Thanks Jim I will try conditioning the space to see what happens.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Jim Dirkes <jim@...> wrote:
>
> I think the problem is that you are not conditioning that zone and the high internal heat is causing a surface temperature to become incorrect. It does not make sense that the surface temperature is too low, but perhaps if you condition the zone, the problem will be resolved?
>
> James V Dirkes II, PE, BEMP, LEED AP
> www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
> Energy Analysis, Commissioning & Training Services
> 1631 Acacia Drive, Grand Rapids, MI 49504 USA
> 616 450 8653
>
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of phidalgosandoval
> Sent: Wednesday, April 24, 2013 10:33 AM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Re: Internal Gains - High Consumption Equipment - Simulate
>
>
>
> Ok, Jim,
>
> thanks for the extremely fast reply, more information is added here:
>
> ** Severe ** Temperature (low) out of bounds [-518.20] for zone="8PAV:ESTERILIZACAORAPIDA", for surface="8PAV:ESTERILIZACAORAPIDA_PARTITION_5_0_11363"
>
> ** ~~~ ** During Warmup & Sizing, Environment=SUMMER DESIGN DAY IN SAO PAULO, at Simulation time=01/15 20:00 - 20:01
>
> ** ~~~ ** Zone="8PAV:ESTERILIZACAORAPIDA", Diagnostic Details:
> ** ~~~ ** ...Internal Heat Gain [4006.000] W/m2
> ** ~~~ ** ...Infiltration/Ventilation [4.447E-003] m3/s
> ** ~~~ ** ...Mixing/Cross Mixing [0.000] m3/s
> ** ~~~ ** ...Zone is not part of HVAC controlled system.
>
> ** Fatal ** CalcHeatBalanceInsideSurf: Program terminates due to preceding conditions.
>
> ...Summary of Errors that led to program termination:
>
> ..... Reference severe error count=1
>
> ..... Last severe error=Temperature (low) out of bounds [-518.20] for zone="8PAV:ESTERILIZACAORAPIDA", for surface="8PAV:ESTERILIZACAORAPIDA_PARTITION_5_0_11363"
>
> ************* Warning: Node connection errors not checked - most system input has not been read (see previous warning).
>
> ************* Fatal error -- final processing. Program exited before simulations began. See previous error messages.
>
> ----------------------------------------------------------
> Is the "6" of the 4006 W/m2 maybe the problem? should I indicate 3999 W/m2 for example?
>
> Any detective hunch?
>
> thanks.
>
> PH
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx<mailto:EnergyPlus_Support%40yahoogroups.com>, Jim Dirkes <jim@<mailto:jim@>> wrote:
> >
> > Pablo,
> > I don't think you have provided enough information.
> > What error is caused at 4000 w/m2?
> > There should be no problem caused by the value 2000 or 4000, so I think the problem is something else.
> >
> > James V Dirkes II, PE, BEMP, LEED AP
> > www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
> > Energy Analysis, Commissioning & Training Services
> > 1631 Acacia Drive, Grand Rapids, MI 49504 USA
> > 616 450 8653
> >
> > From: EnergyPlus_Support@xxxxxxxxxxxxxxx<mailto:EnergyPlus_Support%40yahoogroups.com> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx<mailto:EnergyPlus_Support%40yahoogroups.com>] On Behalf Of phidalgosandoval
> > Sent: Wednesday, April 24, 2013 10:26 AM
> > To: EnergyPlus_Support@xxxxxxxxxxxxxxx<mailto:EnergyPlus_Support%40yahoogroups.com>
> > Subject: [EnergyPlus_Support] Internal Gains - High Consumption Equipment - Simulate
> >
> >
> >
> > Dear all
> >
> > For a high consumption equipment we have 4000 w/m2 and Eplus does not simulate because of the high internal gains, but inputting 2000 w/m2 simulate with no problem (both cases with 20°C as cooling setpoint).
> >
> > Does anyone knows how to simulate properly in this case?
> >
> > Any comments are welcome,
> >
> > Thanks in advance,
> >
> > Pablo
> >
>