Hello, 
For the baseline model, ASHRAE 90.1-2007 says that chillers have a COP and IPLV value according to the table 6.8.1I. 
However, it doesn't say anything about the performance curves, so what you can do is to create your own curves by regression, just make sure that the IPLV is calculated as follows:

 IPLV=0.01*A+0.42*B+0.45*C+0.12*D

 Where: A: efficiency at 100% (COP)
        B: efficiency at 75%
        C: efficiency at 50%
        D: efficiency at 25%

Data that is used to make this curve should be normalized.
You can start with coefficients given in this book: ''Non residential ALTERNATIVE CALCULATION METHOD APPROVAL MANUAL-1998'' and this guide: ''Development and Testing of a Reformulated Regression-Based Electric Chiller Model''

Hope this helps.

- Billy Condor 
  Sumac
  http://sumacinc.com/es/


--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Jeff Haberl <jhaberl@...> wrote:
>
> FYI.
> 
> RP1004 has useful advice on how to do this with real chiller data.
> 
> Jeff
> 
> Jeff S. Haberl, Ph.D., P.E., FASHRAE, FIBPSA
> Department of Architecture
> Texas A&M University
> College Station, Texas 77845-3581
> Office: 979-845-6507, Lab: 979-845-6065
> Fax: 970-862-2457, jhaberl@...<mailto:jhaberl@...>, www.esl.tamu.edu<http://www.esl.tamu.edu>
> 
> On Feb 14, 2013, at 11:58 PM, "shubou" <dingwenting@...<mailto:dingwenting@...>> wrote:
> 
> 
> 
> Hi,
> 
> Who can tell me how to generate the part load performance curve of centrifugal chiller according to ASHRAE STANDARD 90.1-2007 TABLE 6.8.1I?
> 
> Thank you.
>



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/