Also,  you can report CO2 Equilivents with the following objects>>

Environmental Impact Factors
District Heating Efficiency 0.3
District Cooling COP 3.0
Steam Conversion Efficiency 0.25
Total Carbon Equivalent Emission Factor From NOx 80.7272
Total Carbon Equivalent Emission Factor From CH4 6.2727
Total Carbon Equivalent Emission Factor From CO2 0.2727

Fuel Factors
Existing Fuel Resource Name NaturalGas Electricity
Units of Measure m3 kg
Energy per Unit Factor
Source Energy Factor 1.0 3.101
Source Energy Schedule Name
CO2 Emission Factor 50.23439 242.67192
CO2 Emission Factor Schedule Name
CO Emission Factor 3.51641E-02 1.51197E+03
CO Emission Factor Schedule Name
CH4 Emission Factor 9.62826E-04 1.60017E-03
CH4 Emission Factor Schedule Name
NOx Emission Factor 4.18620E-02 4.74004E-01
NOx Emission Factor Schedule Name
N2O Emission Factor 9.20964E-04 3.64134E-03
N2O Emission Factor Schedule Name
SO2 Emission Factor 2.51172E-04 5.83874E-01
SO2 Emission Factor Schedule Name
PM Emission Factor 3.18151E-03 7.29822E-03
PM Emission Factor Schedule Name
PM10 Emission Factor 2.38613E-03 7.23699E-03
PM10 Emission Factor Schedule Name
PM2.5 Emission Factor 7.95378E-04 6.12291E-05
PM2.5 Emission Factor Schedule Name
NH3 Emission Factor 0 9.56430E-05
NH3 Emission Factor Schedule Name
NMVOC Emission Factor 2.30241E-03 4.36770E-03
NMVOC Emission Factor Schedule Name
Hg Emission Factor 1.08841E-07 1.62537E-06
Hg Emission Factor Schedule Name
Pb Emission Factor 2.09310E-07 0
Pb Emission Factor Schedule Name
Water Emission Factor 0 1.26003
Water Emission Factor Schedule Name
Nuclear High Level Emission Factor 0 0
Nuclear High Level Emission Factor Schedule Name
Nuclear Low Level Emission Factor 0 0
Nuclear Low Level Emission Factor Schedule Name

Then using a standard output variable for one of the many CO2 reporting features. 

On Tue, Mar 26, 2013 at 3:08 AM, Esmond Tresidder <e.tresidder@xxxxxxxxx> wrote:
 

Hi there,

I'm trying to use EMS to create a new variable from several standard output options at the end of the simulation period. My new variable does not need to feed back into any simulation, or to cancel the run or modify it in any other complex way, as EMS allows you to do, it just needs to sum several Output: Meter values and Output: Variable values, then increase this figure by a percentage if the discomfort hours exceed a certain amount.

As I said, it only needs to do this at the very end of the simulation, as it's working with values for the total time of the simulation. This doesn't seem to be an option in EMS, so I am using "EndOfZoneTimestepBeforeZoneReporting" as the calling point.

My question is, for something so simple as this, is EMS the right thing to be using at all? The most simple example in the EMS guide literature (EMSCustomOutputVariable) is similarly just summing things, but it is doing it for each time step, rather than just at the end. If it isn't EMS then what should I use?

Relevent code below. At the moment the loop to check the comfort hours isn't in. At the moment it runs but I can't access the variable that I'm trying to produce. Can provide full idf file if needed. Thanks for your time.

EnergyManagementSystem:Sensor,
T1, !- Name
Block1:Zone1, !- Output:Variable or Output:Meter Index Key Name
Time Not Comfortable Summer or Winter Clothes; !- Output:Variable or Output:Meter Name

EnergyManagementSystem:Sensor,
T2, !- Name
*, !- Output:Variable or Output:Meter Index Key Name
Heating:DistrictHeating; !- Output:Variable or Output:Meter Name

EnergyManagementSystem:Sensor,
T3, !- Name
*, !- Output:Variable or Output:Meter Index Key Name
Cooling:DistrictCooling; !- Output:Variable or Output:Meter Name

EnergyManagementSystem:Sensor,
T4, !- Name
*, !- Output:Variable or Output:Meter Index Key Name
WaterSystems:DistrictHeating; !- Output:Variable or Output:Meter Name

EnergyManagementSystem:Sensor,
T5, !- Name
*, !- Output:Variable or Output:Meter Index Key Name
InteriorLights:Electricity; !- Output:Variable or Output:Meter Name

EnergyManagementSystem:Sensor,
T6, !- Name
*, !- Output:Variable or Output:Meter Index Key Name
InteriorEquipment:Electricity; !- Output:Variable or Output:Meter Name

!EnergyManagementSystem:Sensor,
! T7, !- Name
!*, !- Output:Variable or Output:Meter Index Key Name
!Fans:Electricity; !- Output:Variable or Output:Meter Name

EnergyManagementSystem:ProgramCallingManager,
CO2 incl penalty, !- Name
EndOfZoneTimestepBeforeZoneReporting, !- EnergyPlus Model Calling Point
CO2InclPenalty; !- Program Name 1

EnergyManagementSystem:GlobalVariable,
TotCO2InclPenalty; !- Erl Variable 1 Name

EnergyManagementSystem:OutputVariable,
Total CO2 emissions including penalty [kg], !- Name
TotCO2InclPenalty, !- EMS Variable Name !
Summed, !- Type of Data in Variable
SystemTimeStep; !- Update Frequency

! SumOrAverage, !- Type of Data in Variable
! ZoneTimeStep; !- Update Frequency

EnergyManagementSystem:Program,
CO2InclPenalty, !- Name
SET CO2gas = 0.19, ! Kg CO2 per what?
SET CO2elec = 0.43, !Kg CO2 per kWh
SET BoilEff = 0.9, ! efficiency of boiler
SET ChillEff = 3.5, ! efficiency of chiller
SET GasDemand = (T2+T4)/BoilEff, !total demand for gas
SET ElecChill = T3/ChillEff, ! electricity demand from chiller
SET OtherElec = T5+T6,
SET TotalElecDemand = OtherElec+ElecChill, ! total electricity demand
SET CO2ExclPenalty = (GasDemand*CO2gas) + (TotalElecDemand*CO2elec),
SET TotCO2InclPenalty = CO2ExclPenalty*1.2;

! So do the above as a dummy, then work out how to put the if/else loop in for overheating hours.

Output:EnergyManagementSystem,
Verbose, !- Actuator Availability Dictionary Reporting
Verbose, !- Internal Variable Availability Dictionary Reporting
Verbose; !- EMS Runtime Language Debug Output Level




--
Jeremiah D. Crossett  | Senior Analyst  |  Phase Change Energy Solutions
120 E. Pritchard St.  | Asheboro, NC 27203  | Mobile 503-688-8951
  


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.