectiveness {dimensionless}

ZoneHVAC:IdealLoadsAirSystem,
    Z6_BSW Ideal Loads,      !- Name
    ,                        !- Availability Schedule Name
    Z6 Supply Inlets,        !- Zone Supply Air Node Name
    ,                        !- Zone Exhaust Air Node Name
    50,                      !- Maximum Heating Supply Air Temperature {C}
    13,                      !- Minimum Cooling Supply Air Temperature {C}
    0.015,                   !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir}
    0.01,                    !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir}
    NoLimit,                 !- Heating Limit
    autosize,                !- Maximum Heating Air Flow Rate {m3/s}
    ,                        !- Maximum Sensible Heating Capacity {W}
    NoLimit,                 !- Cooling Limit
    autosize,                !- Maximum Cooling Air Flow Rate {m3/s}
    ,                        !- Maximum Total Cooling Capacity {W}
    ,                        !- Heating Availability Schedule Name
    ,                        !- Cooling Availability Schedule Name
    ConstantSupplyHumidityRatio,  !- Dehumidification Control Type
    ,                        !- Cooling Sensible Heat Ratio {dimensionless}
    ConstantSupplyHumidityRatio,  !- Humidification Control Type
    ,                        !- Design Specification Outdoor Air Object Name
    ,                        !- Outdoor Air Inlet Node Name
    ,                        !- Demand Controlled Ventilation Type
    ,                        !- Outdoor Air Economizer Type
    ,                        !- Heat Recovery Type
    ,                        !- Sensible Heat Recovery Effectiveness {dimensionless}
    ;                        !- Latent Heat Recovery Effectiveness {dimensionless}

ZoneHVAC:IdealLoadsAirSystem,
    Z7_BNW Ideal Loads,      !- Name
    ,                        !- Availability Schedule Name
    Z7 Supply Inlets,        !- Zone Supply Air Node Name
    ,                        !- Zone Exhaust Air Node Name
    50,                      !- Maximum Heating Supply Air Temperature {C}
    13,                      !- Minimum Cooling Supply Air Temperature {C}
    0.015,                   !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir}
    0.01,                    !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir}
    NoLimit,                 !- Heating Limit
    autosize,                !- Maximum Heating Air Flow Rate {m3/s}
    ,                        !- Maximum Sensible Heating Capacity {W}
    NoLimit,                 !- Cooling Limit
    autosize,                !- Maximum Cooling Air Flow Rate {m3/s}
    ,                        !- Maximum Total Cooling Capacity {W}
    ,                        !- Heating Availability Schedule Name
    ,                        !- Cooling Availability Schedule Name
    ConstantSupplyHumidityRatio,  !- Dehumidification Control Type
    ,                        !- Cooling Sensible Heat Ratio {dimensionless}
    ConstantSupplyHumidityRatio,  !- Humidification Control Type
    ,                        !- Design Specification Outdoor Air Object Name
    ,                        !- Outdoor Air Inlet Node Name
    ,                        !- Demand Controlled Ventilation Type
    ,                        !- Outdoor Air Economizer Type
    ,                        !- Heat Recovery Type
    ,                        !- Sensible Heat Recovery Effectiveness {dimensionless}
    ;                        !- Latent Heat Recovery Effectiveness {dimensionless}

ZoneHVAC:IdealLoadsAirSystem,
    Z8_BN Ideal Loads,       !- Name
    ,                        !- Availability Schedule Name
    Z8 Supply Inlets,        !- Zone Supply Air Node Name
    ,                        !- Zone Exhaust Air Node Name
    50,                      !- Maximum Heating Supply Air Temperature {C}
    13,                      !- Minimum Cooling Supply Air Temperature {C}
    0.015,                   !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir}
    0.01,                    !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir}
    NoLimit,                 !- Heating Limit
    autosize,                !- Maximum Heating Air Flow Rate {m3/s}
    ,                        !- Maximum Sensible Heating Capacity {W}
    NoLimit,                 !- Cooling Limit
    autosize,                !- Maximum Cooling Air Flow Rate {m3/s}
    ,                        !- Maximum Total Cooling Capacity {W}
    ,                        !- Heating Availability Schedule Name
    ,                        !- Cooling Availability Schedule Name
    ConstantSupplyHumidityRatio,  !- Dehumidification Control Type
    ,                        !- Cooling Sensible Heat Ratio {dimensionless}
    ConstantSupplyHumidityRatio,  !- Humidification Control Type
    ,                        !- Design Specification Outdoor Air Object Name
    ,                        !- Outdoor Air Inlet Node Name
    ,                        !- Demand Controlled Ventilation Type
    ,                        !- Outdoor Air Economizer Type
    ,                        !- Heat Recovery Type
    ,                        !- Sensible Heat Recovery Effectiveness {dimensionless}
    ;                        !- Latent Heat Recovery Effectiveness {dimensionless}

ZoneHVAC:IdealLoadsAirSystem,
    Z9_COR Ideal Loads,      !- Name
    ,                        !- Availability Schedule Name
    Z9 Supply Inlets,        !- Zone Supply Air Node Name
    ,                        !- Zone Exhaust Air Node Name
    50,                      !- Maximum Heating Supply Air Temperature {C}
    13,                      !- Minimum Cooling Supply Air Temperature {C}
    0.015,                   !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir}
    0.01,                    !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir}
    NoLimit,                 !- Heating Limit
    autosize,                !- Maximum Heating Air Flow Rate {m3/s}
    ,                        !- Maximum Sensible Heating Capacity {W}
    NoLimit,                 !- Cooling Limit
    autosize,                !- Maximum Cooling Air Flow Rate {m3/s}
    ,                        !- Maximum Total Cooling Capacity {W}
    ,                        !- Heating Availability Schedule Name
    ,                        !- Cooling Availability Schedule Name
    ConstantSupplyHumidityRatio,  !- Dehumidification Control Type
    ,                        !- Cooling Sensible Heat Ratio {dimensionless}
    ConstantSupplyHumidityRatio,  !- Humidification Control Type
    ,                        !- Design Specification Outdoor Air Object Name
    ,                        !- Outdoor Air Inlet Node Name
    ,                        !- Demand Controlled Ventilation Type
    ,                        !- Outdoor Air Economizer Type
    ,                        !- Heat Recovery Type
    ,                        !- Sensible Heat Recovery Effectiveness {dimensionless}
    ;                        !- Latent Heat Recovery Effectiveness {dimensionless}

ZoneHVAC:IdealLoadsAirSystem,
    Z2_KIT Ideal Loads,      !- Name
    ,                        !- Availability Schedule Name
    Z2 Supply Inlets,        !- Zone Supply Air Node Name
    ,                        !- Zone Exhaust Air Node Name
    50,                      !- Maximum Heating Supply Air Temperature {C}
    13,                      !- Minimum Cooling Supply Air Temperature {C}
    0.015,                   !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir}
    0.01,                    !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir}
    NoLimit,                 !- Heating Limit
    autosize,                !- Maximum Heating Air Flow Rate {m3/s}
    ,                        !- Maximum Sensible Heating Capacity {W}
    NoLimit,                 !- Cooling Limit
    autosize,                !- Maximum Cooling Air Flow Rate {m3/s}
    ,                        !- Maximum Total Cooling Capacity {W}
    ,                        !- Heating Availability Schedule Name
    ,                        !- Cooling Availability Schedule Name
    ConstantSupplyHumidityRatio,  !- Dehumidification Control Type
    ,                        !- Cooling Sensible Heat Ratio {dimensionless}
    ConstantSupplyHumidityRatio,  !- Humidification Control Type
    ,                        !- Design Specification Outdoor Air Object Name
    ,                        !- Outdoor Air Inlet Node Name
    ,                        !- Demand Controlled Ventilation Type
    ,                        !- Outdoor Air Economizer Type
    ,                        !- Heat Recovery Type
    ,                        !- Sensible Heat Recovery Effectiveness {dimensionless}
    ;                        !- Latent Heat Recovery Effectiveness {dimensionless}

ZoneHVAC:IdealLoadsAirSystem,
    Z3_ENT Ideal Loads,      !- Name
    ,                        !- Availability Schedule Name
    Z3 Supply Inlets,        !- Zone Supply Air Node Name
    ,                        !- Zone Exhaust Air Node Name
    50,                      !- Maximum Heating Supply Air Temperature {C}
    13,                      !- Minimum Cooling Supply Air Temperature {C}
    0.015,                   !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir}
    0.01,                    !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir}
    NoLimit,                 !- Heating Limit
    autosize,                !- Maximum Heating Air Flow Rate {m3/s}
    ,                        !- Maximum Sensible Heating Capacity {W}
    NoLimit,                 !- Cooling Limit
    autosize,                !- Maximum Cooling Air Flow Rate {m3/s}
    ,                        !- Maximum Total Cooling Capacity {W}
    ,                        !- Heating Availability Schedule Name
    ,                        !- Cooling Availability Schedule Name
    ConstantSupplyHumidityRatio,  !- Dehumidification Control Type
    ,                        !- Cooling Sensible Heat Ratio {dimensionless}
    ConstantSupplyHumidityRatio,  !- Humidification Control Type
    ,                        !- Design Specification Outdoor Air Object Name
    ,                        !- Outdoor Air Inlet Node Name
    ,                        !- Demand Controlled Ventilation Type
    ,                        !- Outdoor Air Economizer Type
    ,                        !- Heat Recovery Type
    ,                        !- Sensible Heat Recovery Effectiveness {dimensionless}
    ;                        !- Latent Heat Recovery Effectiveness {dimensionless}

ZoneHVAC:IdealLoadsAirSystem,
    Z4_TOI Ideal Loads,      !- Name
    ,                        !- Availability Schedule Name
    Z4 Supply Inlets,        !- Zone Supply Air Node Name
    ,                        !- Zone Exhaust Air Node Name
    50,                      !- Maximum Heating Supply Air Temperature {C}
    13,                      !- Minimum Cooling Supply Air Temperature {C}
    0.015,                   !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir}
    0.01,                    !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir}
    NoLimit,                 !- Heating Limit
    autosize,                !- Maximum Heating Air Flow Rate {m3/s}
    ,                        !- Maximum Sensible Heating Capacity {W}
    NoLimit,                 !- Cooling Limit
    autosize,                !- Maximum Cooling Air Flow Rate {m3/s}
    ,                        !- Maximum Total Cooling Capacity {W}
    ,                        !- Heating Availability Schedule Name
    ,                        !- Cooling Availability Schedule Name
    ConstantSupplyHumidityRatio,  !- Dehumidification Control Type
    ,                        !- Cooling Sensible Heat Ratio {dimensionless}
    ConstantSupplyHumidityRatio,  !- Humidification Control Type
    ,                        !- Design Specification Outdoor Air Object Name
    ,                        !- Outdoor Air Inlet Node Name
    ,                        !- Demand Controlled Ventilation Type
    ,                        !- Outdoor Air Economizer Type
    ,                        !- Heat Recovery Type
    ,                        !- Sensible Heat Recovery Effectiveness {dimensionless}
    ;                        !- Latent Heat Recovery Effectiveness {dimensionless}

Construction,
    Attic Floor,             !- Name
    Gypsum Board 13mm NZS4214,  !- Outside Layer
    Comp 140mm R2.8 9.9%;    !- Layer 2

GroundHeatTransfer:Control,
    Slab,                    !- Name
    No,                      !- Run Basement Preprocessor
    Yes;                     !- Run Slab Preprocessor

Schedule:Compact,
    LIVHeating PMV Setpoints,!- Name
    Any Number,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 18:00, -.7,       !- Field 4
    Until: 21:00, -.5,       !- Field 6
    Until: 24:00, -.7;       !- Field 8

Schedule:Compact,
    LIVCooling PMV Setpoint, !- Name
    Any Number,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 18:00, .7,        !- Field 4
    Until: 21:00, .5,        !- Field 6
    Until: 24:00, .7;        !- Field 8

Schedule:Compact,
    Cooling PMV Setpoint,    !- Name
    Any Number,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00, .7;        !- Field 4

Schedule:Compact,
    Heating PMV Setpoint,    !- Name
    Any Number,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00, -0.7;      !- Field 4

ZoneList,
    AllButLIV,               !- Name
    Z2KIT,                   !- Zone 1 Name
    Z3ENT,                   !- Zone 2 Name
    Z4TOI,                   !- Zone 3 Name
    Z5BAT,                   !- Zone 4 Name
    Z6BSW,                   !- Zone 5 Name
    Z7BNW,                   !- Zone 6 Name
    Z8BN,                    !- Zone 7 Name
    Z9COR;                   !- Zone 8 Name

Schedule:Compact,
    ZONE CONTROL TYPE SCHEDULE,  !- Name
    Control Type,            !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00, 4;         !- Field 4

ThermostatSetpoint:ThermalComfort:Fanger:DualSetpoint,
    AllButLIV DUAL COMFORT SETPOINTS,  !- Name
    Heating PMV Setpoint,    !- Fanger Thermal Comfort Heating Schedule Name
    Cooling PMV Setpoint;    !- Fanger Thermal Comfort Cooling Schedule Name

ThermostatSetpoint:ThermalComfort:Fanger:DualSetpoint,
    Z1_LIV DUAL COMFORT SETPOINTS,  !- Name
    LIVHeating PMV Setpoints,!- Fanger Thermal Comfort Heating Schedule Name
    LIVCooling PMV Setpoint; !- Fanger Thermal Comfort Cooling Schedule Name

ZoneHVAC:EquipmentList,
    Z1LIV EQUIP,             !- Name
    ZoneHVAC:IdealLoadsAirSystem,  !- Zone Equipment 1 Object Type
    Z1_LIV Ideal Loads,      !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence

ZoneHVAC:EquipmentConnections,
    Z3ENT,                   !- Zone Name
    Z3ENT EQUIP,             !- Zone Conditioning Equipment List Name
    Z3 Supply Inlets,        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    Z3 Air Node,             !- Zone Air Node Name
    Z3 Return Outlet;        !- Zone Return Air Node Name

NodeList,
    Z1 Supply Inlets,        !- Name
    Z1 Supply Inlet;         !- Node 1 Name

NodeList,
    Z2 Supply Inlets,        !- Name
    Z2 Supply Inlet;         !- Node 1 Name

NodeList,
    Z3 Supply Inlets,        !- Name
    Z3 Supply Inlet;         !- Node 1 Name

NodeList,
    Z4 Supply Inlets,        !- Name
    Z4 Supply Inlet;         !- Node 1 Name

NodeList,
    Z5 Supply Inlets,        !- Name
    Z5 Supply Inlet;         !- Node 1 Name

NodeList,
    Z6 Supply Inlets,        !- Name
    Z6 Supply Inlet;         !- Node 1 Name

NodeList,
    Z7 Supply Inlets,        !- Name
    Z7 Supply Inlet;         !- Node 1 Name

NodeList,
    Z8 Supply Inlets,        !- Name
    Z8 Supply Inlet;         !- Node 1 Name

NodeList,
    Z9 Supply Inlets,        !- Name
    Z9 Supply Inlet;         !- Node 1 Name

ZoneHVAC:EquipmentList,
    Z2KIT EQUIP,             !- Name
    ZoneHVAC:IdealLoadsAirSystem,  !- Zone Equipment 1 Object Type
    Z2_KIT Ideal Loads,      !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    Z3ENT EQUIP,             !- Name
    ZoneHVAC:IdealLoadsAirSystem,  !- Zone Equipment 1 Object Type
    Z3_ENT Ideal Loads,      !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    Z4TOI EQUIP,             !- Name
    ZoneHVAC:IdealLoadsAirSystem,  !- Zone Equipment 1 Object Type
    Z4_TOI Ideal Loads,      !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    Z5BAT EQUIP,             !- Name
    ZoneHVAC:IdealLoadsAirSystem,  !- Zone Equipment 1 Object Type
    Z5_BAT Ideal Loads,      !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    Z6BSW EQUIP,             !- Name
    ZoneHVAC:IdealLoadsAirSystem,  !- Zone Equipment 1 Object Type
    Z6_BSW Ideal Loads,      !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    Z7BNW EQUIP,             !- Name
    ZoneHVAC:IdealLoadsAirSystem,  !- Zone Equipment 1 Object Type
    Z7_BNW Ideal Loads,      !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    Z8BN EQUIP,              !- Name
    ZoneHVAC:IdealLoadsAirSystem,  !- Zone Equipment 1 Object Type
    Z8_BN Ideal Loads,       !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    Z9COR EQUIP,             !- Name
    ZoneHVAC:IdealLoadsAirSystem,  !- Zone Equipment 1 Object Type
    Z9_COR Ideal Loads,      !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence

ZoneHVAC:EquipmentConnections,
    Z4TOI,                   !- Zone Name
    Z4TOI EQUIP,             !- Zone Conditioning Equipment List Name
    Z4 Supply Inlets,        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    Z4 Air Node,             !- Zone Air Node Name
    Z4 Return Outlet;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    Z5BAT,                   !- Zone Name
    Z5BAT EQUIP,             !- Zone Conditioning Equipment List Name
    Z5 Supply Inlets,        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    Z5 Air Node,             !- Zone Air Node Name
    Z5 Return Outlet;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    Z6BSW,                   !- Zone Name
    Z6BSW EQUIP,             !- Zone Conditioning Equipment List Name
    Z6 Supply Inlets,        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    Z6 Air Node,             !- Zone Air Node Name
    Z6 Return Outlet;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    Z7BNW,                   !- Zone Name
    Z7BNW EQUIP,             !- Zone Conditioning Equipment List Name
    Z7 Supply Inlets,        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    Z7 Air Node,             !- Zone Air Node Name
    Z7 Return Outlet;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    Z8BN,                    !- Zone Name
    Z8BN EQUIP,              !- Zone Conditioning Equipment List Name
    Z8 Supply Inlets,        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    Z8 Air Node,             !- Zone Air Node Name
    Z8 Return Outlet;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    Z9COR,                   !- Zone Name
    Z9COR EQUIP,             !- Zone Conditioning Equipment List Name
    Z9 Supply Inlets,        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    Z9 Air Node,             !- Zone Air Node Name
    Z9 Return Outlet;        !- Zone Return Air Node Name

ZoneInfiltration:DesignFlowRate,
    AirChangeRateHouse,      !- Name
    AllControlledZones,      !- Zone or ZoneList Name
    Sched AC/h,              !- Schedule Name
    AirChanges/Hour,         !- Design Flow Rate Calculation Method
    ,                        !- Design Flow Rate {m3/s}
    ,                        !- Flow per Zone Floor Area {m3/s-m2}
    ,                        !- Flow per Exterior Surface Area {m3/s-m2}
    1,                       !- Air Changes per Hour {1/hr}
    1,                       !- Constant Term Coefficient
    0,                       !- Temperature Term Coefficient
    0,                       !- Velocity Term Coefficient
    0;                       !- Velocity Squared Term Coefficient

Output:Variable,*,People Latent Heat Gain,RunPeriod;
Output:Variable,*,Ideal Loads Total Heating Energy,hourly;
Output:Variable,*,Ideal Loads Sensible Cooling Energy,hourly;
Output:Variable,*,Ideal Loads Latent Cooling Energy,hourly;
Output:Variable,*,Ideal Loads Total Cooling Energy,hourly;
Output:Variable,*,Ideal Loads Zone Total Cooling Energy,hourly;
Output:Variable,*,Ideal Loads Zone Total Heating Energy,hourly;
Output:Variable,*,Outdoor Dry Bulb,hourly;

OtherEquipment,
    Vapour,                  !- Name
    Z5BAT,                   !- Zone Name
    WaterVapourOn,           !- Schedule Name
    EquipmentLevel,          !- Design Level Calculation Method
    0,                       !- Design Level {W}
    ,                        !- Watts per Zone Floor Area {W/m2}
    ,                        !- Watts per Person {W/Person}
    1,                       !- Fraction Latent
    0,                       !- Fraction Radiant
    0;                       !- Fraction Lost

Output:Variable,*,Zone Air Humidity Ratio,RunPeriod;

SizingPeriod:DesignDay,
    Auckland Ann Htg 99.6% Condns DB,  !- Name
    7,                       !- Month
    21,                      !- Day of Month
    WinterDesignDay,         !- Day Type
    1.8,                     !- Maximum Dry-Bulb Temperature {C}
    0.0,                     !- Daily Dry-Bulb Temperature Range {deltaC}
    DefaultMultipliers,      !- Dry-Bulb Temperature Range Modifier Type
    ,                        !- Dry-Bulb Temperature Range Modifier Schedule Name
    Wetbulb,                 !- Humidity Condition Type
    1.8,                     !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
    ,                        !- Humidity Condition Day Schedule Name
    ,                        !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
    ,                        !- Enthalpy at Maximum Dry-Bulb {J/kg}
    ,                        !- Daily Wet-Bulb Temperature Range {deltaC}
    100929.,                 !- Barometric Pressure {Pa}
    4.5,                     !- Wind Speed {m/s}
    230,                     !- Wind Direction {deg}
    No,                      !- Rain Indicator
    No,                      !- Snow Indicator
    No,                      !- Daylight Saving Time Indicator
    ASHRAEClearSky,          !- Solar Model Indicator
    ,                        !- Beam Solar Day Schedule Name
    ,                        !- Diffuse Solar Day Schedule Name
    ,                        !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
    ,                        !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
    0.00;                    !- Sky Clearness

SizingPeriod:DesignDay,
    Auckland Ann Htg 99% Condns DB,  !- Name
    7,                       !- Month
    21,                      !- Day of Month
    WinterDesignDay,         !- Day Type
    2.9,                     !- Maximum Dry-Bulb Temperature {C}
    0.0,                     !- Daily Dry-Bulb Temperature Range {deltaC}
    DefaultMultipliers,      !- Dry-Bulb Temperature Range Modifier Type
    ,                        !- Dry-Bulb Temperature Range Modifier Schedule Name
    Wetbulb,                 !- Humidity Condition Type
    2.9,                     !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
    ,                        !- Humidity Condition Day Schedule Name
    ,                        !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
    ,                        !- Enthalpy at Maximum Dry-Bulb {J/kg}
    ,                        !- Daily Wet-Bulb Temperature Range {deltaC}
    100929.,                 !- Barometric Pressure {Pa}
    4.5,                     !- Wind Speed {m/s}
    230,                     !- Wind Direction {deg}
    No,                      !- Rain Indicator
    No,                      !- Snow Indicator
    No,                      !- Daylight Saving Time Indicator
    ASHRAEClearSky,          !- Solar Model Indicator
    ,                        !- Beam Solar Day Schedule Name
    ,                        !- Diffuse Solar Day Schedule Name
    ,                        !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
    ,                        !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
    0.00;                    !- Sky Clearness

SizingPeriod:DesignDay,
    Auckland Ann Hum_n 99.6% Condns DP=>MCDB,  !- Name
    7,                       !- Month
    21,                      !- Day of Month
    WinterDesignDay,         !- Day Type
    5.9,                     !- Maximum Dry-Bulb Temperature {C}
    0.0,                     !- Daily Dry-Bulb Temperature Range {deltaC}
    DefaultMultipliers,      !- Dry-Bulb Temperature Range Modifier Type
    ,                        !- Dry-Bulb Temperature Range Modifier Schedule Name
    Dewpoint,                !- Humidity Condition Type
    1.8,                     !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
    ,                        !- Humidity Condition Day Schedule Name
    ,                        !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
    ,                        !- Enthalpy at Maximum Dry-Bulb {J/kg}
    ,                        !- Daily Wet-Bulb Temperature Range {deltaC}
    100929.,                 !- Barometric Pressure {Pa}
    4.5,                     !- Wind Speed {m/s}
    230,                     !- Wind Direction {deg}
    No,                      !- Rain Indicator
    No,                      !- Snow Indicator
    No,                      !- Daylight Saving Time Indicator
    ASHRAEClearSky,          !- Solar Model Indicator
    ,                        !- Beam Solar Day Schedule Name
    ,                        !- Diffuse Solar Day Schedule Name
    ,                        !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
    ,                        !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
    0.00;                    !- Sky Clearness

SizingPeriod:DesignDay,
    Auckland Ann Hum_n 99% Condns DP=>MCDB,  !- Name
    7,                       !- Month
    21,                      !- Day of Month
    WinterDesignDay,         !- Day Type
    6.8,                     !- Maximum Dry-Bulb Temperature {C}
    0.0,                     !- Daily Dry-Bulb Temperature Range {deltaC}
    DefaultMultipliers,      !- Dry-Bulb Temperature Range Modifier Type
    ,                        !- Dry-Bulb Temperature Range Modifier Schedule Name
    Dewpoint,                !- Humidity Condition Type
    2.8,                     !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
    ,                        !- Humidity Condition Day Schedule Name
    ,                        !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
    ,                        !- Enthalpy at Maximum Dry-Bulb {J/kg}
    ,                        !- Daily Wet-Bulb Temperature Range {deltaC}
    100929.,                 !- Barometric Pressure {Pa}
    4.5,                     !- Wind Speed {m/s}
    230,                     !- Wind Direction {deg}
    No,                      !- Rain Indicator
    No,                      !- Snow Indicator
    No,                      !- Daylight Saving Time Indicator
    ASHRAEClearSky,          !- Solar Model Indicator
    ,                        !- Beam Solar Day Schedule Name
    ,                        !- Diffuse Solar Day Schedule Name
    ,                        !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
    ,                        !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
    0.00;                    !- Sky Clearness

SizingPeriod:DesignDay,
    Auckland Ann Htg Wind 99.6% Condns WS=>MCDB,  !- Name
    7,                       !- Month
    21,                      !- Day of Month
    WinterDesignDay,         !- Day Type
    12.4,                    !- Maximum Dry-Bulb Temperature {C}
    0.0,                     !- Daily Dry-Bulb Temperature Range {deltaC}
    DefaultMultipliers,      !- Dry-Bulb Temperature Range Modifier Type
    ,                        !- Dry-Bulb Temperature Range Modifier Schedule Name
    Wetbulb,                 !- Humidity Condition Type
    12.4,                    !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
    ,                        !- Humidity Condition Day Schedule Name
    ,                        !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
    ,                        !- Enthalpy at Maximum Dry-Bulb {J/kg}
    ,                        !- Daily Wet-Bulb Temperature Range {deltaC}
    100929.,                 !- Barometric Pressure {Pa}
    15.3,                    !- Wind Speed {m/s}
    230,                     !- Wind Direction {deg}
    No,                      !- Rain Indicator
    No,                      !- Snow Indicator
    No,                      !- Daylight Saving Time Indicator
    ASHRAEClearSky,          !- Solar Model Indicator
    ,                        !- Beam Solar Day Schedule Name
    ,                        !- Diffuse Solar Day Schedule Name
    ,                        !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
    ,                        !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
    0.00;                    !- Sky Clearness

SizingPeriod:DesignDay,
    Auckland Ann Htg Wind 99% Condns WS=>MCDB,  !- Name
    7,                       !- Month
    21,                      !- Day of Month
    WinterDesignDay,         !- Day Type
    12.2,                    !- Maximum Dry-Bulb Temperature {C}
    0.0,                     !- Daily Dry-Bulb Temperature Range {deltaC}
    DefaultMultipliers,      !- Dry-Bulb Temperature Range Modifier Type
    ,                        !- Dry-Bulb Temperature Range Modifier Schedule Name
    Wetbulb,                 !- Humidity Condition Type
    12.2,                    !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
    ,                        !- Humidity Condition Day Schedule Name
    ,                        !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
    ,                        !- Enthalpy at Maximum Dry-Bulb {J/kg}
    ,                        !- Daily Wet-Bulb Temperature Range {deltaC}
    100929.,                 !- Barometric Pressure {Pa}
    13.4,                    !- Wind Speed {m/s}
    230,                     !- Wind Direction {deg}
    No,                      !- Rain Indicator
    No,                      !- Snow Indicator
    No,                      !- Daylight Saving Time Indicator
    ASHRAEClearSky,          !- Solar Model Indicator
    ,                        !- Beam Solar Day Schedule Name
    ,                        !- Diffuse Solar Day Schedule Name
    ,                        !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
    ,                        !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}
    0.00;                    !- Sky Clearness

SizingPeriod:DesignDay,
    Auckland Ann Clg .4% Condns DB=>MWB,  !- Name
    2,                       !- Month
    21,                      !- Day of Month
    SummerDesignDay,         !- Day Type
    25.2,                    !- Maximum Dry-Bulb Temperature {C}
    6.9,                     !- Daily Dry-Bulb Temperature Range {deltaC}
    DefaultMultipliers,      !- Dry-Bulb Temperature Range Modifier Type
    ,                        !- Dry-Bulb Temperature Range Modifier Schedule Name
    Wetbulb,                 !- Humidity Condition Type
    19.7,                    !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
    ,                        !- Humidity Condition Day Schedule Name
    ,                        !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
    ,                        !- Enthalpy at Maximum Dry-Bulb {J/kg}
    ,                        !- Daily Wet-Bulb Temperature Range {deltaC}
    100929.,                 !- Barometric Pressure {Pa}
    5.8,                     !- Wind Speed {m/s}
    20,                      !- Wind Direction {deg}
    No,                      !- Rain Indicator
    No,                      !- Snow Indicator
    No,                      !- Daylight Saving Time Indicator
    ASHRAETau,               !- Solar Model Indicator
    ,                        !- Beam Solar Day Schedule Name
    ,                        !- Diffuse Solar Day Schedule Name
    0.357,                   !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
    2.535;                   !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}

SizingPeriod:DesignDay,
    Auckland Ann Clg 1% Condns DB=>MWB,  !- Name
    2,                       !- Month
    21,                      !- Day of Month
    SummerDesignDay,         !- Day Type
    24.2,                    !- Maximum Dry-Bulb Temperature {C}
    6.9,                     !- Daily Dry-Bulb Temperature Range {deltaC}
    DefaultMultipliers,      !- Dry-Bulb Temperature Range Modifier Type
    ,                        !- Dry-Bulb Temperature Range Modifier Schedule Name
    Wetbulb,                 !- Humidity Condition Type
    19.2,                    !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
    ,                        !- Humidity Condition Day Schedule Name
    ,                        !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
    ,                        !- Enthalpy at Maximum Dry-Bulb {J/kg}
    ,                        !- Daily Wet-Bulb Temperature Range {deltaC}
    100929.,                 !- Barometric Pressure {Pa}
    5.8,                     !- Wind Speed {m/s}
    20,                      !- Wind Direction {deg}
    No,                      !- Rain Indicator
    No,                      !- Snow Indicator
    No,                      !- Daylight Saving Time Indicator
    ASHRAETau,               !- Solar Model Indicator
    ,                        !- Beam Solar Day Schedule Name
    ,                        !- Diffuse Solar Day Schedule Name
    0.357,                   !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
    2.535;                   !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}

SizingPeriod:DesignDay,
    Auckland Ann Clg 2% Condns DB=>MWB,  !- Name
    2,                       !- Month
    21,                      !- Day of Month
    SummerDesignDay,         !- Day Type
    23.3,                    !- Maximum Dry-Bulb Temperature {C}
    6.9,                     !- Daily Dry-Bulb Temperature Range {deltaC}
    DefaultMultipliers,      !- Dry-Bulb Temperature Range Modifier Type
    ,                        !- Dry-Bulb Temperature Range Modifier Schedule Name
    Wetbulb,                 !- Humidity Condition Type
    18.7,                    !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
    ,                        !- Humidity Condition Day Schedule Name
    ,                        !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
    ,                        !- Enthalpy at Maximum Dry-Bulb {J/kg}
    ,                        !- Daily Wet-Bulb Temperature Range {deltaC}
    100929.,                 !- Barometric Pressure {Pa}
    5.8,                     !- Wind Speed {m/s}
    20,                      !- Wind Direction {deg}
    No,                      !- Rain Indicator
    No,                      !- Snow Indicator
    No,                      !- Daylight Saving Time Indicator
    ASHRAETau,               !- Solar Model Indicator
    ,                        !- Beam Solar Day Schedule Name
    ,                        !- Diffuse Solar Day Schedule Name
    0.357,                   !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
    2.535;                   !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}

SizingPeriod:DesignDay,
    Auckland Ann Clg .4% Condns WB=>MDB,  !- Name
    2,                       !- Month
    21,                      !- Day of Month
    SummerDesignDay,         !- Day Type
    23.6,                    !- Maximum Dry-Bulb Temperature {C}
    6.9,                     !- Daily Dry-Bulb Temperature Range {deltaC}
    DefaultMultipliers,      !- Dry-Bulb Temperature Range Modifier Type
    ,                        !- Dry-Bulb Temperature Range Modifier Schedule Name
    Wetbulb,                 !- Humidity Condition Type
    21.2,                    !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
    ,                        !- Humidity Condition Day Schedule Name
    ,                        !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
    ,                        !- Enthalpy at Maximum Dry-Bulb {J/kg}
    ,                        !- Daily Wet-Bulb Temperature Range {deltaC}
    100929.,                 !- Barometric Pressure {Pa}
    5.8,                     !- Wind Speed {m/s}
    20,                      !- Wind Direction {deg}
    No,                      !- Rain Indicator
    No,                      !- Snow Indicator
    No,                      !- Daylight Saving Time Indicator
    ASHRAETau,               !- Solar Model Indicator
    ,                        !- Beam Solar Day Schedule Name
    ,                        !- Diffuse Solar Day Schedule Name
    0.357,                   !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
    2.535;                   !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}

SizingPeriod:DesignDay,
    Auckland Ann Clg 1% Condns WB=>MDB,  !- Name
    2,                       !- Month
    21,                      !- Day of Month
    SummerDesignDay,         !- Day Type
    22.9,                    !- Maximum Dry-Bulb Temperature {C}
    6.9,                     !- Daily Dry-Bulb Temperature Range {deltaC}
    DefaultMultipliers,      !- Dry-Bulb Temperature Range Modifier Type
    ,                        !- Dry-Bulb Temperature Range Modifier Schedule Name
    Wetbulb,                 !- Humidity Condition Type
    20.5,                    !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
    ,                        !- Humidity Condition Day Schedule Name
    ,                        !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
    ,                        !- Enthalpy at Maximum Dry-Bulb {J/kg}
    ,                        !- Daily Wet-Bulb Temperature Range {deltaC}
    100929.,                 !- Barometric Pressure {Pa}
    5.8,                     !- Wind Speed {m/s}
    20,                      !- Wind Direction {deg}
    No,                      !- Rain Indicator
    No,                      !- Snow Indicator
    No,                      !- Daylight Saving Time Indicator
    ASHRAETau,               !- Solar Model Indicator
    ,                        !- Beam Solar Day Schedule Name
    ,                        !- Diffuse Solar Day Schedule Name
    0.357,                   !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
    2.535;                   !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}

