[EnergyPlus_Support] EnvelopeSummary...is there a report where I can see also the internal elements?



EnvelopeSummary...is there a report where I can see also the internal elements? 

ASHRAE 90.1 requires performance U-values for semiheated constructions which as per section A9.4.1.1 and A9.4.1.2 are defined as essentially "partition" elements, i.e. are not on the "envelope".

As these surfaces have other convection coeff. (no wind), the rated U-Value calculations would be as for internal elements so I can't just test it on an external wall.

If I do put it on an external wall and manually change the conditions to "nowind", is that enough or should the boundry condition change from "outside," to "surface,surfacename" for the Rated U-value Calc to be properly executed?



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/