Look to the minimum and maximum flowrate fields in both the controller:coil and coil:water objects. If you put a setpoint on the control node that varies like setpointmanager:singlezone:heat which varies linearly between two bounds, like 13 to 33 deg C, then the controller may see that it must try and reach say 33 deg C, but it can't because the chilled water temp is 7 deg C. The action is reverse for cooling coil so it closes more and more to achieve a higher air temp out. The opposite also applies to the heating coil, which will face the same problem if the setpoint is say 13 deg C. This "error" is popping up when these conditions arrise, but normally the actuator goes to its correct maximum possistion to deal with the problem (be it totally open or totally closed), which is correct and as designed. In your case it may be the impossition of a limit which blocks the actuator from its max position which causes the fatal... I'm just guessing all of this. Jean Sent from my iPhone (excuse the brevity) Mit freundlichen Grü�en i. A. Jean Marais B.Eng (Mech) LEED Accredited Professional Building Energy Modeling with DesignBuilder and EnergyPlus b.i.g. bechtold INGENIEURGESELLSCHAFT MBH Keithstra�e 6 10787 Berlin Tel. +49 30 6706662-23 Fax +49 30 6706662-18 Firmensitz: Berlin, Registergericht: Amtsgericht Charlottenburg, HRB 112242 B Geschäftsführer: Bernd Bechtold, Tino Laupitz, Carsten Teichmann "The LEED® (Leadership in Energy and Environmental Design) Green Building Rating System is the nationally accepted benchmark for the design, construction, and operation of high performance green buildings." Other LEED descriptive copy may be found on the USGBC Web site: http://www.usgbc.org/
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |