thanks for the extremely fast reply, more information is added here:

   ** Severe  ** Temperature (low) out of bounds [-518.20] for zone="8PAV:ESTERILIZACAORAPIDA", for surface="8PAV:ESTERILIZACAORAPIDA_PARTITION_5_0_11363"

   **   ~~~   **  During Warmup & Sizing, Environment=SUMMER DESIGN DAY IN SAO PAULO, at Simulation time=01/15 20:00 - 20:01

   **   ~~~   ** Zone="8PAV:ESTERILIZACAORAPIDA", Diagnostic Details:
   **   ~~~   ** ...Internal Heat Gain [4006.000] W/m2
   **   ~~~   ** ...Infiltration/Ventilation [4.447E-003] m3/s
   **   ~~~   ** ...Mixing/Cross Mixing [0.000] m3/s
   **   ~~~   ** ...Zone is not part of HVAC controlled system.

   **  Fatal  ** CalcHeatBalanceInsideSurf: Program terminates due to preceding conditions.

   ...Summary of Errors that led to program termination:

   ..... Reference severe error count=1

   ..... Last severe error=Temperature (low) out of bounds [-518.20] for zone="8PAV:ESTERILIZACAORAPIDA", for surface="8PAV:ESTERILIZACAORAPIDA_PARTITION_5_0_11363"

   ************* Warning:  Node connection errors not checked - most system input has not been read (see previous warning).

   ************* Fatal error -- final processing.  Program exited before simulations began.  See previous error messages.

-------------------------------------------------------------------
Is the "6" of the 4006 W/m2 maybe the problem? should I indicate 3999 W/m2 for example?

Any detective hunch?

thanks.

PH

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Jim Dirkes <jim@...> wrote:
>
> Pablo,
> I don't think you have provided enough information.
> What error is caused at 4000 w/m2?
> There should be no problem caused by the value 2000 or 4000, so I think the problem is something else.
> 
> James V Dirkes II, PE, BEMP, LEED AP
> www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
> Energy Analysis, Commissioning & Training Services
> 1631 Acacia Drive, Grand Rapids, MI 49504 USA
> 616 450 8653
> 
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of phidalgosandoval
> Sent: Wednesday, April 24, 2013 10:26 AM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Internal Gains - High Consumption Equipment - Simulate
> 
> 
> 
> Dear all
> 
> For a high consumption equipment we have 4000 w/m2 and Eplus does not simulate because of the high internal gains, but inputting 2000 w/m2 simulate with no problem (both cases with 20°C as cooling setpoint).
> 
> Does anyone knows how to simulate properly in this case?
> 
> Any comments are welcome,
> 
> Thanks in advance,
> 
> Pablo
>



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/