[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: Advisory Messages for LEED EAp2 form
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] Re: Advisory Messages for LEED EAp2 form
- From: "billysonny1" <bscr_14@xxxxxxxxxxx>
- Date: Wed, 14 Aug 2013 17:42:50 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Wed, 14 Aug 2013 11:42:59 -0600
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=echoe; t=1376502176; bh=ToFD/TgUXooraE5PdPnK2F2WyfiUkvrD1jmrg8kjvNY=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:In-Reply-To:User-Agent:X-Mailer:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=WvtX+4JlmvAAy7Wpfg6bKwZfOwOfmYaZKY5+63QrImN9/zxKfvN2Jk8R7QY8UWeDzflI0WPx7BMP3nU6k6VItmOOjOMHwwTC0lyCGfv+GQCa/15FuB/zwydl8Nf1LA73/dxcdPuqB6/k4m45P0wzDhyPTGnqElIBtzr8mBQf+s4=
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=echoe; d=yahoogroups.com; b=IZmycbty9J5LYovmQtHHbeH5hde0oYY1sp9W1wH/0RNZYz3qTqXS+0homki12uqb4WynMilY2ijXr/rtY4cw5uGQPRl9Yn3KHpDX2GcdGG1J+pnQhs7i8S5v7ZNUjh/Jr2/6Bu4R7x9HdP86DRTxmb9fmbNJaa2ylPGyKBLCMsw=;
- Envelope-to: linda@xxxxxxxxxxxxxx
- In-reply-to: <CAPsP_xQ1D+PMt-snMqLOqAU86qp=Y-j0D++7BKe_jLAkrd51Gg@mail.gmail.com>
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
Thanks for your reply Jeremiah,
This is part of the Error log file for one of my baseline simulations (0ยบ).
Please advice,
Thanks in advance.
Billy Condor.
Program Version,EnergyPlus-64 7.0.0.036, 08/08/2013 10:50,IDD_Version 7.0.0.036
************* Beginning Zone Sizing Calculations
** Warning ** Site:GroundTemperature:BuildingSurface: Some values fall outside the range of 15-25C.
** ~~~ ** These values may be inappropriate. Please consult the Input Output Reference for more details.
** Warning ** Detached shading effects are ignored when Solar Distribution = MinimalShadowing
** Severe ** GetSurfaceData: Some Outward Facing angles of subsurfaces differ significantly from flat roof/floor base surface.
** ~~~ ** Fixes will be attempted to align subsurface with base surface.
** ~~~ ** ...use Output:Diagnostics,DisplayExtraWarnings; to show more details on individual surfaces.
************* GetSurfaceData: There were 9 subsurfaces whose orientation (azimuth) could not be fixed to align with the base surface.
************* Shadowing calculations may be inaccurate. Use Output:Diagnostics,DisplayExtraWarnings; for details.
** Warning ** CalcSurfaceCentroid: 2 Surfaces have the Z coordinate < 0.
** ~~~ ** ...in any calculations, Wind Speed will be 0.0 for these surfaces.
** ~~~ ** ...in any calculations, Outside temperatures will be the outside temperature + 9.750E-003 for these surfaces.
** ~~~ ** ...that is, these surfaces will have conditions as though at ground level.
** Warning ** GetSurfaceData: There are 4 coincident/collinear vertices; These have been deleted unless the deletion would bring the number of surface sides < 3.
** ~~~ ** For explicit details on each problem surface, use Output:Diagnostics,DisplayExtraWarnings;
** Warning ** CheckUsedConstructions: There are 5 nominally unused constructions in input.
** ~~~ ** For explicit details on each unused construction, use Output:Diagnostics,DisplayExtraWarnings;
************* Beginning System Sizing Calculations
** Warning ** ManageSizing: For a plant sizing run, there must be at least 1 Sizing:Plant object input. SimulationControl Plant Sizing option ignored.
************* Testing Individual Branch Integrity
************* All Branches passed integrity testing
************* Testing Individual Supply Air Path Integrity
************* All Supply Air Paths passed integrity testing
************* Testing Individual Return Air Path Integrity
************* All Return Air Paths passed integrity testing
************* No node connection errors were found.
************* Beginning Simulation
** Warning ** Coil:Cooling:DX:SingleSpeed "AIR LOOP/SOTANO AHU/1 UNITARY DX COOLING COIL" - Air volume flow rate per watt of rated total cooling capacity is out of range at 1.127E-005 m3/s/W.
