RE: [EnergyPlus_Support] VRF Dedicated Outdoor Air System with ERV





Thanks for the prompt response.

The other question is that the DOAS’s cooling coil is VRF type, is it possible to set this coil in EnergyPlus?

 

Thanks.

 

 

Stan Ho

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Bereket Nigusse
Sent: Monday, August 05, 2013 12:11 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] VRF Dedicated Outdoor Air System with ERV

 

 

Stan,

 

You can model the VRF and the DOAS as a separate systems serving each zone. To do this:

(1) set the outdoor air flow rates in " ZoneHVAC:TerminalUnit:VariableRefrigerantFlow" objects to zero.   

(2) set up a central DOAS system that supplies the required amount of outdoor air to each zone.

(3) connect the terminal air distribution units of the DOAS system to each zone

(4) Make the DOAS terminal unit first priority and the VRF Zone Object the second priority in "ZoneHVAC:EquipmentList". The equipment set up in example file "ZoneWSHP_wDOAS" is a good starting point to understand the connection though this example is a single zone.

    

Hope this helps. 

Bereket Nigusse

Florida Solar Energy Center

 


From: kkkimostan <tzunghan.ho@xxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Sunday, August 4, 2013 11:12 AM
Subject: [EnergyPlus_Support] VRF Dedicated Outdoor Air System with ERV

 

 

Hello,

I am simulating a building with VRF system for each thermal zone, and a VRF Dedicated Outdoor Air System with ERV. I cannot decide which is a good method to simulate this VRF Dedicated Outdoor Air System with ERV. It seems that the HVAC template DOAS cannot been assigned to VRF system. Is there any good methodology for this VRF DOAS ERV system? Thanks for the help.

Stan Ho

 



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___
Attachment not found:
C:\Users\lklawrie\Downloads\Embedded\image00194.jpg
Attachment not found:
C:\Users\lklawrie\Downloads\Embedded\image00243.jpg