[EnergyPlus_Support] Re: Error: Heating Load is Zero



The first two errors are for internal zones...the others are probably also, i've not checked. There is no infiltration to any zones (as you said). The zone adjacent to these zones has a large glass front which lets solar in, but little heat escapes. This is a factory and there are some major internal loads. Many of the ODA rates are less than 1.

    8.7,                     !- Maximum Dry-Bulb Temperature {C}
    8.3,                     !- Daily Dry-Bulb Temperature Range {deltaC}

May sound cold, but if the building is still warm from the day before, it may not matter...as soon as the sun comes up, the solar will come.

1) Do you expect a heating load?
2) Why?

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Ivan Mezzacapa <ivan_slip@...> wrote:
>
> Hi!
> i'm getting this error and don't know why.
> My thermostat is Ok and my schedules to.
> ** Warning ** Calculated design heating load for zone=85APOIO:MANUTENCAOOFFICE is zero.   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.   ** Warning ** Calculated design heating load for zone=85APOIO:METALOG is zero.   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.   ** Warning ** Calculated design heating load for zone=85APOIO:GARANTIA is zero.   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.   ** Warning ** Calculated design heating load for zone=80PRODUCAO:RCBMNTQLDDFRNCDR is zero.   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
> How can i solve this?
> Thanks!
> T�cg. Ivan Mezzacapa
> Projetista  de Ar Condicionado / Consultor de Efici�ncia Energ�tica em Ar Condicionado
> LinkedIN: http://www.linkedin.com/in/ivanmezzacapaFacebook: http://www.facebook.com/ivan.mezzacapaCelular: (11)9963-9326
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/