[EnergyPlus_Support] Heat recovery device recovers heat when off



v7.2
Dear Collegues,
For the second time a client is asking me why the heat recovery device is recovering heat when the availibility schedule for the object is indeed scheduled off.

I have looked at the file and it is true.

1) co-insidently, I believe a plate air air heat recovery devise should not have an availibility schedule...the air must pass through the devise unless it is bypassed. Bypass at the moment, is possible only when used together with economizer control switched on. This also works to stop the heat exchanger exchanging heat as it is bypassed when within economizer limits. However, in practise, the bypass is normally on the exhaust stream AND a very significant energy reduction from the normal fan operation is expected, due to the significant pressure reduction when the air does not battle its way through the heat exchanger. Equipment data sheets also have this info to input. I would like the plate model (and possibly generally all heat recovery air devices) to
a) be reworked either eliminating the availibility schedule or making it effective AND updating the documentation
b) include inputs for pressure reductions when in bypass operation AND to be reflected as a saving in the reports AND to possibly include a seperate controller that may or may not couple with the oda damper controller

2) has anyone else come across this issue? Is it restricted to plate heat recovery device? What is the case in v8?

Jean



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/