Harshul,
Most ?real? systems turn the heating source (e.g., boiler) ON and OFF at a certain time of year. In the Northern hemisphere, that might mean ON October 1 and OFF May 1 (obviously It can vary somewhat).
To accomplish this in E+, just assign a schedule to the PlantEquipmentOperationSchemes object. In the example below, the Control Scheme schedule is ?always on?, but you can make it anything you wish.
PlantEquipmentOperationSchemes
PlantOperationSchemeName
PltOpernScheme1
Control Scheme1 Object Type
PlantEquipmentOperation:HeatingLoad
__._,_.___
Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov
The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=28883/stime=1367188846>
Your email settings: Individual Email|Traditional
<http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJmZnA5NzFsBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzEzNjcxODg4NDY->Change settings via the Web (Yahoo! ID required)
Change settings via email: <mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=Email Delivery: Digest>Switch delivery to Daily Digest | Switch to Fully Featured
<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJkMDJmZm9kBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMzY3MTg4ODQ2>Visit Your Group | <http://docs.yahoo.com/info/terms/> Yahoo! Groups Terms of Use | <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> Unsubscribe
__,_._,___