Hi Jean,

I am indeed using a VAV (through the HVACTemplate objects) but I've disabled reheat (Reheat Coil Type = None). The zone heating setpoint is 5degC anyway.

Patrick

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "jeannieboef@..." <jeannieboef@...> wrote:
>
> You are using a vav with reheat, right. In clg mode it will reheat to  
> the zone htg setpoint not the zone clg setpoint.
> 
> Sent from my iPhone (excuse the brevity)
> Mit freundlichen Grü�en
> 
> i. A.
> Jean Marais
> B.Eng (Mech)
> LEED Accredited Professional
> Building Energy Modeling with DesignBuilder and EnergyPlus
> 
> b.i.g. bechtold
> INGENIEURGESELLSCHAFT MBH
> KeithstraÃ?e 6
> 10787 Berlin
> Tel.   +49 30 6706662-23
> Fax  +49 30 6706662-18
> Marais.Jean@...
> www.designbuilder-big.com
> www.big-gruppe.com/tga
> Firmensitz: Berlin, Registergericht: Amtsgericht Charlottenburg, HRB  
> 112242 B
> Geschäftsführer: Bernd Bechtold, Tino Laupitz, Carsten Teichmann
> 
> "The LEED® (Leadership in Energy and Environmental Design) Green  
> Building
> Rating System is the nationally accepted benchmark for the design,  
> construction,
> and operation of high performance green buildings."
> Other LEED descriptive copy may be found on the USGBC Web site: http://www.usgbc.org/leed
> 
> Official Reseller for DesignBuilder in Germany and Austria
> 
> 
> 
> On 12.06.2013, at 03:37, Patrick Bivona <patrick.bivona@...>  
> wrote:
> 
> > Hi,
> >
> > I'm getting this warning message after a run:
> >
> >    ** Warning ** SizeZoneEquipment: Supply air temperature  
> > (calculated) within 5C of zone setpoint temperature
> >    **   ~~~   ** ...check zone thermostat set point and design  
> > supply air temperatures
> >    **   ~~~   ** ...zone = "ZONE 1F ENTRANCE WEST" first occurrence  
> > during cooling load calculations
> >    **   ~~~   ** ...predicted zone cooling load = -863.19 W
> >    **   ~~~   ** ...zone temperature            = 20.00 C
> >    **   ~~~   ** ...supply air temperature      = 16.00 C
> >    **   ~~~   ** ...temperature difference      = -4.00000 C
> >    **   ~~~   ** ...calculated mass flow rate   = 0.21163 kg/s
> >
> > I understand the general purpose of the temperature difference  
> > check: avoid high flow rates.
> > What I don't understand is why the "zone temperature" is reported as  
> > being 20 degC, when my thermostat cooling setpoint is 24 degC.
> >
> > Am I wrong in assuming that "zone temp" should be the cooling  
> > setpoint? If so, why recommend to check the zone thermostat in the  
> > warning message?
> >
> > I'm confused!
> >
> > Thanks in advanced for your help,
> > Patrick Bivona
> >
> >
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/