I am trying to model a chilled water plant. 

On the supply side, there are two identical chillers in parallel, the chillers are constant flow type. In the PlantLoop object, I have specified the load distribution scheme to be "sequential".

The primary pump is a headered pump with two identical constant flow pumps in the bank. Each pump supplys the nominal flow rate for a single chiller. In the "flow sequencing control scheme" of the headered pump, I am using "sequential".

The questions are:

1. In order to have sequenced chiller operation. In the "PlantEquipmentOperation:Cooling", do I need to specify a load range that only one chiller operats and another load range that both chillers operate? I thought that since I have specified "sequential" load distribution, it should automatically do so.

2. For the headered primary pump, I assume that when only one chiller operates, one of the pumps in the headered pump bank will be off. But that does not seem to be the case, when only one chiller operates, the pump still provides twice the flow rate, how do I have the pump flow follow the chiller sequence?

Thanks,

TW





------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/