Hi All,

I have some doubts regarding UFAD simulations and errors and I would appreciate a lot your help:

1.The UFAD systems from exemple files contains just VAV System as HVAC option. Is there some problem in modeling UFAD system with Unit Ventilator or Fan Coil option??

2. I checked some nodes temperature and found something I couldn´t fix until now. The chiller inlet node temp is 75°, the outlet node is 5°C (lower limit), but after the mixer the bypass temperature (supply side bypass) overrides the chiller temp. After the mixer the temperature  around 70°C (CW Supply Outlet Node)
-All equipments (chiller, tower, pumps, unitventilatior, fancoils) are in autosize.
- I tried to set up the chiller capacity but didn´t work.
- Is that a water flow problem?
- Is it mandatory to keep the chiller bypass??
- I got some warnings, maybe can help you understand better.
** Warning ** Temperature out of range [-100. to 200.] (PsyPsatFnTemp)
** ~~~ ** Max=314.03706 C Min=312.949246 C
** Warning ** GetSpecificHeatGlycol: Temperature out of range (too high) for fluid specific heat
** ~~~ ** Max=279.818702 {C} Min=193.974766 {C}
** Warning ** GetDensityGlycol: Temperature out of range (too high) for fluid density
** ~~~ ** Max=107.275179 {C} Min=100.37377 {C}

3. Probably as a consequence of the problem above mentioned the temperature in my simulation is not converging. Room mean temperature around 250°C.....

Thank you very much for your attention.

Regards,

Diego


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___