[EnergyPlus_Support] Re: Help: Inverter AC modeling
Sir My task is to model my experimental setup and perform simulation. If i use autosize feature would it be correct method?
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Jim Dirkes <jim@...> wrote:
>
> I recommend using the Autosize feature. The catalog may not account for all of your building's features.
>
> James V Dirkes II, PE, BEMP, LEED AP
> www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
> Energy Analysis, Commissioning & Training Services
> 1631 Acacia Drive, Grand Rapids, MI 49504 USA
> 616 450 8653
>
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of energy.anant
> Sent: Sunday, June 09, 2013 4:09 AM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Re: Help: Inverter AC modeling
>
>
>
> There is no heating (cooling only VRF System). i have specified the sizing as per the Daikin catalog which came with AC
>
> Yes i have reported the veritable both hourly and timestep (60) zone temperature is nearly equal to setpoint when outdoor temp is around 18 to 24 i also have 2 kW sensible equipment load in the zone.
>
> Anant Joshi
> M Tech Energy Engg
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx<mailto:EnergyPlus_Support%40yahoogroups.com>, Jim Dirkes <jim@<mailto:jim@>> wrote:
> >
> > The cooling setpoint is 23c.
> > What is the heating setpoint?
> > Is the setpoint met at certain times, but not others?
> > How is the equipment sized? Are you specifying a capacity? Autosizing?
> > Have you reported variables to see what is happening for each hour or timestep (Output:Variable) within the VRF? Within the zone?
> >
> >
> > James V Dirkes II, PE, BEMP, LEED AP
> > www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
> > Energy Analysis, Commissioning & Training Services
> > 1631 Acacia Drive, Grand Rapids, MI 49504 USA
> > 616 450 8653
> >
> > From: EnergyPlus_Support@xxxxxxxxxxxxxxx<mailto:EnergyPlus_Support%40yahoogroups.com> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx<mailto:EnergyPlus_Support%40yahoogroups.com>] On Behalf Of energy.anant
> > Sent: Saturday, June 08, 2013 8:31 AM
> > To: EnergyPlus_Support@xxxxxxxxxxxxxxx<mailto:EnergyPlus_Support%40yahoogroups.com>
> > Subject: [EnergyPlus_Support] Re: Help: Inverter AC modeling
> >
> >
> >
> > Dear Mr. James V Dirkes
> >
> > My simulation is running without errors and warnings. and temperatures i am getting are 16 to 20 in winter and around 30 in summer for annual simulation run whereas cooling set point is 23 C.
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx<mailto:EnergyPlus_Support%40yahoogroups.com><mailto:EnergyPlus_Support%40yahoogroups.com>, Jim Dirkes <jim@<mailto:jim@>> wrote:
> > >
> > > Dear Anant,
> > > If your energy simulation works without errors and the zone temperature is not very close to the setpoint, the cooling (or heating) capacity may be too small for the zone.
> > >
> > > James V Dirkes II, PE, BEMP, LEED AP
> > > www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
> > > Energy Analysis, Commissioning & Training Services
> > > 1631 Acacia Drive, Grand Rapids, MI 49504 USA
> > > 616 450 8653
> > >
> > > From: EnergyPlus_Support@xxxxxxxxxxxxxxx<mailto:EnergyPlus_Support%40yahoogroups.com><mailto:EnergyPlus_Support%40yahoogroups.com> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx<mailto:EnergyPlus_Support%40yahoogroups.com><mailto:EnergyPlus_Support%40yahoogroups.com>] On Behalf Of energy.anant
> > > Sent: Friday, June 07, 2013 5:48 PM
> > > To: EnergyPlus_Support@xxxxxxxxxxxxxxx<mailto:EnergyPlus_Support%40yahoogroups.com><mailto:EnergyPlus_Support%40yahoogroups.com>
> > > Subject: [EnergyPlus_Support] Re: Help: Inverter AC modeling
> > >
> > >
> > >
> > > I am trying to model the inverter AC which is a Veritable refrigerant flow system. To achieve this i have used following class objects Cooling coil: DX:VRF, HVAC Template: Terminal Unit : VRF, Air conditioner : VRF and a constant volume fan.
> > >
> > > there is no outdoor air system.
> > >
> > > What i suspect is that the problem may be with cooling capacity curves though i am not sure that my approach of modeling is currect (as i am a new user of energy plus) i have got the capacity table of the system and created the performance curves as per the help documentation. but i am confused about the cooling capacity curve function of flow fraction.
> > >
> > > Hope i have elaborated my problem and will be able to get some help
> > >
> > > Anant Joshi<http://www.linkedin.com/pub/anant-joshi/19/a91/686>
> > >
> > > M Tech Energy Engg
> > > MNIT, Jaipur
> > > +91 9462216493
> > >
> > >
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx<mailto:EnergyPlus_Support%40yahoogroups.com><mailto:EnergyPlus_Support%40yahoogroups.com><mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx<mailto:EnergyPlus_Support%40yahoogroups.com><mailto:EnergyPlus_Support%40yahoogroups.com>>, Jim Dirkes wrote:
> > > >
> > > > Dear energy modeler,
> > > > You have provided very little information and it is not possible to determine what is causing your problem! Please provide more details.
> > > >
> > > > James V Dirkes II, PE, BEMP, LEED AP
> > > > www.buildingperformanceteam.com<http://www.buildingperformanceteam.com>
> > > > Energy Analysis, Commissioning & Training Services
> > > > 1631 Acacia Drive, Grand Rapids, MI 49504 USA
> > > > 616 450 8653
> > > >
> > > > From: EnergyPlus_Support@xxxxxxxxxxxxxxx<mailto:EnergyPlus_Support%40yahoogroups.com><mailto:EnergyPlus_Support%40yahoogroups.com><mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx<mailto:EnergyPlus_Support%40yahoogroups.com><mailto:EnergyPlus_Support%40yahoogroups.com>> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx<mailto:EnergyPlus_Support%40yahoogroups.com><mailto:EnergyPlus_Support%40yahoogroups.com>] On Behalf Of energy.anant
> > > > Sent: Friday, June 07, 2013 12:28 AM
> > > > To: EnergyPlus_Support@xxxxxxxxxxxxxxx<mailto:EnergyPlus_Support%40yahoogroups.com><mailto:EnergyPlus_Support%40yahoogroups.com><mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx<mailto:EnergyPlus_Support%40yahoogroups.com><mailto:EnergyPlus_Support%40yahoogroups.com>>
> > > > Subject: [EnergyPlus_Support] Help: Inverter AC modeling
> > > >
> > > >
> > > >
> > > > Hi
> > > >
> > > > I am trying to model the inverter split AC (Daikin FTKD50FVM inverter pair 1.5 tr capacity) using VRF class objects.
> > > >
> > > > Problem i am getting is that the zone average temperature report variable values are not equal to the set point temperature.
> > > >
> > > > can someone point me in the right direction of possible errors ...
> > > >
> > >
> >
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/