SizingPeriod:DesignDay,
    Auckland Ann Clg 2% Condns WB=>MDB,  !- Name
    2,                       !- Month
    21,                      !- Day of Month
    SummerDesignDay,         !- Day Type
    22.2,                    !- Maximum Dry-Bulb Temperature {C}
    6.9,                     !- Daily Dry-Bulb Temperature Range {deltaC}
    DefaultMultipliers,      !- Dry-Bulb Temperature Range Modifier Type
    ,                        !- Dry-Bulb Temperature Range Modifier Schedule Name
    Wetbulb,                 !- Humidity Condition Type
    19.7,                    !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
    ,                        !- Humidity Condition Day Schedule Name
    ,                        !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
    ,                        !- Enthalpy at Maximum Dry-Bulb {J/kg}
    ,                        !- Daily Wet-Bulb Temperature Range {deltaC}
    100929.,                 !- Barometric Pressure {Pa}
    5.8,                     !- Wind Speed {m/s}
    20,                      !- Wind Direction {deg}
    No,                      !- Rain Indicator
    No,                      !- Snow Indicator
    No,                      !- Daylight Saving Time Indicator
    ASHRAETau,               !- Solar Model Indicator
    ,                        !- Beam Solar Day Schedule Name
    ,                        !- Diffuse Solar Day Schedule Name
    0.357,                   !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
    2.535;                   !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}

SizingPeriod:DesignDay,
    Auckland Ann Clg .4% Condns DP=>MDB,  !- Name
    2,                       !- Month
    21,                      !- Day of Month
    SummerDesignDay,         !- Day Type
    22.4,                    !- Maximum Dry-Bulb Temperature {C}
    6.9,                     !- Daily Dry-Bulb Temperature Range {deltaC}
    DefaultMultipliers,      !- Dry-Bulb Temperature Range Modifier Type
    ,                        !- Dry-Bulb Temperature Range Modifier Schedule Name
    Dewpoint,                !- Humidity Condition Type
    20.2,                    !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
    ,                        !- Humidity Condition Day Schedule Name
    ,                        !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
    ,                        !- Enthalpy at Maximum Dry-Bulb {J/kg}
    ,                        !- Daily Wet-Bulb Temperature Range {deltaC}
    100929.,                 !- Barometric Pressure {Pa}
    5.8,                     !- Wind Speed {m/s}
    20,                      !- Wind Direction {deg}
    No,                      !- Rain Indicator
    No,                      !- Snow Indicator
    No,                      !- Daylight Saving Time Indicator
    ASHRAETau,               !- Solar Model Indicator
    ,                        !- Beam Solar Day Schedule Name
    ,                        !- Diffuse Solar Day Schedule Name
    0.357,                   !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
    2.535;                   !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}

SizingPeriod:DesignDay,
    Auckland Ann Clg 1% Condns DP=>MDB,  !- Name
    2,                       !- Month
    21,                      !- Day of Month
    SummerDesignDay,         !- Day Type
    21.9,                    !- Maximum Dry-Bulb Temperature {C}
    6.9,                     !- Daily Dry-Bulb Temperature Range {deltaC}
    DefaultMultipliers,      !- Dry-Bulb Temperature Range Modifier Type
    ,                        !- Dry-Bulb Temperature Range Modifier Schedule Name
    Dewpoint,                !- Humidity Condition Type
    19.5,                    !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
    ,                        !- Humidity Condition Day Schedule Name
    ,                        !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
    ,                        !- Enthalpy at Maximum Dry-Bulb {J/kg}
    ,                        !- Daily Wet-Bulb Temperature Range {deltaC}
    100929.,                 !- Barometric Pressure {Pa}
    5.8,                     !- Wind Speed {m/s}
    20,                      !- Wind Direction {deg}
    No,                      !- Rain Indicator
    No,                      !- Snow Indicator
    No,                      !- Daylight Saving Time Indicator
    ASHRAETau,               !- Solar Model Indicator
    ,                        !- Beam Solar Day Schedule Name
    ,                        !- Diffuse Solar Day Schedule Name
    0.357,                   !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
    2.535;                   !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}

SizingPeriod:DesignDay,
    Auckland Ann Clg 2% Condns DP=>MDB,  !- Name
    2,                       !- Month
    21,                      !- Day of Month
    SummerDesignDay,         !- Day Type
    21.4,                    !- Maximum Dry-Bulb Temperature {C}
    6.9,                     !- Daily Dry-Bulb Temperature Range {deltaC}
    DefaultMultipliers,      !- Dry-Bulb Temperature Range Modifier Type
    ,                        !- Dry-Bulb Temperature Range Modifier Schedule Name
    Dewpoint,                !- Humidity Condition Type
    18.9,                    !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
    ,                        !- Humidity Condition Day Schedule Name
    ,                        !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
    ,                        !- Enthalpy at Maximum Dry-Bulb {J/kg}
    ,                        !- Daily Wet-Bulb Temperature Range {deltaC}
    100929.,                 !- Barometric Pressure {Pa}
    5.8,                     !- Wind Speed {m/s}
    20,                      !- Wind Direction {deg}
    No,                      !- Rain Indicator
    No,                      !- Snow Indicator
    No,                      !- Daylight Saving Time Indicator
    ASHRAETau,               !- Solar Model Indicator
    ,                        !- Beam Solar Day Schedule Name
    ,                        !- Diffuse Solar Day Schedule Name
    0.357,                   !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
    2.535;                   !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}

SizingPeriod:DesignDay,
    Auckland Ann Clg .4% Condns Enth=>MDB,  !- Name
    2,                       !- Month
    21,                      !- Day of Month
    SummerDesignDay,         !- Day Type
    23.3,                    !- Maximum Dry-Bulb Temperature {C}
    6.9,                     !- Daily Dry-Bulb Temperature Range {deltaC}
    DefaultMultipliers,      !- Dry-Bulb Temperature Range Modifier Type
    ,                        !- Dry-Bulb Temperature Range Modifier Schedule Name
    Enthalpy,                !- Humidity Condition Type
    ,                        !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
    ,                        !- Humidity Condition Day Schedule Name
    ,                        !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
    61600.0,                 !- Enthalpy at Maximum Dry-Bulb {J/kg}
    ,                        !- Daily Wet-Bulb Temperature Range {deltaC}
    100929.,                 !- Barometric Pressure {Pa}
    5.8,                     !- Wind Speed {m/s}
    20,                      !- Wind Direction {deg}
    No,                      !- Rain Indicator
    No,                      !- Snow Indicator
    No,                      !- Daylight Saving Time Indicator
    ASHRAETau,               !- Solar Model Indicator
    ,                        !- Beam Solar Day Schedule Name
    ,                        !- Diffuse Solar Day Schedule Name
    0.357,                   !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
    2.535;                   !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}

SizingPeriod:DesignDay,
    Auckland Ann Clg 1% Condns Enth=>MDB,  !- Name
    2,                       !- Month
    21,                      !- Day of Month
    SummerDesignDay,         !- Day Type
    22.5,                    !- Maximum Dry-Bulb Temperature {C}
    6.9,                     !- Daily Dry-Bulb Temperature Range {deltaC}
    DefaultMultipliers,      !- Dry-Bulb Temperature Range Modifier Type
    ,                        !- Dry-Bulb Temperature Range Modifier Schedule Name
    Enthalpy,                !- Humidity Condition Type
    ,                        !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
    ,                        !- Humidity Condition Day Schedule Name
    ,                        !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
    59000.0,                 !- Enthalpy at Maximum Dry-Bulb {J/kg}
    ,                        !- Daily Wet-Bulb Temperature Range {deltaC}
    100929.,                 !- Barometric Pressure {Pa}
    5.8,                     !- Wind Speed {m/s}
    20,                      !- Wind Direction {deg}
    No,                      !- Rain Indicator
    No,                      !- Snow Indicator
    No,                      !- Daylight Saving Time Indicator
    ASHRAETau,               !- Solar Model Indicator
    ,                        !- Beam Solar Day Schedule Name
    ,                        !- Diffuse Solar Day Schedule Name
    0.357,                   !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
    2.535;                   !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}

SizingPeriod:DesignDay,
    Auckland Ann Clg 2% Condns Enth=>MDB,  !- Name
    2,                       !- Month
    21,                      !- Day of Month
    SummerDesignDay,         !- Day Type
    22.4,                    !- Maximum Dry-Bulb Temperature {C}
    6.9,                     !- Daily Dry-Bulb Temperature Range {deltaC}
    DefaultMultipliers,      !- Dry-Bulb Temperature Range Modifier Type
    ,                        !- Dry-Bulb Temperature Range Modifier Schedule Name
    Enthalpy,                !- Humidity Condition Type
    ,                        !- Wetbulb or DewPoint at Maximum Dry-Bulb {C}
    ,                        !- Humidity Condition Day Schedule Name
    ,                        !- Humidity Ratio at Maximum Dry-Bulb {kgWater/kgDryAir}
    56500.0,                 !- Enthalpy at Maximum Dry-Bulb {J/kg}
    ,                        !- Daily Wet-Bulb Temperature Range {deltaC}
    100929.,                 !- Barometric Pressure {Pa}
    5.8,                     !- Wind Speed {m/s}
    20,                      !- Wind Direction {deg}
    No,                      !- Rain Indicator
    No,                      !- Snow Indicator
    No,                      !- Daylight Saving Time Indicator
    ASHRAETau,               !- Solar Model Indicator
    ,                        !- Beam Solar Day Schedule Name
    ,                        !- Diffuse Solar Day Schedule Name
    0.357,                   !- ASHRAE Clear Sky Optical Depth for Beam Irradiance (taub) {dimensionless}
    2.535;                   !- ASHRAE Clear Sky Optical Depth for Diffuse Irradiance (taud) {dimensionless}

Site:Location,
    Auckland_Auckland_New Zealand Design_Conditions,  !- Name
    -37.01,                  !- Latitude {deg}
    174.79,                  !- Longitude {deg}
    12.0,                    !- Time Zone {hr}
    33.00;                   !- Elevation {m}

SizingPeriod:WeatherFileConditionType,
    AKL_WinterExtreme,       !- Name
    WinterExtreme,           !- Period Selection
    Monday,                  !- Day of Week for Start Day
    Yes,                     !- Use Weather File Daylight Saving Period
    Yes;                     !- Use Weather File Rain and Snow Indicators

Schedule:Constant,WaterVapourOn,On/Off,1;
Schedule:Constant,WaterVapourOff,On/Off,0;
ZoneCapacitanceMultiplier:ResearchSpecial,1,15,1,1;
Output:Variable,*,Zone Air Relative Humidity,Hourly;
Output:Variable,*,FangerPMV,Hourly;

People,
    PeopleKidsBed,           !- Name
    Kids Bedrooms,           !- Zone or ZoneList Name
    Kids Bedroom occ,        !- Number of People Schedule Name
    People,                  !- Number of People Calculation Method
    2,                       !- Number of People
    ,                        !- People per Zone Floor Area {person/m2}
    ,                        !- Zone Floor Area per Person {m2/person}
    0.3000000,               !- Fraction Radiant
    ,                        !- Sensible Heat Fraction
    Activity Sch,            !- Activity Level Schedule Name
    3.82E-8,                 !- Carbon Dioxide Generation Rate {m3/s-W}
    ,                        !- Enable ASHRAE 55 Comfort Warnings
    zoneaveraged,            !- Mean Radiant Temperature Calculation Type
    ,                        !- Surface Name/Angle Factor List Name
    Work Eff Sch,            !- Work Efficiency Schedule Name
    Clothing Sch,            !- Clothing Insulation Schedule Name
    Air Velo Sch,            !- Air Velocity Schedule Name
    FANGER;                  !- Thermal Comfort Model 1 Type

People,
    PeopleFamilyRooms,       !- Name
    Family Rooms,            !- Zone or ZoneList Name
    Living occ,              !- Number of People Schedule Name
    People,                  !- Number of People Calculation Method
    4,                       !- Number of People
    ,                        !- People per Zone Floor Area {person/m2}
    ,                        !- Zone Floor Area per Person {m2/person}
    0.3000000,               !- Fraction Radiant
    ,                        !- Sensible Heat Fraction
    Activity Sch,            !- Activity Level Schedule Name
    3.82E-8,                 !- Carbon Dioxide Generation Rate {m3/s-W}
    ,                        !- Enable ASHRAE 55 Comfort Warnings
    zoneaveraged,            !- Mean Radiant Temperature Calculation Type
    ,                        !- Surface Name/Angle Factor List Name
    Work Eff Sch,            !- Work Efficiency Schedule Name
    Clothing Sch,            !- Clothing Insulation Schedule Name
    Air Velo Sch,            !- Air Velocity Schedule Name
    FANGER;                  !- Thermal Comfort Model 1 Type

People,
    PeopleWetrooms,          !- Name
    Wetrooms,                !- Zone or ZoneList Name
    Wetrooms occ,            !- Number of People Schedule Name
    People,                  !- Number of People Calculation Method
    4,                       !- Number of People
    ,                        !- People per Zone Floor Area {person/m2}
    ,                        !- Zone Floor Area per Person {m2/person}
    0.3000000,               !- Fraction Radiant
    ,                        !- Sensible Heat Fraction
    Activity Sch,            !- Activity Level Schedule Name
    3.82E-8,                 !- Carbon Dioxide Generation Rate {m3/s-W}
    ,                        !- Enable ASHRAE 55 Comfort Warnings
    zoneaveraged,            !- Mean Radiant Temperature Calculation Type
    ,                        !- Surface Name/Angle Factor List Name
    Work Eff Sch,            !- Work Efficiency Schedule Name
    Clothing Sch,            !- Clothing Insulation Schedule Name
    Air Velo Sch,            !- Air Velocity Schedule Name
    FANGER;                  !- Thermal Comfort Model 1 Type

ZoneList,
    AllControlledZones,      !- Name
    Z1LIV,                   !- Zone 1 Name
    Z2KIT,                   !- Zone 2 Name
    Z4TOI,                   !- Zone 3 Name
    Z5BAT,                   !- Zone 4 Name
    Z6BSW,                   !- Zone 5 Name
    Z7BNW,                   !- Zone 6 Name
    Z8BN;                    !- Zone 7 Name

ZoneHVAC:IdealLoadsAirSystem,
    Z1_LIV Ideal Loads,      !- Name
    ,                        !- Availability Schedule Name
    Z1 Supply Inlets,        !- Zone Supply Air Node Name
    ,                        !- Zone Exhaust Air Node Name
    50,                      !- Maximum Heating Supply Air Temperature {C}
    13,                      !- Minimum Cooling Supply Air Temperature {C}
    0.015,                   !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir}
    0.01,                    !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir}
    NoLimit,                 !- Heating Limit
    autosize,                !- Maximum Heating Air Flow Rate {m3/s}
    ,                        !- Maximum Sensible Heating Capacity {W}
    NoLimit,                 !- Cooling Limit
    autosize,                !- Maximum Cooling Air Flow Rate {m3/s}
    ,                        !- Maximum Total Cooling Capacity {W}
    ,                        !- Heating Availability Schedule Name
    ,                        !- Cooling Availability Schedule Name
    ConstantSupplyHumidityRatio,  !- Dehumidification Control Type
    ,                        !- Cooling Sensible Heat Ratio {dimensionless}
    ConstantSupplyHumidityRatio,  !- Humidification Control Type
    ,                        !- Design Specification Outdoor Air Object Name
    ,                        !- Outdoor Air Inlet Node Name
    ,                        !- Demand Controlled Ventilation Type
    ,                        !- Outdoor Air Economizer Type
    ,                        !- Heat Recovery Type
    ,                        !- Sensible Heat Recovery Effectiveness {dimensionless}
    ;                        !- Latent Heat Recovery Effectiveness {dimensionless}

ZoneHVAC:EquipmentConnections,
    Z1LIV,                   !- Zone Name
    Z1LIV EQUIP,             !- Zone Conditioning Equipment List Name
    Z1 Supply Inlets,        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    Z1 Air Node,             !- Zone Air Node Name
    Z1 Return Outlet;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    Z2KIT,                   !- Zone Name
    Z2KIT EQUIP,             !- Zone Conditioning Equipment List Name
    Z2 Supply Inlets,        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    Z2 Air Node,             !- Zone Air Node Name
    Z2 Return Outlet;        !- Zone Return Air Node Name

Schedule:Compact,
    Sched AC/h,              !- Name
    Any Number,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until:24:00,  1;         !- Field 4

Schedule:Compact,
    Living occ,              !- Name
    Fraction,                !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: WeekDays,           !- Field 2
    Until: 7:00, 0,          !- Field 4
    Until: 8:30, 1,          !- Field 6
    Until: 9:00, .25,        !- Field 8
    Until: 14:00, 0,         !- Field 10
    Until: 17:00, .25,       !- Field 12
    Until: 20:00, 1,         !- Field 14
    Until: 24:00, 0,         !- Field 16
    For:AllOtherDays,        !- Field 17
    Until:8:00, 0,           !- Field 19
    Until: 16:00, .5,        !- Field 21
    Until: 20:00, 1,         !- Field 23
    Until: 24:00, 0;         !- Field 25

Schedule:Compact,
    Master Bedroom occ,      !- Name
    Fraction,                !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: WeekDays,           !- Field 2
    Until: 07:00, 1,         !- Field 4
    Until: 21:00, 0,         !- Field 6
    Until: 24:00, 1,         !- Field 8
    For: AllOtherDays,       !- Field 9
    Until:8:30, 1,           !- Field 11
    Until: 22:00, 0,         !- Field 13
    Until: 24:00, 1;         !- Field 15

Output:Variable,*,Zone Operative Temperature,Hourly;

Material,
    Wood 1inch,              !- Name
    MediumSmooth,            !- Roughness
    0.0254,                  !- Thickness {m}
    0.15,                    !- Conductivity {W/m-K}
    608,                     !- Density {kg/m3}
    1630,                    !- Specific Heat {J/kg-K}
    0.9,                     !- Thermal Absorptance
    0.7;                     !- Solar Absorptance

Material,
    Coloured zincalume roofing,  !- Name
    Smooth,                  !- Roughness
    0.0005,                  !- Thickness {m}
    150,                     !- Conductivity {W/m-K}
    4000,                    !- Density {kg/m3}
    600,                     !- Specific Heat {J/kg-K}
    0.9,                     !- Thermal Absorptance
    0.7,                     !- Solar Absorptance
    0.7;                     !- Visible Absorptance

Material,
    PS 2cm,                  !- Name
    MediumRough,             !- Roughness
    0.02,                    !- Thickness {m}
    0.038,                   !- Conductivity {W/m-K}
    16,                      !- Density {kg/m3}
    837.0000,                !- Specific Heat {J/kg-K}
    0.9000000,               !- Thermal Absorptance
    0.7500000,               !- Solar Absorptance
    0.7500000;               !- Visible Absorptance

Material,
    Gypsum Board 13mm NZS4214,  !- Name
    MediumSmooth,            !- Roughness
    0.013,                   !- Thickness {m}
    0.22,                    !- Conductivity {W/m-K}
    800,                     !- Density {kg/m3}
    1090,                    !- Specific Heat {J/kg-K}
    0.9,                     !- Thermal Absorptance
    0.7,                     !- Solar Absorptance
    0.7;                     !- Visible Absorptance

Material,
    Fibre cement NZS 4214,   !- Name
    MediumRough,             !- Roughness
    0.0075,                  !- Thickness {m}
    0.25,                    !- Conductivity {W/m-K}
    1470,                    !- Density {kg/m3}
    1000,                    !- Specific Heat {J/kg-K}
    0.9,                     !- Thermal Absorptance
    0.7,                     !- Solar Absorptance
    0.7;                     !- Visible Absorptance

Material,
    Concrete 80mm heavyweight,  !- Name
    MediumRough,             !- Roughness
    0.08,                    !- Thickness {m}
    1.95,                    !- Conductivity {W/m-K}
    2240,                    !- Density {kg/m3}
    900,                     !- Specific Heat {J/kg-K}
    0.9,                     !- Thermal Absorptance
    0.7;                     !- Solar Absorptance

Material,
    Comp 140mm R2.8 9.9%,    !- Name
    MediumRough,             !- Roughness
    0.14,                    !- Thickness {m}
    0.0556,                  !- Conductivity {W/m-K}
    48.3,                    !- Density {kg/m3}
    914,                     !- Specific Heat {J/kg-K}
    0.9,                     !- Thermal Absorptance
    0.7;                     !- Solar Absorptance

Material,
    Comp 90mm R1.8 14.4%,    !- Name
    MediumSmooth,            !- Roughness
    0.09,                    !- Thickness {m}
    0.0577,                  !- Conductivity {W/m-K}
    73.79,                   !- Density {kg/m3}
    964,                     !- Specific Heat {J/kg-K}
    0.9,                     !- Thermal Absorptance
    0.7,                     !- Solar Absorptance
    0.7;                     !- Visible Absorptance

Schedule:Compact,
    Kids Bedroom occ,        !- Name
    Fraction,                !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: WeekDays,           !- Field 2
    Until: 7:00, .5,         !- Field 4
    Until: 15:00, 0,         !- Field 6
    Until: 17:00, .5,        !- Field 8
    Until: 20:00, 0,         !- Field 10
    Until: 24:00, .5,        !- Field 12
    For:AllOtherDays,        !- Field 13
    Until:8:00, .5,          !- Field 15
    Until: 16:00, .5,        !- Field 17
    Until: 24:00, .5;        !- Field 19

Schedule:Compact,
    VDoorInt,                !- Name
    On/Off,                  !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: WeekDays,           !- Field 2
    Until: 7:00, 0,          !- Field 4
    Until: 21:00, 1,         !- Field 6
    Until: 24:00, 0,         !- Field 8
    For: AllOtherDays,       !- Field 9
    Until:8:00, 0,           !- Field 11
    Until: 21:00, 1,         !- Field 13
    Until: 24:00, 0;         !- Field 15

Schedule:Constant,VwinClosed,On/Off,0;
Schedule:Constant,VOpening 1_2,On/Off,1;

People,
    PeopleMB,                !- Name
    Z7BNW,                   !- Zone or ZoneList Name
    Master Bedroom occ,      !- Number of People Schedule Name
    People,                  !- Number of People Calculation Method
    2,                       !- Number of People
    ,                        !- People per Zone Floor Area {person/m2}
    ,                        !- Zone Floor Area per Person {m2/person}
    0.3000000,               !- Fraction Radiant
    ,                        !- Sensible Heat Fraction
    Activity Sch,            !- Activity Level Schedule Name
    3.82E-8,                 !- Carbon Dioxide Generation Rate {m3/s-W}
    ,                        !- Enable ASHRAE 55 Comfort Warnings
    zoneaveraged,            !- Mean Radiant Temperature Calculation Type
    ,                        !- Surface Name/Angle Factor List Name
    Work Eff Sch,            !- Work Efficiency Schedule Name
    Clothing Sch,            !- Clothing Insulation Schedule Name
    Air Velo Sch,            !- Air Velocity Schedule Name
    FANGER;                  !- Thermal Comfort Model 1 Type

Schedule:Compact,
    Wetrooms occ,            !- Name
    Fraction,                !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: WeekDays,           !- Field 2
    Until: 7:00, 0,          !- Field 4
    Until: 8:00, .25,        !- Field 6
    Until: 19:00, 0,         !- Field 8
    Until: 21:00, .25,       !- Field 10
    Until: 24:00, 0,         !- Field 12
    For:AllOtherDays,        !- Field 13
    Until: 8:00, 0,          !- Field 15
    Until: 9:00, .25,        !- Field 17
    Until: 19:00, 0,         !- Field 19
    Until: 22:00, .25,       !- Field 21
    Until: 24:00, 0;         !- Field 23

ZoneList,
    Wetrooms,                !- Name
    Z5BAT,                   !- Zone 1 Name
    Z4TOI;                   !- Zone 2 Name

ZoneList,
    Family Rooms,            !- Name
    Z2KIT,                   !- Zone 1 Name
    Z1LIV;                   !- Zone 2 Name

Schedule:Compact,
    Activity Sch,            !- Name
    Any Number,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 07:00, 72,        !- Field 4
    Until: 21:00, 126,       !- Field 6
    Until: 24:00, 72;        !- Field 8

ZoneList,
    Living Zone,             !- Name
    Z1LIV,                   !- Zone 1 Name
    Z2KIT,                   !- Zone 2 Name
    Z3ENT,                   !- Zone 3 Name
    Z4TOI,                   !- Zone 4 Name
    Z5BAT,                   !- Zone 5 Name
    Z6BSW,                   !- Zone 6 Name
    Z7BNW,                   !- Zone 7 Name
    Z8BN,                    !- Zone 8 Name
    Z9COR;                   !- Zone 9 Name

ZoneList,
    Kids Bedrooms,           !- Name
    Z8BN,                    !- Zone 1 Name
    Z6BSW;                   !- Zone 2 Name

Schedule:Compact,
    Work Eff Sch,            !- Name
    Any Number,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00, 0.0;       !- Field 4

Schedule:Compact,
    Clothing Sch,            !- Name
    Any Number,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 07:00, 2,         !- Field 4
    Until: 21:00, 1,         !- Field 6
    Until: 24:00, 2;         !- Field 8

Schedule:Compact,
    Air Velo Sch,            !- Name
    Any Number,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00, .2;        !- Field 4

Output:Diagnostics,
    DisplayExtraWarnings;    !- Key 1

Construction:FfactorGroundFloor,
    Ground1,                 !- Name
    0.6,                     !- F-Factor {W/m-K}
    91.1,                    !- Area {m2}
    43.8;                    !- PerimeterExposed {m}

SurfaceConvectionAlgorithm:Inside,TARP;
SurfaceConvectionAlgorithm:Outside,DOE-2;
Site:GroundTemperature:BuildingSurface,18,18,18,18,18,18,18,18,18,18,18,18;
Output:Surfaces:Drawing,DXF;

Material,
    Comp 90mm R2.2 14.4%,    !- Name
    MediumSmooth,            !- Roughness
    0.09,                    !- Thickness {m}
    0.052,                   !- Conductivity {W/m-K}
    73.79,                   !- Density {kg/m3}
    964,                     !- Specific Heat {J/kg-K}
    0.9,                     !- Thermal Absorptance
    0.7;                     !- Solar Absorptance

Material,
    Particle Board HD NZS4214,  !- Name
    MediumRough,             !- Roughness
    0.02,                    !- Thickness {m}
    0.14,                    !- Conductivity {W/m-K}
    700,                     !- Density {kg/m3}
    1700,                    !- Specific Heat {J/kg-K}
    0.9,                     !- Thermal Absorptance
    0.7;                     !- Solar Absorptance

Material:AirGap,
    18mm ventilated,         !- Name
    0.097;                   !- Thermal Resistance {m2-K/W}

Construction,
    Exterior Door,           !- Name
    Wood 1inch;              !- Outside Layer

WindowMaterial:Glazing,
    Stratobel sunergy 33.1,  !- Name
    SpectralAverage,         !- Optical Data Type
    ,                        !- Window Glass Spectral Data Set Name
    0.006218,                !- Thickness {m}
    0.495,                   !- Solar Transmittance at Normal Incidence
    0.084,                   !- Front Side Solar Reflectance at Normal Incidence
    0.103,                   !- Back Side Solar Reflectance at Normal Incidence
    0.674,                   !- Visible Transmittance at Normal Incidence
    0.084,                   !- Front Side Visible Reflectance at Normal Incidence
    0.103,                   !- Back Side Visible Reflectance at Normal Incidence
    0,                       !- Infrared Transmittance at Normal Incidence
    0.84,                    !- Front Side Infrared Hemispherical Emissivity
    0.279,                   !- Back Side Infrared Hemispherical Emissivity
    0.814,                   !- Conductivity {W/m-K}
    1,                       !- Dirt Correction Factor for Solar and Visible Transmittance
    No;                      !- Solar Diffusing

Material,
    Gypsum Board 10mm NZS4214,  !- Name
    MediumSmooth,            !- Roughness
    0.01,                    !- Thickness {m}
    0.22,                    !- Conductivity {W/m-K}
    800,                     !- Density {kg/m3}
    1090,                    !- Specific Heat {J/kg-K}
    0.9,                     !- Thermal Absorptance
    0.7,                     !- Solar Absorptance
    0.7;                     !- Visible Absorptance

Building,
    NMH,                     !- Name
    -0,                      !- North Axis {deg}
    Suburbs,                 !- Terrain
    0.001,                   !- Loads Convergence Tolerance Value
    0.005,                   !- Temperature Convergence Tolerance Value {deltaC}
    FullExterior,            !- Solar Distribution
    25,                      !- Maximum Number of Warmup Days
    6;                       !- Minimum Number of Warmup Days

Timestep,1;

SimulationControl,
    No,                      !- Do Zone Sizing Calculation
    No,                      !- Do System Sizing Calculation
    No,                      !- Do Plant Sizing Calculation
    No,                      !- Run Simulation for Sizing Periods
    Yes;                     !- Run Simulation for Weather File Run Periods

Material:AirGap,
    F04 Wall air space resistance,  !- Name
    0.15;                    !- Thermal Resistance {m2-K/W}

Material:AirGap,
    F05 Ceiling air space resistance,  !- Name
    0.18;                    !- Thermal Resistance {m2-K/W}

WindowMaterial:Gas,
    Air 13mm,                !- Name
    Air,                     !- Gas Type
    0.0127;                  !- Thickness {m}

Construction,
    Exterior Floor,          !- Name
    PS 2cm,                  !- Outside Layer
    Concrete 80mm heavyweight;  !- Layer 2

Construction,
    Exterior Wall,           !- Name
    Fibre cement NZS 4214,   !- Outside Layer
    18mm ventilated,         !- Layer 2
    Comp 90mm R2.2 14.4%,    !- Layer 3
    Gypsum Board 13mm NZS4214;  !- Layer 4

Construction,
    Interior Wall,           !- Name
    Gypsum Board 10mm NZS4214,  !- Outside Layer
    F04 Wall air space resistance,  !- Layer 2
    Gypsum Board 10mm NZS4214;  !- Layer 3

Construction,
    Exterior Roof,           !- Name
    Coloured zincalume roofing;  !- Outside Layer

Construction,
    Exterior Window,         !- Name
    Stratobel sunergy 33.1;  !- Outside Layer

Construction,
    Interior Door,           !- Name
    Wood 1inch;              !- Outside Layer

ScheduleTypeLimits,
    Any Number;              !- Name

ScheduleTypeLimits,
    Fraction,                !- Name
    0.0,                     !- Lower Limit Value
    1.0,                     !- Upper Limit Value
    CONTINUOUS;              !- Numeric Type

ScheduleTypeLimits,
    Temperature,             !- Name
    -60,                     !- Lower Limit Value
    200,                     !- Upper Limit Value
    CONTINUOUS;              !- Numeric Type

ScheduleTypeLimits,
    On/Off,                  !- Name
    0,                       !- Lower Limit Value
    1,                       !- Upper Limit Value
    DISCRETE;                !- Numeric Type

ScheduleTypeLimits,
    Control Type,            !- Name
    0,                       !- Lower Limit Value
    4,                       !- Upper Limit Value
    DISCRETE;                !- Numeric Type

ScheduleTypeLimits,
    Humidity,                !- Name
    10,                      !- Lower Limit Value
    90,                      !- Upper Limit Value
    CONTINUOUS;              !- Numeric Type

ScheduleTypeLimits,
    Number;                  !- Name

Output:VariableDictionary,regular;

Zone,
    Z5BAT,                   !- Name
    -0,                      !- Direction of Relative North {deg}
    4.2460079999999998, 0.63530500000000001, 0,
                                        !- X,Y,Z  {m}
    ,                        !- Type
    1,                       !- Multiplier
    ,                        !- Ceiling Height {m}
    ,                        !- Volume {m3}
    ,                        !- Floor Area {m2}
    ,                        !- Zone Inside Convection Algorithm
    ,                        !- Zone Outside Convection Algorithm
    Yes;                     !- Part of Total Floor Area

BuildingSurface:Detailed,
    5Int4,                   !- Name
    WALL,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z5BAT,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    4Int5,                   !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    5.750000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    5.750000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    5.750000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    5.750000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    5Int9,                   !- Name
    WALL,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z5BAT,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    9Int5,                   !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    5.750000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    5.750000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    3.760000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    3.760000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    5Int6WN,                 !- Name
    WALL,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z5BAT,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    6Int5EN,                 !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    3.760000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    3.760000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    3.760000000000, 0.760000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    3.760000000000, 0.760000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    5Int6N,                  !- Name
    WALL,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z5BAT,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    6Int5S,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    3.760000000000, 0.760000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    3.760000000000, 0.760000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    3.150000000000, 0.760000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    3.150000000000, 0.760000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    5Ceiling,                !- Name
    CEILING,                 !- Surface Type
    Exterior Ceiling,        !- Construction Name
    Z5BAT,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    Attic5,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    6,                       !- Number of Vertices
    3.760000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    3.760000000000, 0.760000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    3.150000000000, 0.760000000000, 2.400000000000,
                                        !- X,Y,Z  3 {m}
    3.150000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  4 {m}
    5.750000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  5 {m}
    5.750000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  6 {m}

BuildingSurface:Detailed,
    5ExS,                    !- Name
    WALL,                    !- Surface Type
    Exterior Wall,           !- Construction Name
    Z5BAT,                   !- Zone Name
    OUTDOORS,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    3.150000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    3.150000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    5.750000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    5.750000000000, 0.000000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    5Int6WS,                 !- Name
    WALL,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z5BAT,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    6Int5ES,                 !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    3.150000000000, 0.760000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    3.150000000000, 0.760000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    3.150000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    3.150000000000, 0.000000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

Zone,
    Z4TOI,                   !- Name
    -0,                      !- Direction of Relative North {deg}
    6.5212580000000004, 0.53437500000000004, 0,
                                        !- X,Y,Z  {m}
    ,                        !- Type
    1,                       !- Multiplier
    ,                        !- Ceiling Height {m}
    ,                        !- Volume {m3}
    ,                        !- Floor Area {m2}
    ,                        !- Zone Inside Convection Algorithm
    ,                        !- Zone Outside Convection Algorithm
    Yes;                     !- Part of Total Floor Area