** ~~~ ** Environment=AULARIO, at Simulation time=01/01 00:10 - 00:15
** ~~~ ** Expected range for VolumeFlowPerRatedTotalCapacity=[2.684E-005--6.713E-005]
** ~~~ ** Possible causes include inconsistent air flow rates in system components,
** ~~~ ** or variable air volume [VAV] system using incorrect coil type.
** Warning ** Coil:Cooling:DX:SingleSpeed "AIR LOOP/SOTANO AHU/1 UNITARY DX COOLING COIL" - Full load outlet air dry-bulb temperature < 2C. This indicates the possibility of coil frost/freeze. Outlet temperature = -25.14 C.
** ~~~ ** ...Occurrence info = AULARIO, 01/01 00:10 - 00:15
** ~~~ ** ... Possible reasons for low outlet air dry-bulb temperatures are: This DX coil
** ~~~ ** 1) may have a low inlet air dry-bulb temperature. Inlet air temperature = 20.661 C.
** ~~~ ** 2) may have a low air flow rate per watt of cooling capacity. Check inputs.
** ~~~ ** 3) is used as part of a HX assisted cooling coil which uses a high sensible effectiveness. Check inputs.
** Warning ** Enthalpy out of range (PsyTsatFnHPb)
** ~~~ ** Routine=CalcDoe2DXCoil, Environment=AULARIO, at Simulation time=01/01 00:23 - 00:30
** ~~~ ** Enthalpy=-48083.47942 Pressure= 100900.00
** ~~~ ** Initial Resultant Temperature= -59.98
** Warning ** Calculated Humidity Ratio invalid (PsyWFnTdbH)
** ~~~ ** Routine=CalcDoe2DXCoil, Environment=AULARIO, at Simulation time=01/01 00:23 - 00:30
** ~~~ ** Dry-Bulb= -59.98 Enthalpy= -65947.179
** ~~~ ** Calculated Humidity Ratio= -2.3718E-003 ... Humidity Ratio set to .00001
** Warning ** WriteVeriSumTable: InputVerificationsAndResultsSummary: Wall area based on [>=60,<=120] degrees (tilt) as walls
** ~~~ ** differs ~18.3% from user entered Wall class surfaces. Degree calculation based on ASHRAE 90.1 wall definitions.
** ~~~ ** Calculated based on degrees=[8085.092] m2, Calculated from user entered Wall class surfaces=[6833.452] m2.
** ~~~ ** Check classes of surfaces and tilts for discrepancies.
************* Simulation Error Summary *************
** Warning ** The following Report Variables were requested but not generated
** ~~~ ** because IDF did not contain these elements or misspelled variable name -- check .rdd file
************* Key=SOTANO:DEPOSITO, VarName=ZONE MECHANICAL VENTILATION AIR CHANGE RATE, Frequency=Monthly
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Jeremiah Crossett <jcrossett@...> wrote:
>
> The rule is that you must understand the warning and be able to explain it.
> Does not really matter what the warning is, just that you understand why it
> does not matter. The question then is, why is this warning happening and
> why does it not matter? Could you paste the warning into the body of your
> email..?
>
>
> *
> *
> *
> *
> *Jeremiah D. Crossett | Senior Analyst | Phase Change Energy Solutions*
> *
> 120 E. Pritchard St. | Asheboro, NC 27203 | Mobile 503-688-8951
> www.phasechange.com
> *
>
> *
> *
> *
> *
>
>
>
> On Mon, Aug 12, 2013 at 9:11 AM, billysonny1 <bscr_14@...> wrote:
>
> > **
> >
> >
> > Hello dear forum,
> >
> > For LEED EAp2 form, I got over 2 million warning messages and 1 error
> > message recorded in the Error log file, the results say the simulation was
> > completed successfully, though.
> >
> > So, I have two specific questions:
> > 1. Where can I find in the reports the 'Number of defaults overriden'?
> > 2. According to your experience, do you consider that a lot of Warning
> > messages would make the LEED reviewer ask for a clarification?
> >
> > Thanks in advance,
> >
> > Billy Condor.
> >
> >
> >
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/