Re: [EnergyPlus_Support] RES: Apparent error on ASHRAE 90.1-2007 (and perhaps 2010)





JIm,

I noticed this too and have always gone under the assumption that the calculation given in the IP version is correct since it does call out Pfan = CFMs * 0.3 even in the SI version.

Jason


On Fri, Apr 26, 2013 at 11:08 AM, Fabiano Domingues Ferreira <fabiano.ferreira@xxxxxxxxxxxxxxx> wrote:
 

Or maybe swap the factors:

 

(SI): (1 L/s * 1000) * .3 = 300 W

(IP): 2118.64 cfm * .14  = 296.61 W 

J

 

Fabiano Ferreira

 

De: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] Em nome de Jim Dirkes
Enviada em: Friday, April 26, 2013 2:55 PM
Para: EnergyPlus_Support@xxxxxxxxxxxxxxx; bldg-sim@xxxxxxxxxxxxxxxxxxxxx
Assunto: [EnergyPlus_Support] RE: Apparent error on ASHRAE 90.1-2007 (and perhaps 2010)

 

 

Forgot to say:

A factor of .636 seems to work better.

(SI): (1 L/s * 1000) * .636 = 636 W (This is 1 m3/s)

(IP): 2118.64 cfm * .3  = 636 W  (This is also 1 m3/s)

 

 

James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Jim Dirkes
Sent: Friday, April 26, 2013 1:53 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx; bldg-sim@xxxxxxxxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] RE: Apparent error on ASHRAE 90.1-2007 (and perhaps 2010)

 

 

Fabiano,

It?s encouraging that they noticed something, however I don?t think the math works properly with the formula you sent.

(SI): (1 L/s * 1000) * .14 = 140 W (This is 1 m3/s)

(IP): 2118.64 cfm * .3  = 636 W  (This is also 1 m3/s)

 

 

James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Fabiano Domingues Ferreira
Sent: Friday, April 26, 2013 1:48 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx; bldg-sim@xxxxxxxxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] RES: Apparent error on ASHRAE 90.1-2007 (and perhaps 2010)

 

 

Hi Jim,

 

I was checking 90.1-2010 ? User?s Manual and seems that they have fixed this mistake, follow bellow.

 

 

 

Thanks,

 

Fabiano Ferreira

 

De: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] Em nome de Jim Dirkes
Enviada em: Friday, April 26, 2013 8:11 AM
Para: bldg-sim@xxxxxxxxxxxxxxxxxxxxx; EnergyPlus_Support@xxxxxxxxxxxxxxx
Assunto: [EnergyPlus_Support] FW: Apparent error on ASHRAE 90.1-2007 (and perhaps 2010)

 

 

Dear forums,

I think I have discovered an error in the SI version of ASHRAE 90.1 regarding fan power for Baseline Systems 1 & 2.  I sent the message below to ASHRAE, but then thought, ?Perhaps someone else has also noticed this and received some guidance from ASHRAE?.  Regardless, if it is actually an error, it?s worth mentioning to all of you so that you can be aware of it.

Please  let me know if you are aware of this, and how you have dealt with the discrepancy.  My plan is to use the IP formula because it allows more fan power J.

 

James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653

 

From: Jim Dirkes
Sent: Friday, April 26, 2013 5:59 AM
To: 'change.proposal@xxxxxxxxxx'
Cc: Santiago Velez (santiago@xxxxxxxxxx); francisco@xxxxxxxxxx; 'Jason Glazer'
Subject: Apparent error on ASHRAE 90.1-2007 (and perhaps 2010)

 

Dear ASHRAE,

I am comparing Appendix G fan power calculations for ASHRAE 90.1 in both SI and IP units.  It appears that they do not agree for Baseline Systems 1 & 2.

The formulae for Systems 1 & 2 are:

(IP): Pfan (watts) = CFMs (cfm) * 0.3

(SI): Pfan (watts) = CFMs (L/s) * 0.3

 

Calculating fan power for Systems 1&2:

Given:

L/s * 1000 = m3/s

m3/s * 2118.64 = cfm

 

Substituting these into the fan power equations for Baseline Systems 1 & 2:

(SI): (1 L/s * 1000) * .3 = 300 W

(IP): 2118.64 cfm * .3  = 636 W

 

The fan power should be identical, but isn?t even close! Have you ever noticed this?  I could not find an errata sheet that corrected the formula. Will you please check to see if there is a correction?  Please make a correction if I am not missing something!

Thank you!

 

p.s., In a smaller way, the fan power calculations do not agree for the other System types.  This appears to be due in part to using 5 digit precision for IP units and 4 digits for SI (e.g., 0.00094 for IP and 0.0015 for SI)  If you use SI factors of 0.0014857 and 0.0020547 for Systems 3-4 and 5-8 respectively, the agreement is better.

 

James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653

 

The information contained in this communication is confidential, may be privileged and is intended for the exclusive use of the above named addressee(s). If you are not the intended recipient(s), you are expressly prohibited from copying, distributing, disseminating, or in any other way using any information contained within this communication. If you have received this communication in error please contact the sender by telephone or by response via mail.

We have taken precautions to minimize the risk of transmitting software viruses, but we advise you to carry out your own virus checks on any attachment to this message. We cannot accept liability for any loss or damage caused by software viruses.




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___