[EnergyPlus_Support] Plant temperatures are getting far too cold
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] Plant temperatures are getting far too cold
- From: "mariasole297" <mariasole297@xxxxxxxxx>
- Date: Thu, 22 Aug 2013 10:03:28 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Thu, 22 Aug 2013 06:45:19 -0600
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=echoe; t=1377175498; bh=Oa1IOW17/FkBer6zOjXu3bqUcUaZVkQNCxcW1eUHb4Y=; h=Received:Received:X-Yahoo-Newman-Id:Received:Received:Received:Received:DKIM-Signature:Received:Received:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:User-Agent:X-Mailer:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:X-Yahoo-Profile:X-eGroups-Approved-By:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=5AjIGiFI3DRyo+gxTuzWUI34UjgbnEI2bnxKjB4CWCHlJS6kYe02nLxX+wO/gU2wu/KCZ3ZPb/flSJvAiurN/8E1y9ZBHJJ3cGv55U7Pa3J025EJsb2tmTd3HkhR7zi24bDBtST7oFyPzdwjLseS5VXnAYzlOLEbwbxCBYQAl/Q=
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=echoe; t=1377175488; bh=r+fzBtMtJea33fgtaq79s3/OJkunYui4lbfA5zoNWLk=; h=Received:Received:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:X-Received:Date:To:Message-ID:User-Agent:MIME-Version:Content-Type:Content-Transfer-Encoding:X-Mailer:X-Yahoo-Newman-Property:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:Subject:X-Yahoo-Group-Post:X-Yahoo-Profile:X-YGroups-SubInfo:Sender:X-eGroups-Approved-By:X-eGroups-Auth; b=g6VxiSQK7vJCPTxpqeCWMbX3KTn/1hLzHKFlKXnscFreIWBJMtR81lCmf+9sAsUf/RNno4Rw0zypjZp+48AxHM6jXSwZK0Owzayq7sGsM3gG1uFCjrhQAIZqAdK1ep2fXpAQxY28NCsWE8loQ3VryfJh7eDL/E+I1wfEGL/sYrY=
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=echoe; d=yahoogroups.com; b=MiU4CCIwybYV8hDl+YU9mYSvjYzEuLvKB1e3/KNkS6iAf1MTL9oUimTMTK70waaDCpayqGvfXXzCxVh81EwVuf2WGdfBaEIcJKHeHMq+H/OLVaKzxmU6rqxoJQWc0UlNr0297C3QOwf4ZPrx5s31xi5T4pxKtSdgLWL7smweGBc=;
- Envelope-to: linda@xxxxxxxxxxxxxx
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
Hi,
i'm tring to simulate the following heating and cooling system:
Groung heat exchanger+ heat pump+ heating/cooling floor
When I start the simulation E+ always returns this sever error.
** Severe ** Plant temperatures are getting far too cold, check controls and relative loads and capacities
** ~~~ ** Environment=SENZA TITOLO, at Simulation time=05/08 19:16 - 19:19
** ~~~ ** PlantLoop Name (SupplySide)= CHW LOOP
** ~~~ ** PlantLoop Setpoint Temperature=6.7 {C}
** ~~~ ** PlantLoop Inlet Node (SupplySide) does not have a Setpoint.
** ~~~ ** PlantLoop Inlet Node (DemandSide) does not have a Setpoint.
** ~~~ ** PlantLoop Outlet Node (SupplySide) has a Setpoint.
** ~~~ ** PlantLoop Outlet Node (DemandSide) does not have a Setpoint.
** ~~~ ** PlantLoop Outlet Node (SupplySide) "CHW LOOP SUPPLY SIDE OUTLET" has temperature=-105.3 {C}
** ~~~ ** PlantLoop Inlet Node (SupplySide) "CHW LOOP SUPPLY SIDE INLET" has temperature=7.1 {C}
** ~~~ ** PlantLoop Minimum Temperature=1.0 {C}
** ~~~ ** PlantLoop Maximum Temperature=98.0 {C}
** ~~~ ** PlantLoop Flow Request (SupplySide)=0.0 {kg/s}
** ~~~ ** PlantLoop Flow Request (DemandSide)=0.1 {kg/s}
** ~~~ ** PlantLoop Node (SupplySide) "CHW LOOP SUPPLY SIDE OUTLET" has mass flow rate =0.1 {kg/s}
** ~~~ ** PlantLoop PumpHeat (SupplySide)=3.4 {W}
** ~~~ ** PlantLoop PumpHeat (DemandSide)=0.0 {W}
** ~~~ ** PlantLoop Cooling Demand=218.9 {W}
** ~~~ ** PlantLoop Heating Demand=0.0 {W}
** ~~~ ** PlantLoop Demand not Dispatched=0.0 {W}
** ~~~ ** PlantLoop Unmet Demand=62323.8 {W}
** ~~~ ** PlantLoop Capacity=120000.0 {W}
** ~~~ ** PlantLoop Capacity (SupplySide)=120000.0 {W}
** ~~~ ** PlantLoop Capacity (DemandSide)=0.0 {W}
** ~~~ ** PlantLoop Operation Scheme=CHW LOOP OPERAZIONE
** ~~~ ** PlantLoop Operation Dispatched Load = 218.9 {W}
** ~~~ ** PlantLoop Operation Dispatched Load (SupplySide)= 218.9 {W}
** ~~~ ** PlantLoop Operation Dispatched Load (DemandSide)= 0.0 {W}
** ~~~ ** Branches on the Loop.
I've tried to check the GSHPSimple-GLHE in the ExampleFile and get some changes but it doesn't work... Any ideas????
Maria
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/