|
Thank you Andy. The environments are not small and have a relatively load required for the use of air conditioning. I do not understand why the same error. I am sending the model to you in email. Again, thank you my friend. I'm in your hold. Técg. Ivan Mezzacapa Projetista de Ar Condicionado / Consultor de Eficiência Energética em Ar Condicionado LinkedIN: http://www.linkedin.com/in/ivanmezzacapa Facebook: http://www.facebook.com/ivan.mezzacapa Celular: (11)9963-9326To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: andy.tindale@xxxxxxxxxxxxxxxxxxx Date: Wed, 12 Jun 2013 12:10:13 +0100 Subject: RE: [EnergyPlus_Support] Heating Load = Zero? Ivan,
It's hard to know for sure without seeing the model but I believe that this is caused by specifying heating/cooling equipment in a zone which the autosizing calculations determine have no heating/cooling requirement. Are the zones listed perhaps small interior zones without a load?
Regards,
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Ivan Mezzacapa
I have a little urgency with this problem and can not figure out.
If anyone knows anything, any comments greatly help.
Thank you all!
Técg. Ivan Mezzacapa Projetista de Ar Condicionado / Consultor de Eficiência Energética em Ar Condicionado LinkedIN: http://www.linkedin.com/in/ivanmezzacapa Facebook: http://www.facebook.com/ivan.mezzacapa Celular: (11)9963-9326 To: energyplus_support@xxxxxxxxxxxxxxx
Hi!
i need a help. My simulation is giving this error however, I pointed out all the capabilities and equipment in their respective environments. My thermostats are normal.
These are the errors:
** Warning ** Calculated design cooling load for zone = bloco7: SALA15 is zero. ~ ** ~ ~ ** Check Sizing: Zone and ZoneControl: Thermostat inputs. ** Warning ** Calculated design heating load for zone = bloco7: SALA15 is zero. ~ ** ~ ~ ** Check Sizing: Zone and ZoneControl: Thermostat inputs. ** Warning ** Calculated design cooling load for zone = bloco7: SALA14 is zero. ~ ** ~ ~ ** Check Sizing: Zone and ZoneControl: Thermostat inputs. ** Warning ** Calculated design heating load for zone = bloco7: SALA14 is zero. ~ ** ~ ~ ** Check Sizing: Zone and ZoneControl: Thermostat inputs. ** Warning ** Calculated design cooling load for zone = bloco7: SALA13 is zero. ~ ** ~ ~ ** Check Sizing: Zone and ZoneControl: Thermostat inputs. ** Warning ** Calculated design heating load for zone = bloco7: SALA13 is zero. ~ ** ~ ~ ** Check Sizing: Zone and ZoneControl: Thermostat inputs. ** Warning ** Calculated design cooling load for zone = bloco6: SALA04 is zero. ~ ** ~ ~ ** Check Sizing: Zone and ZoneControl: Thermostat inputs. ** Warning ** Calculated design heating load for zone = bloco6: SALA04 is zero. ~ ** ~ ~ ** Check Sizing: Zone and ZoneControl: Thermostat inputs.
This is happening in all environments and not know why.
Thank you!
Técg. Ivan Mezzacapa Projetista de Ar Condicionado / Consultor de Eficiência Energética em Ar Condicionado LinkedIN: http://www.linkedin.com/in/ivanmezzacapa Facebook: http://www.facebook.com/ivan.mezzacapa Celular: (11)9963-9326
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |