RE: [EnergyPlus_Support] Controller error for Chilled Water system



It could be that the coil is just not large enough to meet the load at full water flow.  The chilled water is only 4C colder than the air temperature setpoint, that may be limiting the cooling capacity.  



Also that coil controller works better when the sensor node is the air outlet of the coil (rather than a node further downstream).



From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Celia King-Scott
Sent: Tuesday, April 30, 2013 12:01 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Controller error for Chilled Water system





Hi all, 



I was wondering if someone can help me. 

I am getting the following error for all my water coil controllers: 



* Severe  ** FindRootSimpleController: Controller error for controller = "S-23 AHU COOLING COIL CONTROLLER"

   **   ~~~   **  Environment=COMMUNITYCENTER_CKS122812, at Simulation time=01/03 14:00 - 14:30

   **   ~~~   **   Controller function is inconsistent with user specified controller action = Reverse action

   **   ~~~   **   Actuator will be set to maximum action


__._,_.___

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=28914/stime=1367350117>

Your email settings: Individual Email|Traditional
<http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJmaDNmMGVxBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzEzNjczNTAxMTc->Change settings via the Web (Yahoo! ID required)
Change settings via email: <mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=Email Delivery: Digest>Switch delivery to Daily Digest | Switch to Fully Featured
<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJkbzE2Y2hkBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMzY3MzUwMTE3>Visit Your Group  | <http://docs.yahoo.com/info/terms/> Yahoo! Groups Terms of Use  | <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> Unsubscribe

__,_._,___