BuildingSurface:Detailed,
    4Floor,                  !- Name
    FLOOR,                   !- Surface Type
    Exterior Floor,          !- Construction Name
    Z4TOI,                   !- Zone Name
    GroundSlabPreprocessorCore,  !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    6.750000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  1 {m}
    6.750000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    5.750000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    5.750000000000, 1.740000000000, 0.000000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    4Int9,                   !- Name
    WALL,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z4TOI,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    9Int4,                   !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    6.750000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    6.750000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    5.750000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    5.750000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    4Ceiling,                !- Name
    CEILING,                 !- Surface Type
    Exterior Ceiling,        !- Construction Name
    Z4TOI,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    Attic4,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    5.750000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    5.750000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    6.750000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  3 {m}
    6.750000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    4Int3,                   !- Name
    WALL,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z4TOI,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    3Int4,                   !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    6.750000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    6.750000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    6.750000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    6.750000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    4ExS,                    !- Name
    WALL,                    !- Surface Type
    Exterior Wall,           !- Construction Name
    Z4TOI,                   !- Zone Name
    OUTDOORS,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    5.750000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    5.750000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    6.750000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    6.750000000000, 0.000000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    4Int5,                   !- Name
    WALL,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z4TOI,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    5Int4,                   !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    5.750000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    5.750000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    5.750000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    5.750000000000, 0.000000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

Zone,
    Z3ENT,                   !- Name
    -0,                      !- Direction of Relative North {deg}
    8.0350509999999993, 0.63711300000000004, 0,
                                        !- X,Y,Z  {m}
    ,                        !- Type
    1,                       !- Multiplier
    ,                        !- Ceiling Height {m}
    ,                        !- Volume {m3}
    ,                        !- Floor Area {m2}
    ,                        !- Zone Inside Convection Algorithm
    ,                        !- Zone Outside Convection Algorithm
    Yes;                     !- Part of Total Floor Area

BuildingSurface:Detailed,
    3Floor,                  !- Name
    FLOOR,                   !- Surface Type
    Exterior Floor,          !- Construction Name
    Z3ENT,                   !- Zone Name
    GroundSlabPreprocessorCore,  !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    8.610000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  1 {m}
    8.610000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    6.750000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    6.750000000000, 1.740000000000, 0.000000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    3Ceiling,                !- Name
    Ceiling,                 !- Surface Type
    Exterior Ceiling,        !- Construction Name
    Z3ENT,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    Attic3,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0.0,                     !- View Factor to Ground
    4,                       !- Number of Vertices
    6.750000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    6.750000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    8.610000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  3 {m}
    8.610000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    3Int2,                   !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z3ENT,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    2Int3,                   !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    8.610000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    8.610000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    8.610000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    8.610000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    3Int1,                   !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z3ENT,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    1Int3,                   !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    8.610000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    8.610000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    7.640000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    7.640000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    3Int4,                   !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z3ENT,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    4Int3,                   !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    6.750000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    6.750000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    6.750000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    6.750000000000, 0.000000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    3ExS,                    !- Name
    Wall,                    !- Surface Type
    Exterior Wall,           !- Construction Name
    Z3ENT,                   !- Zone Name
    OUTDOORS,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    6.750000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    6.750000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    8.610000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    8.610000000000, 0.000000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    EntranceDoorS,           !- Name
    DOOR,                    !- Surface Type
    Exterior Door,           !- Construction Name
    3ExS,                    !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    ,                        !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    7.700000000000, 0.000000000000, 1.980000000000,
                                        !- X,Y,Z  1 {m}
    7.700000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    8.460000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    8.460000000000, 0.000000000000, 1.980000000000;
                                        !- X,Y,Z  4 {m}

Zone,
    Z2KIT,                   !- Name
    -0,                      !- Direction of Relative North {deg}
    11.230407, 1.069831, 0,             !- X,Y,Z  {m}
    ,                        !- Type
    1,                       !- Multiplier
    ,                        !- Ceiling Height {m}
    ,                        !- Volume {m3}
    ,                        !- Floor Area {m2}
    ,                        !- Zone Inside Convection Algorithm
    ,                        !- Zone Outside Convection Algorithm
    Yes;                     !- Part of Total Floor Area

BuildingSurface:Detailed,
    2Floor,                  !- Name
    Floor,                   !- Surface Type
    Exterior Floor,          !- Construction Name
    Z2KIT,                   !- Zone Name
    GroundSlabPreprocessorCore,  !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    11.660000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  1 {m}
    11.660000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    8.610000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    8.610000000000, 1.740000000000, 0.000000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    2ExS,                    !- Name
    WALL,                    !- Surface Type
    Exterior Wall,           !- Construction Name
    Z2KIT,                   !- Zone Name
    OUTDOORS,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    8.610000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    8.610000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    11.660000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    11.660000000000, 0.000000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    2Ceiling,                !- Name
    Ceiling,                 !- Surface Type
    Exterior Ceiling,        !- Construction Name
    Z2KIT,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    Attic2,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    8.610000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    8.610000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    11.660000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  3 {m}
    11.660000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    2Int3,                   !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z2KIT,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    3Int2,                   !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    8.610000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    8.610000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    8.610000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    8.610000000000, 0.000000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    2Int1N,                  !- Name
    WALL,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z2KIT,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    1Int2S,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    11.660000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    11.660000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    8.610000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    8.610000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    2Int1E,                  !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z2KIT,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    1Int2W,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    11.660000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    11.660000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    11.660000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    11.660000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    2S,                      !- Name
    WINDOW,                  !- Surface Type
    Exterior Window,         !- Construction Name
    2ExS,                    !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    AluFrame,                !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    9.470000000000, 0.000000000000, 2.200000000000,
                                        !- X,Y,Z  1 {m}
    9.470000000000, 0.000000000000, 0.900000000000,
                                        !- X,Y,Z  2 {m}
    10.110000000000, 0.000000000000, 0.900000000000,
                                        !- X,Y,Z  3 {m}
    10.110000000000, 0.000000000000, 2.200000000000;
                                        !- X,Y,Z  4 {m}

Zone,
    Z9COR,                   !- Name
    -0,                      !- Direction of Relative North {deg}
    9.0645729999999993, 8.5105260000000005, 0,
                                        !- X,Y,Z  {m}
    ,                        !- Type
    1,                       !- Multiplier
    ,                        !- Ceiling Height {m}
    ,                        !- Volume {m3}
    ,                        !- Floor Area {m2}
    ,                        !- Zone Inside Convection Algorithm
    ,                        !- Zone Outside Convection Algorithm
    Yes;                     !- Part of Total Floor Area

BuildingSurface:Detailed,
    9Int1,                   !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z9COR,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    1Int9,                   !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    7.640000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    7.640000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    7.640000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    7.640000000000, 3.550000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    9Int6W,                  !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z9COR,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    6Int9E,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    3.150000000000, 2.850000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    3.150000000000, 2.850000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    3.150000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    3.150000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    9Int7NW,                 !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z9COR,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    7Int9NW,                 !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    4.050000000000, 2.850000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    4.050000000000, 2.850000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    3.150000000000, 2.850000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    3.150000000000, 2.850000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    9Int7NE,                 !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z9COR,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    7Int9S,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    4.750000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    4.750000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    4.050000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    4.050000000000, 3.550000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    9Int7W,                  !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z9COR,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    7Int9W,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    4.050000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    4.050000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    4.050000000000, 2.850000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    4.050000000000, 2.850000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    9Int8NE,                 !- Name
    WALL,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z9COR,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    8Int9SW,                 !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    7.640000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    7.640000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    6.250000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    6.250000000000, 3.550000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    9Int6S,                  !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z9COR,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    6Int9N,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    3.150000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    3.150000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    3.760000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    3.760000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    9Int8W,                  !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z9COR,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    8Int9E,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    6.250000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    6.250000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    6.250000000000, 2.860000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    6.250000000000, 2.860000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    9Int8NW,                 !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z9COR,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    8Int9SE,                 !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    6.250000000000, 2.860000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    6.250000000000, 2.860000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    4.750000000000, 2.860000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    4.750000000000, 2.860000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    9Int8E,                  !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z9COR,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    8Int9W,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    4.750000000000, 2.860000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    4.750000000000, 2.860000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    4.750000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    4.750000000000, 3.550000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    9Ceiling,                !- Name
    Ceiling,                 !- Surface Type
    Exterior Ceiling,        !- Construction Name
    Z9COR,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    Attic9,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    10,                      !- Number of Vertices
    3.150000000000, 2.850000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    3.150000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    7.640000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  3 {m}
    7.640000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  4 {m}
    6.250000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  5 {m}
    6.250000000000, 2.860000000000, 2.400000000000,
                                        !- X,Y,Z  6 {m}
    4.750000000000, 2.860000000000, 2.400000000000,
                                        !- X,Y,Z  7 {m}
    4.750000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  8 {m}
    4.050000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  9 {m}
    4.050000000000, 2.850000000000, 2.400000000000;
                                        !- X,Y,Z  10 {m}

Zone,
    Z7BNW,                   !- Name
    -0,                      !- Direction of Relative North {deg}
    4.0559849999999997, 8.661683, 0,    !- X,Y,Z  {m}
    ,                        !- Type
    1,                       !- Multiplier
    ,                        !- Ceiling Height {m}
    ,                        !- Volume {m3}
    ,                        !- Floor Area {m2}
    ,                        !- Zone Inside Convection Algorithm
    ,                        !- Zone Outside Convection Algorithm
    Yes;                     !- Part of Total Floor Area

BuildingSurface:Detailed,
    7Int6,                   !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z7BNW,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    6Int7,                   !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    0.000000000000, 2.850000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    0.000000000000, 2.850000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    3.150000000000, 2.850000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    3.150000000000, 2.850000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    7Int9S,                  !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z7BNW,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    9Int7NE,                 !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    4.050000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    4.050000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    4.750000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    4.750000000000, 3.550000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    7ExN,                    !- Name
    Wall,                    !- Surface Type
    Exterior Wall,           !- Construction Name
    Z7BNW,                   !- Zone Name
    OUTDOORS,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    4.050000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    4.050000000000, 6.600000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    0.000000000000, 6.600000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    0.000000000000, 6.600000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    7Int9W,                  !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z7BNW,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    9Int7W,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    4.050000000000, 2.850000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    4.050000000000, 2.850000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    4.050000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    4.050000000000, 3.550000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    7Int8WS,                 !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z7BNW,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    8Int7WS,                 !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    4.750000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    4.750000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    4.750000000000, 5.450000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    4.750000000000, 5.450000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    7Ceiling,                !- Name
    Ceiling,                 !- Surface Type
    Exterior Ceiling,        !- Construction Name
    Z7BNW,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    Attic7,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    8,                       !- Number of Vertices
    0.000000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    0.000000000000, 2.850000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    4.050000000000, 2.850000000000, 2.400000000000,
                                        !- X,Y,Z  3 {m}
    4.050000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  4 {m}
    4.750000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  5 {m}
    4.750000000000, 5.450000000000, 2.400000000000,
                                        !- X,Y,Z  6 {m}
    4.050000000000, 5.450000000000, 2.400000000000,
                                        !- X,Y,Z  7 {m}
    4.050000000000, 6.600000000000, 2.400000000000;
                                        !- X,Y,Z  8 {m}

BuildingSurface:Detailed,
    7ExW,                    !- Name
    Wall,                    !- Surface Type
    Exterior Wall,           !- Construction Name
    Z7BNW,                   !- Zone Name
    OUTDOORS,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    0.000000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    0.000000000000, 6.600000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    0.000000000000, 2.850000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    0.000000000000, 2.850000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    7Int8EN,                 !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z7BNW,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    8Int7WN,                 !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    4.050000000000, 5.450000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    4.050000000000, 5.450000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    4.050000000000, 6.600000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    4.050000000000, 6.600000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    7Int8N,                  !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z7BNW,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    8Int7S,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    4.750000000000, 5.450000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    4.750000000000, 5.450000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    4.050000000000, 5.450000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    4.050000000000, 5.450000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    7W,                      !- Name
    WINDOW,                  !- Surface Type
    Exterior Window,         !- Construction Name
    7ExW,                    !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    AluFrame,                !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    0.000000000000, 5.340000000000, 2.200000000000,
                                        !- X,Y,Z  1 {m}
    0.000000000000, 5.340000000000, 0.540000000000,
                                        !- X,Y,Z  2 {m}
    0.000000000000, 4.700000000000, 0.540000000000,
                                        !- X,Y,Z  3 {m}
    0.000000000000, 4.700000000000, 2.200000000000;
                                        !- X,Y,Z  4 {m}

Zone,
    Z8BN,                    !- Name
    -0,                      !- Direction of Relative North {deg}
    7.8639239999999999, 8.7680969999999991, 0,
                                        !- X,Y,Z  {m}
    ,                        !- Type
    1,                       !- Multiplier
    ,                        !- Ceiling Height {m}
    ,                        !- Volume {m3}
    ,                        !- Floor Area {m2}
    ,                        !- Zone Inside Convection Algorithm
    ,                        !- Zone Outside Convection Algorithm
    Yes;                     !- Part of Total Floor Area

BuildingSurface:Detailed,
    8ExN,                    !- Name
    Wall,                    !- Surface Type
    Exterior Wall,           !- Construction Name
    Z8BN,                    !- Zone Name
    OUTDOORS,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    7.640000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    7.640000000000, 6.600000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    4.050000000000, 6.600000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    4.050000000000, 6.600000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    8Ceiling,                !- Name
    CEILING,                 !- Surface Type
    Exterior Ceiling,        !- Construction Name
    Z8BN,                    !- Zone Name
    Surface,                 !- Outside Boundary Condition
    Attic8,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    8,                       !- Number of Vertices
    4.050000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    4.050000000000, 5.450000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    4.750000000000, 5.450000000000, 2.400000000000,
                                        !- X,Y,Z  3 {m}
    4.750000000000, 2.860000000000, 2.400000000000,
                                        !- X,Y,Z  4 {m}
    6.250000000000, 2.860000000000, 2.400000000000,
                                        !- X,Y,Z  5 {m}
    6.250000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  6 {m}
    7.640000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  7 {m}
    7.640000000000, 6.600000000000, 2.400000000000;
                                        !- X,Y,Z  8 {m}

BuildingSurface:Detailed,
    8Int7WN,                 !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z8BN,                    !- Zone Name
    Surface,                 !- Outside Boundary Condition
    7Int8EN,                 !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    4.050000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    4.050000000000, 6.600000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    4.050000000000, 5.450000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    4.050000000000, 5.450000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    8Int1,                   !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z8BN,                    !- Zone Name
    Surface,                 !- Outside Boundary Condition
    1Int8,                   !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    7.640000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    7.640000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    7.640000000000, 6.600000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    7.640000000000, 6.600000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    8Int7S,                  !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z8BN,                    !- Zone Name
    Surface,                 !- Outside Boundary Condition
    7Int8N,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    4.050000000000, 5.450000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    4.050000000000, 5.450000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    4.750000000000, 5.450000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    4.750000000000, 5.450000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    8Int9SE,                 !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z8BN,                    !- Zone Name
    Surface,                 !- Outside Boundary Condition
    9Int8NW,                 !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    4.750000000000, 2.860000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    4.750000000000, 2.860000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    6.250000000000, 2.860000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    6.250000000000, 2.860000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    8Int9SW,                 !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z8BN,                    !- Zone Name
    Surface,                 !- Outside Boundary Condition
    9Int8NE,                 !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    6.250000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    6.250000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    7.640000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    7.640000000000, 3.550000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    8Int7WS,                 !- Name
    WALL,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z8BN,                    !- Zone Name
    Surface,                 !- Outside Boundary Condition
    7Int8WS,                 !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    4.750000000000, 5.450000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    4.750000000000, 5.450000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    4.750000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    4.750000000000, 3.550000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    8Int9E,                  !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z8BN,                    !- Zone Name
    Surface,                 !- Outside Boundary Condition
    9Int8W,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    6.250000000000, 2.860000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    6.250000000000, 2.860000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    6.250000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    6.250000000000, 3.550000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    8N,                      !- Name
    WINDOW,                  !- Surface Type
    Exterior Window,         !- Construction Name
    8ExN,                    !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    AluFrame,                !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    7.080000000000, 6.600000000000, 2.200000000000,
                                        !- X,Y,Z  1 {m}
    7.080000000000, 6.600000000000, 0.700000000000,
                                        !- X,Y,Z  2 {m}
    6.510000000000, 6.600000000000, 0.700000000000,
                                        !- X,Y,Z  3 {m}
    6.510000000000, 6.600000000000, 2.200000000000;
                                        !- X,Y,Z  4 {m}

Zone,
    Z1LIV,                   !- Name
    -0,                      !- Direction of Relative North {deg}
    13.320711000000001, 10.271779, 0,   !- X,Y,Z  {m}
    ,                        !- Type
    1,                       !- Multiplier
    ,                        !- Ceiling Height {m}
    ,                        !- Volume {m3}
    ,                        !- Floor Area {m2}
    ,                        !- Zone Inside Convection Algorithm
    ,                        !- Zone Outside Convection Algorithm
    Yes;                     !- Part of Total Floor Area

