Re: [EnergyPlus_Support] Zone Level Airflows
Sizing:zone object you specify the air temperature and humidity with
which the air should enter the zone (it doesn't matter where the air
comes from or what amount of it is ODA). This air's energy (enthalpy
and moisture) is added to the zones energy and moisture balance
equations. In effect the volume airflow to meet the load at specified
supply temp is calculated...sizing factor is included.
This is how the load is deturmined for the zone. The equipment is then
sized (sizing:system object) to meet this load (air flow at specified
temp). It may be specified that the equipment must supply a minimum
ODA amount (and the equipment looks up this value from the sizing:zone
object). If the value of the minimum ODA flowrate exceeds the total
needed for cooling, the ODA rate will be used (100% ODA) and
conditioned to the setpoints. The setpoint manager assigned air
setpoint temps should be setup to deliver at least the air at the same
setpoints as the design air setpoints that you put in the sizing:zone
object.
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/