[EnergyPlus_Support] Re: Controller error for Chilled Water system





in my experience this is not a coil or system issue, but an issue with Schedules. something is off that should be on. I think the meaning of the error message is that it is calling for a big flow rate but it is not achievable - for example the chiller or chw pump may have  different schedule than the cooling coil.