BuildingSurface:Detailed,
    1ExNW,                   !- Name
    Wall,                    !- Surface Type
    Exterior Wall,           !- Construction Name
    Z1LIV,                   !- Zone Name
    OUTDOORS,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    10.900000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    10.900000000000, 6.600000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    7.640000000000, 6.600000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    7.640000000000, 6.600000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    1ExS,                    !- Name
    WALL,                    !- Surface Type
    Exterior Wall,           !- Construction Name
    Z1LIV,                   !- Zone Name
    OUTDOORS,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    11.660000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    11.660000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    14.500000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    14.500000000000, 0.000000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    1Int2W,                  !- Name
    WALL,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z1LIV,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    2Int1E,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    11.660000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    11.660000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    11.660000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    11.660000000000, 0.000000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    1Int2S,                  !- Name
    WALL,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z1LIV,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    2Int1N,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    8.610000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    8.610000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    11.660000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    11.660000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    1NW,                     !- Name
    WINDOW,                  !- Surface Type
    Exterior Window,         !- Construction Name
    1ExNW,                   !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    AluFrame,                !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    10.100000000000, 6.600000000000, 2.200000000000,
                                        !- X,Y,Z  1 {m}
    10.100000000000, 6.600000000000, 0.120000000000,
                                        !- X,Y,Z  2 {m}
    8.600000000000, 6.600000000000, 0.120000000000,
                                        !- X,Y,Z  3 {m}
    8.600000000000, 6.600000000000, 2.200000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    1W,                      !- Name
    WINDOW,                  !- Surface Type
    Exterior Window,         !- Construction Name
    1ExW,                    !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    AluFrame,                !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    10.900000000000, 7.550000000000, 2.200000000000,
                                        !- X,Y,Z  1 {m}
    10.900000000000, 7.550000000000, 0.550000000000,
                                        !- X,Y,Z  2 {m}
    10.900000000000, 6.850000000000, 0.550000000000,
                                        !- X,Y,Z  3 {m}
    10.900000000000, 6.850000000000, 2.200000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    1S,                      !- Name
    WINDOW,                  !- Surface Type
    Exterior Window,         !- Construction Name
    1ExS,                    !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    AluFrame,                !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    11.960000000000, 0.000000000000, 2.200000000000,
                                        !- X,Y,Z  1 {m}
    11.960000000000, 0.000000000000, 0.500000000000,
                                        !- X,Y,Z  2 {m}
    13.260000000000, 0.000000000000, 0.500000000000,
                                        !- X,Y,Z  3 {m}
    13.260000000000, 0.000000000000, 2.200000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    Door9to1,                !- Name
    DOOR,                    !- Surface Type
    Interior Door,           !- Construction Name
    9Int1,                   !- Building Surface Name
    Door1to9,                !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    ,                        !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    7.640000000000, 1.890000000000, 1.980000000000,
                                        !- X,Y,Z  1 {m}
    7.640000000000, 1.890000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    7.640000000000, 2.700000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    7.640000000000, 2.700000000000, 1.980000000000;
                                        !- X,Y,Z  4 {m}

! Name
! Surface Type
! Construction Name
! Building Surface Name
! Outside Boundary Condition Object
! View Factor to Ground
! Shading Control Name
! Frame and Divider Name
! Multiplier
! Number of Vertices
FenestrationSurface:Detailed,
    Door1to9,                !- Name
    DOOR,                    !- Surface Type
    Interior Door,           !- Construction Name
    1Int9,                   !- Building Surface Name
    Door9to1,                !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    ,                        !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    7.640000000000, 2.700000000000, 1.980000000000,
                                        !- X,Y,Z  1 {m}
    7.640000000000, 2.700000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    7.640000000000, 1.890000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    7.640000000000, 1.890000000000, 1.980000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    Door3to1,                !- Name
    Door,                    !- Surface Type
    Interior Door,           !- Construction Name
    3Int1,                   !- Building Surface Name
    Door1to3,                !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    ,                        !- Frame and Divider Name
    1.0,                     !- Multiplier
    4,                       !- Number of Vertices
    8.530000000000, 1.740000000000, 1.980000000000,
                                        !- X,Y,Z  1 {m}
    8.530000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    7.720000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    7.720000000000, 1.740000000000, 1.980000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    Door1to3,                !- Name
    Door,                    !- Surface Type
    Interior Door,           !- Construction Name
    1Int3,                   !- Building Surface Name
    Door3to1,                !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    ,                        !- Frame and Divider Name
    1.0,                     !- Multiplier
    4,                       !- Number of Vertices
    7.720000000000, 1.740000000000, 1.980000000000,
                                        !- X,Y,Z  1 {m}
    7.720000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    8.530000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    8.530000000000, 1.740000000000, 1.980000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    Door9to4,                !- Name
    Door,                    !- Surface Type
    Interior Door,           !- Construction Name
    9Int4,                   !- Building Surface Name
    Door4to9,                !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    ,                        !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    5.940000000000, 1.740000000000, 1.980000000000,
                                        !- X,Y,Z  1 {m}
    5.940000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    6.600000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    6.600000000000, 1.740000000000, 1.980000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    Door4to9,                !- Name
    Door,                    !- Surface Type
    Interior Door,           !- Construction Name
    4Int9,                   !- Building Surface Name
    Door9to4,                !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    ,                        !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    6.600000000000, 1.740000000000, 1.980000000000,
                                        !- X,Y,Z  1 {m}
    6.600000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    5.940000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    5.940000000000, 1.740000000000, 1.980000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    Door9to5,                !- Name
    Door,                    !- Surface Type
    Interior Door,           !- Construction Name
    9Int5,                   !- Building Surface Name
    Door5to9,                !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    ,                        !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    4.270000000000, 1.740000000000, 1.980000000000,
                                        !- X,Y,Z  1 {m}
    4.270000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    4.930000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    4.930000000000, 1.740000000000, 1.980000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    Door5to9,                !- Name
    Door,                    !- Surface Type
    Interior Door,           !- Construction Name
    5Int9,                   !- Building Surface Name
    Door9to5,                !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    ,                        !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    4.930000000000, 1.740000000000, 1.980000000000,
                                        !- X,Y,Z  1 {m}
    4.930000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    4.270000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    4.270000000000, 1.740000000000, 1.980000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    Door9to6,                !- Name
    Door,                    !- Surface Type
    Interior Door,           !- Construction Name
    9Int6W,                  !- Building Surface Name
    Door6to9,                !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    ,                        !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    3.150000000000, 2.700000000000, 1.980000000000,
                                        !- X,Y,Z  1 {m}
    3.150000000000, 2.700000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    3.150000000000, 1.990000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    3.150000000000, 1.990000000000, 1.980000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    Door6to9,                !- Name
    Door,                    !- Surface Type
    Interior Door,           !- Construction Name
    6Int9E,                  !- Building Surface Name
    Door9to6,                !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    ,                        !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    3.150000000000, 1.990000000000, 1.980000000000,
                                        !- X,Y,Z  1 {m}
    3.150000000000, 1.990000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    3.150000000000, 2.700000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    3.150000000000, 2.700000000000, 1.980000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    Door9to7,                !- Name
    Door,                    !- Surface Type
    Interior Door,           !- Construction Name
    9Int7NW,                 !- Building Surface Name
    Door7to9,                !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    ,                        !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    3.900000000000, 2.850000000000, 1.980000000000,
                                        !- X,Y,Z  1 {m}
    3.900000000000, 2.850000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    3.190000000000, 2.850000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    3.190000000000, 2.850000000000, 1.980000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    Door7to9,                !- Name
    Door,                    !- Surface Type
    Interior Door,           !- Construction Name
    7Int9NW,                 !- Building Surface Name
    Door9to7,                !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    ,                        !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    3.190000000000, 2.850000000000, 1.980000000000,
                                        !- X,Y,Z  1 {m}
    3.190000000000, 2.850000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    3.900000000000, 2.850000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    3.900000000000, 2.850000000000, 1.980000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    Door9to8,                !- Name
    Door,                    !- Surface Type
    Interior Door,           !- Construction Name
    9Int8NW,                 !- Building Surface Name
    Door8to9,                !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    ,                        !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    5.610000000000, 2.860000000000, 1.980000000000,
                                        !- X,Y,Z  1 {m}
    5.610000000000, 2.860000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    4.900000000000, 2.860000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    4.900000000000, 2.860000000000, 1.980000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    Door8to9,                !- Name
    DOOR,                    !- Surface Type
    Interior Door,           !- Construction Name
    8Int9SE,                 !- Building Surface Name
    Door9to8,                !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    ,                        !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    4.900000000000, 2.860000000000, 1.980000000000,
                                        !- X,Y,Z  1 {m}
    4.900000000000, 2.860000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    5.610000000000, 2.860000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    5.610000000000, 2.860000000000, 1.980000000000;
                                        !- X,Y,Z  4 {m}

Zone,
    Z6BSW,                   !- Name
    -0,                      !- Direction of Relative North {deg}
    0.82150400000000001, -0.46749500000000005, 0,
                                        !- X,Y,Z  {m}
    ,                        !- Type
    1,                       !- Multiplier
    ,                        !- Ceiling Height {m}
    ,                        !- Volume {m3}
    ,                        !- Floor Area {m2}
    ,                        !- Zone Inside Convection Algorithm
    ,                        !- Zone Outside Convection Algorithm
    Yes;                     !- Part of Total Floor Area

BuildingSurface:Detailed,
    6Int9N,                  !- Name
    WALL,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z6BSW,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    9Int6S,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    3.760000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    3.760000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    3.150000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    3.150000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    6ExS,                    !- Name
    WALL,                    !- Surface Type
    Exterior Wall,           !- Construction Name
    Z6BSW,                   !- Zone Name
    OUTDOORS,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    0.000000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    0.000000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    3.150000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    3.150000000000, 0.000000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    6ExW,                    !- Name
    WALL,                    !- Surface Type
    Exterior Wall,           !- Construction Name
    Z6BSW,                   !- Zone Name
    OUTDOORS,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    0.000000000000, 2.850000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    0.000000000000, 2.850000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    0.000000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    0.000000000000, 0.000000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    6Int7,                   !- Name
    WALL,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z6BSW,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    7Int6,                   !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    3.150000000000, 2.850000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    3.150000000000, 2.850000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    0.000000000000, 2.850000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    0.000000000000, 2.850000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    6Int5ES,                 !- Name
    WALL,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z6BSW,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    5Int6WS,                 !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    3.150000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    3.150000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    3.150000000000, 0.760000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    3.150000000000, 0.760000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    6Ceiling,                !- Name
    CEILING,                 !- Surface Type
    Exterior Ceiling,        !- Construction Name
    Z6BSW,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    Attic6,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    8,                       !- Number of Vertices
    0.000000000000, 2.850000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    0.000000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    3.150000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  3 {m}
    3.150000000000, 0.760000000000, 2.400000000000,
                                        !- X,Y,Z  4 {m}
    3.760000000000, 0.760000000000, 2.400000000000,
                                        !- X,Y,Z  5 {m}
    3.760000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  6 {m}
    3.150000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  7 {m}
    3.150000000000, 2.850000000000, 2.400000000000;
                                        !- X,Y,Z  8 {m}

BuildingSurface:Detailed,
    6Int5S,                  !- Name
    WALL,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z6BSW,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    5Int6N,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    3.150000000000, 0.760000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    3.150000000000, 0.760000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    3.760000000000, 0.760000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    3.760000000000, 0.760000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    6Int9E,                  !- Name
    WALL,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z6BSW,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    9Int6W,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    3.150000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    3.150000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    3.150000000000, 2.850000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    3.150000000000, 2.850000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

! Name
Zone,
    Attic,                   !- Name
    -0,                      !- Direction of Relative North {deg}
    12.796792959338672, 3.4337442792584452, 2.4,
                                        !- X,Y,Z  {m}
    ,                        !- Type
    1,                       !- Multiplier
    ,                        !- Ceiling Height {m}
    ,                        !- Volume {m3}
    ,                        !- Floor Area {m2}
    ,                        !- Zone Inside Convection Algorithm
    ,                        !- Zone Outside Convection Algorithm
    No;                      !- Part of Total Floor Area

! Name
! Surface Type
! Construction Name
! Zone Name
! Outside Boundary Condition
! Outside Boundary Condition Object
! Sun Exposure
! Wind Exposure
! View Factor to Ground
! Number of Vertices
BuildingSurface:Detailed,
    Roof1NE,                 !- Name
    Roof,                    !- Surface Type
    Exterior Roof,           !- Construction Name
    Attic,                   !- Zone Name
    OUTDOORS,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    3,                       !- Number of Vertices
    14.500000000000, 3.300000000000, 3.500000000000,
                                        !- X,Y,Z  1 {m}
    14.500000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    11.050000000000, 3.300000000000, 3.500000000000;
                                        !- X,Y,Z  3 {m}

! Name
! Surface Type
! Construction Name
! Zone Name
! Outside Boundary Condition
! Outside Boundary Condition Object
! Sun Exposure
! Wind Exposure
! View Factor to Ground
! Number of Vertices
BuildingSurface:Detailed,
    AtticE,                  !- Name
    Wall,                    !- Surface Type
    Wall Unconditioned,      !- Construction Name
    Attic,                   !- Zone Name
    Outdoors,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    3,                       !- Number of Vertices
    14.500000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    14.500000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    14.500000000000, 3.300000000000, 3.500000000000;
                                        !- X,Y,Z  3 {m}

! Name
! Surface Type
! Construction Name
! Zone Name
! Outside Boundary Condition
! Outside Boundary Condition Object
! Sun Exposure
! Wind Exposure
! View Factor to Ground
! Number of Vertices
BuildingSurface:Detailed,
    RoofS,                   !- Name
    Roof,                    !- Surface Type
    Exterior Roof,           !- Construction Name
    Attic,                   !- Zone Name
    OUTDOORS,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    0.000000000000, 3.300000000000, 3.500000000000,
                                        !- X,Y,Z  1 {m}
    0.000000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    14.500000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  3 {m}
    14.500000000000, 3.300000000000, 3.500000000000;
                                        !- X,Y,Z  4 {m}

! Name
! Surface Type
! Construction Name
! Zone Name
! Outside Boundary Condition
! Outside Boundary Condition Object
! Sun Exposure
! Wind Exposure
! View Factor to Ground
! Number of Vertices
BuildingSurface:Detailed,
    1Int8,                   !- Name
    WALL,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z1LIV,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    8Int1,                   !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    7.640000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    7.640000000000, 6.600000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    7.640000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    7.640000000000, 3.550000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

! Name
Construction,
    Wall Unconditioned,      !- Name
    Fibre cement NZS 4214;   !- Outside Layer

! Name
Construction,
    Exterior Ceiling,        !- Name
    Comp 140mm R2.8 9.9%,    !- Outside Layer
    Gypsum Board 13mm NZS4214;  !- Layer 2

! Name
! Surface Type
! Construction Name
! Building Surface Name
! Outside Boundary Condition Object
! View Factor to Ground
! Shading Control Name
! Frame and Divider Name
! Multiplier
! Number of Vertices
FenestrationSurface:Detailed,
    4S,                      !- Name
    WINDOW,                  !- Surface Type
    Exterior Window,         !- Construction Name
    4ExS,                    !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    ,                        !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    5.900000000000, 0.000000000000, 2.200000000000,
                                        !- X,Y,Z  1 {m}
    5.900000000000, 0.000000000000, 0.900000000000,
                                        !- X,Y,Z  2 {m}
    6.590000000000, 0.000000000000, 0.900000000000,
                                        !- X,Y,Z  3 {m}
    6.590000000000, 0.000000000000, 2.200000000000;
                                        !- X,Y,Z  4 {m}

! Name
! Surface Type
! Construction Name
! Building Surface Name
! Outside Boundary Condition Object
! View Factor to Ground
! Shading Control Name
! Frame and Divider Name
! Multiplier
! Number of Vertices
FenestrationSurface:Detailed,
    7N,                      !- Name
    WINDOW,                  !- Surface Type
    Exterior Window,         !- Construction Name
    7ExN,                    !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    ,                        !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    2.860000000000, 6.600000000000, 2.200000000000,
                                        !- X,Y,Z  1 {m}
    2.860000000000, 6.600000000000, 0.700000000000,
                                        !- X,Y,Z  2 {m}
    1.110000000000, 6.600000000000, 0.700000000000,
                                        !- X,Y,Z  3 {m}
    1.110000000000, 6.600000000000, 2.200000000000;
                                        !- X,Y,Z  4 {m}

! Name
! Surface Type
! Construction Name
! Building Surface Name
! Outside Boundary Condition Object
! View Factor to Ground
! Shading Control Name
! Frame and Divider Name
! Multiplier
! Number of Vertices
FenestrationSurface:Detailed,
    Opening1to2S,            !- Name
    DOOR,                    !- Surface Type
    Interior Door,           !- Construction Name
    1Int2S,                  !- Building Surface Name
    Opening2to1N,            !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    ,                        !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    8.780000000000, 1.740000000000, 2.320000000000,
                                        !- X,Y,Z  1 {m}
    8.780000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    11.500000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    11.500000000000, 1.740000000000, 2.320000000000;
                                        !- X,Y,Z  4 {m}

! Name
! Surface Type
! Construction Name
! Building Surface Name
! Outside Boundary Condition Object
! View Factor to Ground
! Shading Control Name
! Frame and Divider Name
! Multiplier
! Number of Vertices
FenestrationSurface:Detailed,
    Opening2to1N,            !- Name
    DOOR,                    !- Surface Type
    Interior Door,           !- Construction Name
    2Int1N,                  !- Building Surface Name
    Opening1to2S,            !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    ,                        !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    11.500000000000, 1.740000000000, 2.320000000000,
                                        !- X,Y,Z  1 {m}
    11.500000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    8.780000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    8.780000000000, 1.740000000000, 2.320000000000;
                                        !- X,Y,Z  4 {m}

! Name
! Surface Type
! Construction Name
! Building Surface Name
! Outside Boundary Condition Object
! View Factor to Ground
! Shading Control Name
! Frame and Divider Name
! Multiplier
! Number of Vertices
FenestrationSurface:Detailed,
    Opening2to1E,            !- Name
    Door,                    !- Surface Type
    Interior Door,           !- Construction Name
    2Int1E,                  !- Building Surface Name
    Opening1to2W,            !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    ,                        !- Frame and Divider Name
    1.0,                     !- Multiplier
    4,                       !- Number of Vertices
    11.660000000000, 0.110000000000, 2.320000000000,
                                        !- X,Y,Z  1 {m}
    11.660000000000, 0.110000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    11.660000000000, 1.620000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    11.660000000000, 1.620000000000, 2.320000000000;
                                        !- X,Y,Z  4 {m}

! Name
! Surface Type
! Construction Name
! Building Surface Name
! Outside Boundary Condition Object
! View Factor to Ground
! Shading Control Name
! Frame and Divider Name
! Multiplier
! Number of Vertices
FenestrationSurface:Detailed,
    Opening1to2W,            !- Name
    DOOR,                    !- Surface Type
    Interior Door,           !- Construction Name
    1Int2W,                  !- Building Surface Name
    Opening2to1E,            !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    ,                        !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    11.660000000000, 1.620000000000, 2.320000000000,
                                        !- X,Y,Z  1 {m}
    11.660000000000, 1.620000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    11.660000000000, 0.110000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    11.660000000000, 0.110000000000, 2.320000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    8Int9W,                  !- Name
    WALL,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z8BN,                    !- Zone Name
    Surface,                 !- Outside Boundary Condition
    9Int8E,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    4.750000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    4.750000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    4.750000000000, 2.860000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    4.750000000000, 2.860000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

! Name
! Surface Type
! Construction Name
! Zone Name
! Outside Boundary Condition
! Outside Boundary Condition Object
! Sun Exposure
! Wind Exposure
! View Factor to Ground
! Number of Vertices
BuildingSurface:Detailed,
    1Int9,                   !- Name
    WALL,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z1LIV,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    9Int1,                   !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    7.640000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    7.640000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    7.640000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    7.640000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    3Int9,                   !- Name
    WALL,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z3ENT,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    9Int3,                   !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    7.640000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    7.640000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    6.750000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    6.750000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

! Name
! Surface Type
! Construction Name
! Zone Name
! Outside Boundary Condition
! Outside Boundary Condition Object
! Sun Exposure
! Wind Exposure
! View Factor to Ground
! Number of Vertices
BuildingSurface:Detailed,
    AtticW,                  !- Name
    WALL,                    !- Surface Type
    Wall Unconditioned,      !- Construction Name
    Attic,                   !- Zone Name
    OUTDOORS,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    3,                       !- Number of Vertices
    0.000000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    0.000000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    0.000000000000, 3.300000000000, 3.500000000000;
                                        !- X,Y,Z  3 {m}

! Name
! Surface Type
! Construction Name
! Zone Name
! Outside Boundary Condition
! Outside Boundary Condition Object
! Sun Exposure
! Wind Exposure
! View Factor to Ground
! Number of Vertices
BuildingSurface:Detailed,
    Attic4,                  !- Name
    FLOOR,                   !- Surface Type
    Attic Floor,             !- Construction Name
    Attic,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    4Ceiling,                !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    6.750000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    6.750000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    5.750000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  3 {m}
    5.750000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

! Name
! Surface Type
! Construction Name
! Zone Name
! Outside Boundary Condition
! Outside Boundary Condition Object
! Sun Exposure
! Wind Exposure
! View Factor to Ground
! Number of Vertices
BuildingSurface:Detailed,
    Attic6,                  !- Name
    FLOOR,                   !- Surface Type
    Attic Floor,             !- Construction Name
    Attic,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    6Ceiling,                !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    8,                       !- Number of Vertices
    3.150000000000, 2.850000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    3.150000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    3.760000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  3 {m}
    3.760000000000, 0.760000000000, 2.400000000000,
                                        !- X,Y,Z  4 {m}
    3.150000000000, 0.760000000000, 2.400000000000,
                                        !- X,Y,Z  5 {m}
    3.150000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  6 {m}
    0.000000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  7 {m}
    0.000000000000, 2.850000000000, 2.400000000000;
                                        !- X,Y,Z  8 {m}

! Name
! Surface Type
! Construction Name
! Zone Name
! Outside Boundary Condition
! Outside Boundary Condition Object
! Sun Exposure
! Wind Exposure
! View Factor to Ground
! Number of Vertices
BuildingSurface:Detailed,
    Attic2,                  !- Name
    Floor,                   !- Surface Type
    Attic Floor,             !- Construction Name
    Attic,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    2Ceiling,                !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0.0,                     !- View Factor to Ground
    4,                       !- Number of Vertices
    11.660000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    11.660000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    8.610000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  3 {m}
    8.610000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

! Name
! Surface Type
! Construction Name
! Zone Name
! Outside Boundary Condition
! Outside Boundary Condition Object
! Sun Exposure
! Wind Exposure
! View Factor to Ground
! Number of Vertices
BuildingSurface:Detailed,
    Attic5,                  !- Name
    FLOOR,                   !- Surface Type
    Attic Floor,             !- Construction Name
    Attic,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    5Ceiling,                !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    6,                       !- Number of Vertices
    5.750000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    5.750000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    3.150000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  3 {m}
    3.150000000000, 0.760000000000, 2.400000000000,
                                        !- X,Y,Z  4 {m}
    3.760000000000, 0.760000000000, 2.400000000000,
                                        !- X,Y,Z  5 {m}
    3.760000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  6 {m}

! Name
! Surface Type
! Construction Name
! Zone Name
! Outside Boundary Condition
! Outside Boundary Condition Object
! Sun Exposure
! Wind Exposure
! View Factor to Ground
! Number of Vertices
BuildingSurface:Detailed,
    Attic9,                  !- Name
    FLOOR,                   !- Surface Type
    Attic Floor,             !- Construction Name
    Attic,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    9Ceiling,                !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    10,                      !- Number of Vertices
    7.640000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    7.640000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    3.150000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  3 {m}
    3.150000000000, 2.850000000000, 2.400000000000,
                                        !- X,Y,Z  4 {m}
    4.050000000000, 2.850000000000, 2.400000000000,
                                        !- X,Y,Z  5 {m}
    4.050000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  6 {m}
    4.750000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  7 {m}
    4.750000000000, 2.860000000000, 2.400000000000,
                                        !- X,Y,Z  8 {m}
    6.250000000000, 2.860000000000, 2.400000000000,
                                        !- X,Y,Z  9 {m}
    6.250000000000, 3.550000000000, 2.400000000000;
                                        !- X,Y,Z  10 {m}

! Name
! Surface Type
! Construction Name
! Zone Name
! Outside Boundary Condition
! Outside Boundary Condition Object
! Sun Exposure
! Wind Exposure
! View Factor to Ground
! Number of Vertices
BuildingSurface:Detailed,
    Attic7,                  !- Name
    Floor,                   !- Surface Type
    Attic Floor,             !- Construction Name
    Attic,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    7Ceiling,                !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    8,                       !- Number of Vertices
    4.050000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    4.050000000000, 5.450000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    4.750000000000, 5.450000000000, 2.400000000000,
                                        !- X,Y,Z  3 {m}
    4.750000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  4 {m}
    4.050000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  5 {m}
    4.050000000000, 2.850000000000, 2.400000000000,
                                        !- X,Y,Z  6 {m}
    0.000000000000, 2.850000000000, 2.400000000000,
                                        !- X,Y,Z  7 {m}
    0.000000000000, 6.600000000000, 2.400000000000;
                                        !- X,Y,Z  8 {m}

BuildingSurface:Detailed,
    9Int5,                   !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z9COR,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    5Int9,                   !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    3.760000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    3.760000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    5.750000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    5.750000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    9Int3,                   !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z9COR,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    3Int9,                   !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    6.750000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    6.750000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    7.640000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    7.640000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    7Int9NW,                 !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z7BNW,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    9Int7NW,                 !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    3.150000000000, 2.850000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    3.150000000000, 2.850000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    4.050000000000, 2.850000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    4.050000000000, 2.850000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    9Int4,                   !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z9COR,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    4Int9,                   !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    5.750000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    5.750000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    6.750000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    6.750000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    1Int3,                   !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z1LIV,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    3Int1,                   !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    7.640000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    7.640000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    8.610000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    8.610000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

! Name
! Transmittance Schedule Name
! Number of Vertices
Shading:Building:Detailed,
    ShadeEN,                 !- Name
    ,                        !- Transmittance Schedule Name
    4,                       !- Number of Vertices
    14.500000000000, 8.200000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    14.880000000000, 8.200000000000, 2.280000000000,
                                        !- X,Y,Z  2 {m}
    14.880000000000, 6.960000000000, 2.280000000000,
                                        !- X,Y,Z  3 {m}
    14.500000000000, 6.600000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

! Name
! Transmittance Schedule Name
! Number of Vertices
Shading:Building:Detailed,
    Shade ES,                !- Name
    ,                        !- Transmittance Schedule Name
    4,                       !- Number of Vertices
    14.900000000000, 3.300000000000, 3.500000000000,
                                        !- X,Y,Z  1 {m}
    14.900000000000, -0.380000000000, 2.270000000000,
                                        !- X,Y,Z  2 {m}
    14.500000000000, -0.380000000000, 2.270000000000,
                                        !- X,Y,Z  3 {m}
    14.500000000000, 3.300000000000, 3.500000000000;
                                        !- X,Y,Z  4 {m}

! Name
! Transmittance Schedule Name
! Number of Vertices
Shading:Building:Detailed,
    ShadeWN,                 !- Name
    ,                        !- Transmittance Schedule Name
    4,                       !- Number of Vertices
    -0.400000000000, 3.300000000000, 3.500000000000,
                                        !- X,Y,Z  1 {m}
    -0.400000000000, 6.979473319220, 2.273508893593,
                                        !- X,Y,Z  2 {m}
    0.000000000000, 6.979473319220, 2.273508893593,
                                        !- X,Y,Z  3 {m}
    0.000000000000, 3.300000000000, 3.500000000000;
                                        !- X,Y,Z  4 {m}

! Name
! Transmittance Schedule Name
! Number of Vertices
Shading:Building:Detailed,
    ShadeE,                  !- Name
    ,                        !- Transmittance Schedule Name
    4,                       !- Number of Vertices
    14.500000000000, 3.300000000000, 3.500000000000,
                                        !- X,Y,Z  1 {m}
    14.500000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    14.880000000000, 6.960000000000, 2.280000000000,
                                        !- X,Y,Z  3 {m}
    14.900000000000, 3.300000000000, 3.500000000000;
                                        !- X,Y,Z  4 {m}

! Name
! Transmittance Schedule Name
! Number of Vertices
Shading:Building:Detailed,
    7F1001,                  !- Name
    ,                        !- Transmittance Schedule Name
    4,                       !- Number of Vertices
    0.000000000000, 3.300000000000, 3.500000000000,
                                        !- X,Y,Z  1 {m}
    0.000000000000, -0.380000000000, 2.270000000000,
                                        !- X,Y,Z  2 {m}
    -0.400000000000, -0.380000000000, 2.270000000000,
                                        !- X,Y,Z  3 {m}
    -0.400000000000, 3.300000000000, 3.500000000000;
                                        !- X,Y,Z  4 {m}

! Name
! Transmittance Schedule Name
! Number of Vertices
Shading:Building:Detailed,
    ShadeS,                  !- Name
    ,                        !- Transmittance Schedule Name
    4,                       !- Number of Vertices
    14.500000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    14.500000000000, -0.380000000000, 2.270000000000,
                                        !- X,Y,Z  2 {m}
    0.000000000000, -0.380000000000, 2.270000000000,
                                        !- X,Y,Z  3 {m}
    0.000000000000, 0.000000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

! Name
! Transmittance Schedule Name
! Number of Vertices
Shading:Building:Detailed,
    ShadeNE,                 !- Name
    ,                        !- Transmittance Schedule Name
    4,                       !- Number of Vertices
    11.050000000000, 8.200000000000, 3.500000000000,
                                        !- X,Y,Z  1 {m}
    14.500000000000, 8.200000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    14.500000000000, 7.800000000000, 2.400000000000,
                                        !- X,Y,Z  3 {m}
    11.050000000000, 7.800000000000, 3.500000000000;
                                        !- X,Y,Z  4 {m}

GlobalGeometryRules,
    UpperLeftCorner,         !- Starting Vertex Position
    Counterclockwise,        !- Vertex Entry Direction
    Absolute,                !- Coordinate System
    Relative,                !- Daylighting Reference Point Coordinate System
    Relative;                !- Rectangular Surface Coordinate System

Output:Table:SummaryReports,
    AllSummaryAndMonthly;    !- Report 1 Name

OutputControl:Table:Style,
    HTML;                    !- Column Separator

Output:SQLite,
    SimpleAndTabular;        !- Option Type

BuildingSurface:Detailed,
    5Floor,                  !- Name
    Floor,                   !- Surface Type
    Exterior Floor,          !- Construction Name
    Z5BAT,                   !- Zone Name
    GroundSlabPreprocessorCore,  !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    6,                       !- Number of Vertices
    5.750000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  1 {m}
    5.750000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    3.150000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    3.150000000000, 0.760000000000, 0.000000000000,
                                        !- X,Y,Z  4 {m}
    3.760000000000, 0.760000000000, 0.000000000000,
                                        !- X,Y,Z  5 {m}
    3.760000000000, 1.740000000000, 0.000000000000;
                                        !- X,Y,Z  6 {m}

BuildingSurface:Detailed,
    6Floor,                  !- Name
    Floor,                   !- Surface Type
    Exterior Floor,          !- Construction Name
    Z6BSW,                   !- Zone Name
    GroundSlabPreprocessorCore,  !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    8,                       !- Number of Vertices
    3.150000000000, 2.850000000000, 0.000000000000,
                                        !- X,Y,Z  1 {m}
    3.150000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    3.760000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    3.760000000000, 0.760000000000, 0.000000000000,
                                        !- X,Y,Z  4 {m}
    3.150000000000, 0.760000000000, 0.000000000000,
                                        !- X,Y,Z  5 {m}
    3.150000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  6 {m}
    0.000000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  7 {m}
    0.000000000000, 2.850000000000, 0.000000000000;
                                        !- X,Y,Z  8 {m}

BuildingSurface:Detailed,
    9Floor,                  !- Name
    Floor,                   !- Surface Type
    Exterior Floor,          !- Construction Name
    Z9COR,                   !- Zone Name
    GroundSlabPreprocessorCore,  !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    10,                      !- Number of Vertices
    7.640000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  1 {m}
    7.640000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    3.150000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    3.150000000000, 2.850000000000, 0.000000000000,
                                        !- X,Y,Z  4 {m}
    4.050000000000, 2.850000000000, 0.000000000000,
                                        !- X,Y,Z  5 {m}
    4.050000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  6 {m}
    4.750000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  7 {m}
    4.750000000000, 2.860000000000, 0.000000000000,
                                        !- X,Y,Z  8 {m}
    6.250000000000, 2.860000000000, 0.000000000000,
                                        !- X,Y,Z  9 {m}
    6.250000000000, 3.550000000000, 0.000000000000;
                                        !- X,Y,Z  10 {m}

BuildingSurface:Detailed,
    7Floor,                  !- Name
    Floor,                   !- Surface Type
    Exterior Floor,          !- Construction Name
    Z7BNW,                   !- Zone Name
    GroundSlabPreprocessorCore,  !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    8,                       !- Number of Vertices
    4.050000000000, 6.600000000000, 0.000000000000,
                                        !- X,Y,Z  1 {m}
    4.050000000000, 5.450000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    4.750000000000, 5.450000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    4.750000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  4 {m}
    4.050000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  5 {m}
    4.050000000000, 2.850000000000, 0.000000000000,
                                        !- X,Y,Z  6 {m}
    0.000000000000, 2.850000000000, 0.000000000000,
                                        !- X,Y,Z  7 {m}
    0.000000000000, 6.600000000000, 0.000000000000;
                                        !- X,Y,Z  8 {m}

BuildingSurface:Detailed,
    8Floor,                  !- Name
    Floor,                   !- Surface Type
    Exterior Floor,          !- Construction Name
    Z8BN,                    !- Zone Name
    GroundSlabPreprocessorCore,  !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    8,                       !- Number of Vertices
    7.640000000000, 6.600000000000, 0.000000000000,
                                        !- X,Y,Z  1 {m}
    7.640000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    6.250000000000, 3.550000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    6.250000000000, 2.860000000000, 0.000000000000,
                                        !- X,Y,Z  4 {m}
    4.750000000000, 2.860000000000, 0.000000000000,
                                        !- X,Y,Z  5 {m}
    4.750000000000, 5.450000000000, 0.000000000000,
                                        !- X,Y,Z  6 {m}
    4.050000000000, 5.450000000000, 0.000000000000,
                                        !- X,Y,Z  7 {m}
    4.050000000000, 6.600000000000, 0.000000000000;
                                        !- X,Y,Z  8 {m}

FenestrationSurface:Detailed,
    5S,                      !- Name
    Window,                  !- Surface Type
    Exterior Window,         !- Construction Name
    5ExS,                    !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    AluFrame,                !- Frame and Divider Name
    1,                       !- Multiplier
    4,                       !- Number of Vertices
    4.100000000000, 0.000000000000, 2.200000000000,
                                        !- X,Y,Z  1 {m}
    4.100000000000, 0.000000000000, 0.900000000000,
                                        !- X,Y,Z  2 {m}
    4.740000000000, 0.000000000000, 0.900000000000,
                                        !- X,Y,Z  3 {m}
    4.740000000000, 0.000000000000, 2.200000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    5Sa,                     !- Name
    Window,                  !- Surface Type
    Exterior Window,         !- Construction Name
    5ExS,                    !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    AluFrame,                !- Frame and Divider Name
    ,                        !- Multiplier
    4,                       !- Number of Vertices
    4.760000000000, 0.000000000000, 2.200000000000,
                                        !- X,Y,Z  1 {m}
    4.760000000000, 0.000000000000, 0.900000000000,
                                        !- X,Y,Z  2 {m}
    5.400000000000, 0.000000000000, 0.900000000000,
                                        !- X,Y,Z  3 {m}
    5.400000000000, 0.000000000000, 2.200000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    6Int5EN,                 !- Name
    Wall,                    !- Surface Type
    Interior Wall,           !- Construction Name
    Z6BSW,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    5Int6WN,                 !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0.0,                     !- View Factor to Ground
    4,                       !- Number of Vertices
    3.760000000000, 0.760000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    3.760000000000, 0.760000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    3.760000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    3.760000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    6S,                      !- Name
    Window,                  !- Surface Type
    Exterior Window,         !- Construction Name
    6ExS,                    !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    AluFrame,                !- Frame and Divider Name
    ,                        !- Multiplier
    4,                       !- Number of Vertices
    0.680000000000, 0.000000000000, 2.200000000000,
                                        !- X,Y,Z  1 {m}
    0.680000000000, 0.000000000000, 0.700000000000,
                                        !- X,Y,Z  2 {m}
    1.250000000000, 0.000000000000, 0.700000000000,
                                        !- X,Y,Z  3 {m}
    1.250000000000, 0.000000000000, 2.200000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    6Sa,                     !- Name
    Window,                  !- Surface Type
    Exterior Window,         !- Construction Name
    6ExS,                    !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    AluFrame,                !- Frame and Divider Name
    ,                        !- Multiplier
    4,                       !- Number of Vertices
    1.270000000000, 0.000000000000, 2.200000000000,
                                        !- X,Y,Z  1 {m}
    1.270000000000, 0.000000000000, 0.700000000000,
                                        !- X,Y,Z  2 {m}
    1.840000000000, 0.000000000000, 0.700000000000,
                                        !- X,Y,Z  3 {m}
    1.840000000000, 0.000000000000, 2.200000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    6Sb,                     !- Name
    Window,                  !- Surface Type
    Exterior Window,         !- Construction Name
    6ExS,                    !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    AluFrame,                !- Frame and Divider Name
    ,                        !- Multiplier
    4,                       !- Number of Vertices
    1.860000000000, 0.000000000000, 2.200000000000,
                                        !- X,Y,Z  1 {m}
    1.860000000000, 0.000000000000, 0.700000000000,
                                        !- X,Y,Z  2 {m}
    2.430000000000, 0.000000000000, 0.700000000000,
                                        !- X,Y,Z  3 {m}
    2.430000000000, 0.000000000000, 2.200000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    7Wa,                     !- Name
    Window,                  !- Surface Type
    Exterior Window,         !- Construction Name
    7ExW,                    !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    AluFrame,                !- Frame and Divider Name
    ,                        !- Multiplier
    4,                       !- Number of Vertices
    0.000000000000, 4.680000000000, 2.200000000000,
                                        !- X,Y,Z  1 {m}
    0.000000000000, 4.680000000000, 0.540000000000,
                                        !- X,Y,Z  2 {m}
    0.000000000000, 4.030000000000, 0.540000000000,
                                        !- X,Y,Z  3 {m}
    0.000000000000, 4.030000000000, 2.200000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    8Na,                     !- Name
    Window,                  !- Surface Type
    Exterior Window,         !- Construction Name
    8ExN,                    !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    AluFrame,                !- Frame and Divider Name
    ,                        !- Multiplier
    4,                       !- Number of Vertices
    6.490000000000, 6.600000000000, 2.200000000000,
                                        !- X,Y,Z  1 {m}
    6.490000000000, 6.600000000000, 0.700000000000,
                                        !- X,Y,Z  2 {m}
    5.920000000000, 6.600000000000, 0.700000000000,
                                        !- X,Y,Z  3 {m}
    5.920000000000, 6.600000000000, 2.200000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    8Nb,                     !- Name
    Window,                  !- Surface Type
    Exterior Window,         !- Construction Name
    8ExN,                    !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    AluFrame,                !- Frame and Divider Name
    ,                        !- Multiplier
    4,                       !- Number of Vertices
    5.900000000000, 6.600000000000, 2.200000000000,
                                        !- X,Y,Z  1 {m}
    5.900000000000, 6.600000000000, 0.700000000000,
                                        !- X,Y,Z  2 {m}
    5.330000000000, 6.600000000000, 0.700000000000,
                                        !- X,Y,Z  3 {m}
    5.330000000000, 6.600000000000, 2.200000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    1ExNE,                   !- Name
    Wall,                    !- Surface Type
    Exterior Wall,           !- Construction Name
    Z1LIV,                   !- Zone Name
    Outdoors,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    ,                        !- View Factor to Ground
    4,                       !- Number of Vertices
    14.500000000000, 7.800000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    14.500000000000, 7.800000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    10.900000000000, 7.800000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    10.900000000000, 7.800000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    1ExE,                    !- Name
    Wall,                    !- Surface Type
    Exterior Wall,           !- Construction Name
    Z1LIV,                   !- Zone Name
    Outdoors,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    ,                        !- View Factor to Ground
    4,                       !- Number of Vertices
    14.500000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    14.500000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    14.500000000000, 7.800000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    14.500000000000, 7.800000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    1ExW,                    !- Name
    Wall,                    !- Surface Type
    Exterior Wall,           !- Construction Name
    Z1LIV,                   !- Zone Name
    Outdoors,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    ,                        !- View Factor to Ground
    4,                       !- Number of Vertices
    10.900000000000, 7.800000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    10.900000000000, 7.800000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    10.900000000000, 6.600000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    10.900000000000, 6.600000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    1Floor,                  !- Name
    Floor,                   !- Surface Type
    Exterior Floor,          !- Construction Name
    Z1LIV,                   !- Zone Name
    GroundSlabPreprocessorCore,  !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    ,                        !- View Factor to Ground
    8,                       !- Number of Vertices
    14.500000000000, 7.800000000000, 0.000000000000,
                                        !- X,Y,Z  1 {m}
    14.500000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  2 {m}
    11.660000000000, 0.000000000000, 0.000000000000,
                                        !- X,Y,Z  3 {m}
    11.660000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  4 {m}
    7.640000000000, 1.740000000000, 0.000000000000,
                                        !- X,Y,Z  5 {m}
    7.640000000000, 6.600000000000, 0.000000000000,
                                        !- X,Y,Z  6 {m}
    10.900000000000, 6.600000000000, 0.000000000000,
                                        !- X,Y,Z  7 {m}
    10.900000000000, 7.800000000000, 0.000000000000;
                                        !- X,Y,Z  8 {m}

BuildingSurface:Detailed,
    1Ceiling,                !- Name
    Ceiling,                 !- Surface Type
    Exterior Ceiling,        !- Construction Name
    Z1LIV,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    Attic1,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0.0,                     !- View Factor to Ground
    8,                       !- Number of Vertices
    7.640000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    7.640000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    11.660000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  3 {m}
    11.660000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  4 {m}
    14.500000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  5 {m}
    14.500000000000, 7.800000000000, 2.400000000000,
                                        !- X,Y,Z  6 {m}
    10.900000000000, 7.800000000000, 2.400000000000,
                                        !- X,Y,Z  7 {m}
    10.900000000000, 6.600000000000, 2.400000000000;
                                        !- X,Y,Z  8 {m}

FenestrationSurface:Detailed,
    1NEa,                    !- Name
    Window,                  !- Surface Type
    Exterior Window,         !- Construction Name
    1ExNE,                   !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    AluFrame,                !- Frame and Divider Name
    ,                        !- Multiplier
    4,                       !- Number of Vertices
    12.700000000000, 7.800000000000, 2.200000000000,
                                        !- X,Y,Z  1 {m}
    12.700000000000, 7.800000000000, 0.450000000000,
                                        !- X,Y,Z  2 {m}
    12.060000000000, 7.800000000000, 0.450000000000,
                                        !- X,Y,Z  3 {m}
    12.060000000000, 7.800000000000, 2.200000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    1NE,                     !- Name
    Window,                  !- Surface Type
    Exterior Window,         !- Construction Name
    1ExNE,                   !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    AluFrame,                !- Frame and Divider Name
    ,                        !- Multiplier
    4,                       !- Number of Vertices
    13.360000000000, 7.800000000000, 2.200000000000,
                                        !- X,Y,Z  1 {m}
    13.360000000000, 7.800000000000, 0.450000000000,
                                        !- X,Y,Z  2 {m}
    12.720000000000, 7.800000000000, 0.450000000000,
                                        !- X,Y,Z  3 {m}
    12.720000000000, 7.800000000000, 2.200000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    1WS,                     !- Name
    Window,                  !- Surface Type
    Exterior Window,         !- Construction Name
    1ExE,                    !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    AluFrame,                !- Frame and Divider Name
    ,                        !- Multiplier
    4,                       !- Number of Vertices
    14.500000000000, 1.300000000000, 2.200000000000,
                                        !- X,Y,Z  1 {m}
    14.500000000000, 1.300000000000, 0.540000000000,
                                        !- X,Y,Z  2 {m}
    14.500000000000, 3.050000000000, 0.540000000000,
                                        !- X,Y,Z  3 {m}
    14.500000000000, 3.050000000000, 2.200000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    1WN,                     !- Name
    Window,                  !- Surface Type
    Exterior Window,         !- Construction Name
    1ExE,                    !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    AluFrame,                !- Frame and Divider Name
    ,                        !- Multiplier
    4,                       !- Number of Vertices
    14.500000000000, 4.750000000000, 2.200000000000,
                                        !- X,Y,Z  1 {m}
    14.500000000000, 4.750000000000, 0.540000000000,
                                        !- X,Y,Z  2 {m}
    14.500000000000, 6.500000000000, 0.540000000000,
                                        !- X,Y,Z  3 {m}
    14.500000000000, 6.500000000000, 2.200000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    Attic8,                  !- Name
    Floor,                   !- Surface Type
    Attic Floor,             !- Construction Name
    Attic,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    8Ceiling,                !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0.0,                     !- View Factor to Ground
    8,                       !- Number of Vertices
    7.640000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    7.640000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    6.250000000000, 3.550000000000, 2.400000000000,
                                        !- X,Y,Z  3 {m}
    6.250000000000, 2.860000000000, 2.400000000000,
                                        !- X,Y,Z  4 {m}
    4.750000000000, 2.860000000000, 2.400000000000,
                                        !- X,Y,Z  5 {m}
    4.750000000000, 5.450000000000, 2.400000000000,
                                        !- X,Y,Z  6 {m}
    4.050000000000, 5.450000000000, 2.400000000000,
                                        !- X,Y,Z  7 {m}
    4.050000000000, 6.600000000000, 2.400000000000;
                                        !- X,Y,Z  8 {m}

BuildingSurface:Detailed,
    RoofNW,                  !- Name
    Roof,                    !- Surface Type
    Exterior Roof,           !- Construction Name
    Attic,                   !- Zone Name
    Outdoors,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    ,                        !- View Factor to Ground
    4,                       !- Number of Vertices
    11.050000000000, 3.300000000000, 3.500000000000,
                                        !- X,Y,Z  1 {m}
    7.600000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    0.000000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  3 {m}
    0.000000000000, 3.300000000000, 3.500000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    AtticNW,                 !- Name
    Wall,                    !- Surface Type
    Exterior Wall,           !- Construction Name
    Attic,                   !- Zone Name
    Outdoors,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    ,                        !- View Factor to Ground
    3,                       !- Number of Vertices
    10.900000000000, 6.600000000000, 3.452173913043,
                                        !- X,Y,Z  1 {m}
    10.900000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    7.600000000000, 6.600000000000, 2.400000000000;
                                        !- X,Y,Z  3 {m}

BuildingSurface:Detailed,
    Attic1,                  !- Name
    Floor,                   !- Surface Type
    Attic Floor,             !- Construction Name
    Attic,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    1Ceiling,                !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0.0,                     !- View Factor to Ground
    8,                       !- Number of Vertices
    14.500000000000, 7.800000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    14.500000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    11.660000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  3 {m}
    11.660000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  4 {m}
    7.640000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  5 {m}
    7.640000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  6 {m}
    10.900000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  7 {m}
    10.900000000000, 7.800000000000, 2.400000000000;
                                        !- X,Y,Z  8 {m}

BuildingSurface:Detailed,
    AtticNE,                 !- Name
    Wall,                    !- Surface Type
    Exterior Wall,           !- Construction Name
    Attic,                   !- Zone Name
    Outdoors,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    ,                        !- View Factor to Ground
    4,                       !- Number of Vertices
    14.500000000000, 7.800000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    10.900000000000, 7.800000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    10.900000000000, 7.800000000000, 3.452173913043,
                                        !- X,Y,Z  3 {m}
    11.050000000000, 7.800000000000, 3.500000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    RoofE,                   !- Name
    Roof,                    !- Surface Type
    Exterior Roof,           !- Construction Name
    Attic,                   !- Zone Name
    Outdoors,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    ,                        !- View Factor to Ground
    4,                       !- Number of Vertices
    11.050000000000, 3.300000000000, 3.500000000000,
                                        !- X,Y,Z  1 {m}
    14.500000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    14.500000000000, 7.800000000000, 2.400000000000,
                                        !- X,Y,Z  3 {m}
    11.050000000000, 7.800000000000, 3.500000000000;
                                        !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    Attic1W,                 !- Name
    Wall,                    !- Surface Type
    Exterior Wall,           !- Construction Name
    Attic,                   !- Zone Name
    Outdoors,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    ,                        !- View Factor to Ground
    4,                       !- Number of Vertices
    10.900000000000, 7.800000000000, 3.452173913043,
                                        !- X,Y,Z  1 {m}
    10.900000000000, 7.800000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    10.900000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  3 {m}
    10.900000000000, 6.600000000000, 3.452173913043;
                                        !- X,Y,Z  4 {m}

Shading:Building:Detailed,
    ShadeW,                  !- Name
    ,                        !- Transmittance Schedule Name
    6,                       !- Number of Vertices
    10.900000000000, 6.600000000000, 3.452173913043,
                                        !- X,Y,Z  1 {m}
    10.518902292915, 6.600000000000, 3.330664499190,
                                        !- X,Y,Z  2 {m}
    10.518902292915, 8.200000000000, 3.330664499190,
                                        !- X,Y,Z  3 {m}
    11.050000000000, 8.200000000000, 3.500000000000,
                                        !- X,Y,Z  4 {m}
    11.050000000000, 7.800000000000, 3.500000000000,
                                        !- X,Y,Z  5 {m}
    10.900000000000, 7.800000000000, 3.452173913043;
                                        !- X,Y,Z  6 {m}

Shading:Building:Detailed,
    ShadeNW,                 !- Name
    ,                        !- Transmittance Schedule Name
    4,                       !- Number of Vertices
    0.000000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    0.000000000000, 6.979473319220, 2.273508893593,
                                        !- X,Y,Z  2 {m}
    7.203277893543, 6.979473319220, 2.273508893593,
                                        !- X,Y,Z  3 {m}
    7.600000000000, 6.600000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

Shading:Building:Detailed,
    ShadeN,                  !- Name
    ,                        !- Transmittance Schedule Name
    4,                       !- Number of Vertices
    10.518902292915, 6.600000000000, 3.330664499190,
                                        !- X,Y,Z  1 {m}
    7.600000000000, 6.600000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    7.203277893543, 6.979473319220, 2.273508893593,
                                        !- X,Y,Z  3 {m}
    10.518902292915, 6.979473319220, 3.330664499190;
                                        !- X,Y,Z  4 {m}

! Name
! Surface Type
! Construction Name
! Zone Name
! Outside Boundary Condition
! Outside Boundary Condition Object
! Sun Exposure
! Wind Exposure
! View Factor to Ground
! Number of Vertices
BuildingSurface:Detailed,
    Attic3,                  !- Name
    Floor,                   !- Surface Type
    Attic Floor,             !- Construction Name
    Attic,                   !- Zone Name
    Surface,                 !- Outside Boundary Condition
    3Ceiling,                !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0.0,                     !- View Factor to Ground
    4,                       !- Number of Vertices
    8.610000000000, 1.740000000000, 2.400000000000,
                                        !- X,Y,Z  1 {m}
    8.610000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  2 {m}
    6.750000000000, 0.000000000000, 2.400000000000,
                                        !- X,Y,Z  3 {m}
    6.750000000000, 1.740000000000, 2.400000000000;
                                        !- X,Y,Z  4 {m}

FenestrationSurface:Detailed,
    2Sa,                     !- Name
    Window,                  !- Surface Type
    Exterior Window,         !- Construction Name
    2ExS,                    !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    autocalculate,           !- View Factor to Ground
    ,                        !- Shading Control Name
    AluFrame,                !- Frame and Divider Name
    ,                        !- Multiplier
    4,                       !- Number of Vertices
    10.130000000000, 0.000000000000, 2.200000000000,
                                        !- X,Y,Z  1 {m}
    10.130000000000, 0.000000000000, 0.900000000000,
                                        !- X,Y,Z  2 {m}
    10.770000000000, 0.000000000000, 0.900000000000,
                                        !- X,Y,Z  3 {m}
    10.770000000000, 0.000000000000, 2.200000000000;
                                        !- X,Y,Z  4 {m}





------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/