Jean, You can propagate a contaminant through an air flow network in EnergyPlus, but the results will not be very useful (so mixing also works). The problem is that
the contaminant will be fully mixed in the first zone as it is dispersed. If you start a fire in Zone 1, smoke rises to fill the space from the ceiling down. It doesn’t flow to the next zone until it reaches the top of a door (or some other crack in the
ceiling). In EnergyPlus the contaminant is immediately fully mixed in the space (fully diluted) and will start moving into the next zone in a diluted form where it is again further diluted by complete mixing in that zone. Generally you want to be able
to see high concentration areas when working with contaminates. CFD is better at moving the contaminant and maintaining concentrations with in a space, but many codes only have the contaminant riding on the air movement and not propagating on their own vapor
pressures. Consequently, it is difficult to properly simulate a pool of warm water in a space using most CFD because the water only moves as a contaminant on the air streams and not by vapor pressure. More sophisticated CFD that can handle phase change materials
can do better, but most of the focus in on combustion and very turbulent flow regimes, not typical of most building environments. Ned Lyon, P.E. (MA, WV) SIMPSON GUMPERTZ & HEGER
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
On Behalf Of Jean marais Nothing wrong with uniform gas, but the question would be how this is or can be handled across zone boundries, i.e. non-CFD, IMO. It couldn't be too hard, or? __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.