[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] G3.1.3.7: Type and number of chillers
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] G3.1.3.7: Type and number of chillers
- From: "billysonny1" <bscr_14@xxxxxxxxxxx>
- Date: Wed, 15 May 2013 23:17:05 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Wed, 15 May 2013 17:17:08 -0600
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=echoe; t=1368659827; bh=vx0fb1Juo+vNaIIunmrWm3p/P3MXjYAGInEZhiRSsWA=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:User-Agent:X-Mailer:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=M557fV4KSYotLb2ICI8dFJGRvPBEZHDQ8fKTLaQu8LK8IJaZMQiVXwnmmiDNE3UZ8tp+79yDEQiL9XX2TXSFmzJzkK+FN7Wu+63pnb3+FkliTd7qNziiLNVlDnZ0jU9Nwt5Cj7lC9oj3TurIYBrkjz95QFvw4b3lbpQUGpHiLeA=
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=echoe; d=yahoogroups.com; b=I4KoB4J+i8Y+NinchEo+lizXmb6MumcVhFMd9GZawQs7shh0dvn56s2EF4RR8UZTJRmaielx50KLkQSrnz2ObGig63/+hFCZQHJwkmFoFRAuvEQRxKtTNyC6VBQgEvfVN+x5fNChslo8FIQCjAoxDEd4Dh4Ajc3dwwu13VPdxAA=;
- Envelope-to: linda@xxxxxxxxxxxxxx
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
Hello,
I have a question about the type and number of chillers I have to use for the baseline model according to ASHRAE 90.1-2007.
The issue is that in the IP version, these values are in tons and in the SI version, these are in m2. Actually, I think that these two units shouldn't be equivalent because the capacity not only depends on the area but also in the weather and Window-to-wall ratio, among others.
I get 370 tons for cooling load, which according to the IP version fits the second option (2 chillers), however the conditioned area for my project is less that 11148 m2, which according to the SI version fits the first option (just 1 chiller).
Please advice.
Thanks in advance.
-Billy Condor.
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/