[EnergyPlus_Support] multizone temperature setpoint



Hi, I would like to ask how control a multizone average temperature.

I have an AHU which serves two zones. These are two identical rooms with different internal gains.

There is a pre-heat which increases outdoor temperature up to 15 °C and then I used an electric heating coil. I would like to obtain 21°C as average temperature of these two zones.

Firstly I tried to put the coil setpoint on the node which mixes the two zones' return air and a SetpiontManager:Scheduled. The behaviour of the coil is "highly floating" and it doesn't achieve the setpoint.

Secondly I tried to use ZoneControl:Thermostat + SetpointManager:MultiZone:Heating:Average. It works perfectly without internal gains. But if I schedule people gains, it doesn't work. (people in only one room: 21°C in the unoccupied room and more in the occupied one, while I want an average of 21; equal number of people in both rooms: "highly floating" and it doesn't achieve the setpoint).

I suppose to ignore some important element of control. Thank you if you have some suggestions.



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/