Jaime,
Your main problem seems to be that your DX coil is missing a setpoint. I run full weather simulations all the time with auto-sizing and do not â??Run Simulation for Sizing Periodsâ??. Whenever autosizing is used, you must define DesignDays (but the simulation need not include the sizing periods)
James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Jaime Zuluaga Machado
Sent: Thursday, August 15, 2013 12:52 PM
To: EnergyPlus Suppport Yahoo
Subject: [EnergyPlus_Support] HVAC doubt
How I
do work the HVAC system with the Weather File and no with Design Day.
When i change my Design Day the next error appears:
nput file has requested Sizing Calculations but no Simulations are requested (in SimulationControl object). Succeeding warnings/errors may be confusing.
** Severe ** Sizing: Coil:Cooling:DX:SingleSpeed "OS:COIL:COOLING:DX:SINGLESPEED 1": Rated air volume flow rate per watt of rated total cooling capacity is out of range.
** ~~~ ** Min Rated Vol Flow Per Watt=[4.027E-005], Rated Vol Flow Per Watt=[6.997E-005], Max Rated Vol Flow
Per Watt=[6.041E-005]. See Input-Output Reference Manual for valid range.
** Severe ** CoilSystem:Cooling:DX: Missing temperature setpoint for DX unit= OS:COIL:COOLING:DX:SINGLESPEED 1 COILSYSTEM
** ~~~ ** use a Setpoint Manager to establish a setpoint at the unit control node.
** Fatal ** Previous severe set point errors cause program termination
...Summary of Errors that led to program termination:
..... Reference severe error
count=2
..... Last severe error=CoilSystem:Cooling:DX: Missing temperature setpoint for DX unit= OS:COIL:COOLING:DX:SINGLESPEED 1 COILSYSTEM