[EnergyPlus_Support] Re: UFAD systems and supply side errors
Firstly, your problems are unrelated. Tackle your plant problem first, and get your simulation working properly.
Then, when this is working read the RoomAir Models chapter in the inputoutputreferance and pay particular attention to perhaps the 3-node model and
UnderFloorAirDistributionInterior. Modeling other than fully mixed air in zones requires a bit of background reading and employing more than one objects in tandem. These models should be used within their limits or at least understanding their limits, and were designed for annual simulation because CFD for annual simulation is too slow.
As to your chilled water plant problem, the users on the forum often have this problem so check / search keywords in previous posts and the helpdesk website has a knowlege base where this sort of problem may be captured.
Think about your problem logically. If the chilled water is heating up to over 200 deg C, something (like a pump) is injecting energy into the medium. This could be because the pump is operating far outside of its operating limits on the associated pump curve. I.e. the pump (curve) is too small, to big, or the water amount being pumped is too much due to another problem, etc. There are many possibilities. Report and monitor mass flows and temperatures to try and track the error to it's source.
Goodluck,
Jean
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/