|
Hi Nick The air terminals with reheat only reheat to the heating setpoint, if they were to reheat all the way up to cooling setpoint it would require more operating energy. So under conditions of low zone cooling load, reheat systems will run at the heating setpoint. It looks like you are only scheduling 5% of the electric plug loads, so that might explain the relatively low load. You can examine the expanded IDF file produced by HVAC templates yourself but it shouldn’t introduce any odd scheduling on the weekends. A good way to debug schedules is to request output variable for Schedule Value and double check them by looking at them as time series results. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of thexenyth I realize I forgot to include an actual question... Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |