|
Jaime, The error message says “Input file has requested Sizing Calculations�” That means you have ann autosizing field in the IDF somewhere. If you replace it with a specific capacity value, that message will go away. You must still address the DX coil that is missing a setpoint and may need to address the flow / watt warning for the DX coil. James V Dirkes II, PE, BEMP, LEED AP From: Jaime Zuluaga Machado [mailto:jaimezuluagam@xxxxxxxxx] Thanks James, Let me explain what I want to do; I am doing a simulation No looking for an auto-sizing, I just want to know the results of the actual conditions of a building, I get all variables, like internal loads, weather file, construction materials, schedules, and even the HVAC equipment. So I do not know why the program get problem with the Design Day file if I do not want to do with this. Thanks in advance. Jaime Zuluaga M From: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx> Jaime, Your main problem seems to be that your DX coil is missing a setpoint. I run full weather simulations all the time with auto-sizing and do not “Run Simulation for Sizing Periods”. Whenever autosizing is used, you must define DesignDays (but the simulation need not include the sizing periods) James V Dirkes II, PE, BEMP, LEED AP From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Jaime Zuluaga Machado Hi! How I do work the HVAC system with the Weather File and no with Design Day.
nput file has requested Sizing Calculations but no Simulations are requested (in SimulationControl object). Succeeding warnings/errors may be confusing. ** Severe ** Sizing: Coil:Cooling:DX:SingleSpeed "OS:COIL:COOLING:DX:SINGLESPEED 1": Rated air volume flow rate per watt of rated total cooling capacity is out of range. ** ~~~ ** Min Rated Vol Flow Per Watt=[4.027E-005], Rated Vol Flow Per Watt=[6.997E-005], Max Rated Vol Flow Per Watt=[6.041E-005]. See Input-Output Reference Manual for valid range. ** Severe ** CoilSystem:Cooling:DX: Missing temperature setpoint for DX unit= OS:COIL:COOLING:DX:SINGLESPEED 1 COILSYSTEM ** ~~~ ** use a Setpoint Manager to establish a setpoint at the unit control node. ** Fatal ** Previous severe set point errors cause program termination ...Summary of Errors that led to program termination: ..... Reference severe error count=2 ..... Last severe error=CoilSystem:Cooling:DX: Missing temperature setpoint for DX unit= OS:COIL:COOLING:DX:SINGLESPEED 1 COILSYSTEM Jaime Zuluaga M __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |