[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: AirTerminal:SingleDuct:ParallelPIU LEED ASHRAE
I'm modeling system 6 of ASHRAE and therefore I have to consider G3.1.3.14 too. How shall the statement "the supply air temperature setpoint shall be constant at the design conditions" be applied in EnergyPlus? Does it mean that for the summer season (cooling mode) I have to use a setpoint manager with the same temperature that is used at the sizing conditions, i.e. zone setpoint temperature - 11°C (see G3.1.2.8)? And for the winter season? In heating mode the supply air temperature depends both on the AHU and on the AirTerminal:SingleDuct:ParallelPIU:Reheat and at the same time some zones could need heating and some other zones could need cooling. Could a setpoint manager be applied on the AirTerminal:SingleDuct:ParallelPIU:Reheat ?
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Jim Dirkes <jim@...> wrote:
>
> That sounds like something unexpected and is probably not intended. I recommend that you submit the file to the Help Desk to ask why that happens. Please let the forum know what you learn!
>
> James V Dirkes II, PE, BEMP, LEED AP
> www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
> Energy Analysis, Commissioning & Training Services
> 1631 Acacia Drive, Grand Rapids, MI 49504 USA
> 616 450 8653
>
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of andresdagm
> Sent: Monday, February 04, 2013 5:16 PM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Re: AirTerminal:SingleDuct:ParallelPIU LEED ASHRAE
>
>
>
> Thank you,it have help me a lot.
>
> Umm, Although my air loop doesn't operate, the PFP box is operate, I have use an office schedule (8:00-18:00) also a night cycle schedule for my VAV System, and the air loop makes a cycle on/off, but the PFP never turns off.
>
> I think that I can change the Outdoor Air Flow Rate Fraction Schedule of the DesignSpecification:outdoorAir object, the way I can change my schedule of the Air Loop to On.
>
> Don't know why my PFP never turn off.
>
> Thanks you,
>
> Dante
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/