If the simulation stops after you see Warmup {1} on the DOS screen, then you can tell the program to report during warmup so you can see what's happening.

Output:Diagnostics,ReportDuringWarmup;

On 8/22/2013 9:43 AM, Maria Sole wrote:
I have already tried to change the CHW Loop Setpoint Manager but the severe error is always the same, i mean the outlet temperature is every time different but is always too low.


From: energyplus_mimis <welma.pereira@xxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Thursday, August 22, 2013 2:57 PM
Subject: [EnergyPlus_Support] Re: Plant temperatures are getting far too cold

 

It seems like your set point temperature for the plant loop is very low, check the temperature schedule in the SetpointManager:Scheduled

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "mariasole297" <mariasole297@...> wrote:
>
> Hi,
> i'm tring to simulate the following heating and cooling system:
>
> Groung heat exchanger+ heat pump+ heating/cooling floor
>
> When I start the simulation E+ always returns this sever error.
>
> ** Severe ** Plant temperatures are getting far too cold, check controls and relative loads and capacities
> ** ~~~ ** Environment=SENZA TITOLO, at Simulation time=05/08 19:16 - 19:19
> ** ~~~ ** PlantLoop Name (SupplySide)= CHW LOOP
> ** ~~~ ** PlantLoop Setpoint Temperature=6.7 {C}
> ** ~~~ ** PlantLoop Inlet Node (SupplySide) does not have a Setpoint.
> ** ~~~ ** PlantLoop Inlet Node (DemandSide) does not have a Setpoint.
> ** ~~~ ** PlantLoop Outlet Node (SupplySide) has a Setpoint.
> ** ~~~ ** PlantLoop Outlet Node (DemandSide) does not have a Setpoint.
> ** ~~~ ** PlantLoop Outlet Node (SupplySide) "CHW LOOP SUPPLY SIDE OUTLET" has temperature=-105.3 {C}
> ** ~~~ ** PlantLoop Inlet Node (SupplySide) "CHW LOOP SUPPLY SIDE INLET" has temperature=7.1 {C}
> ** ~~~ ** PlantLoop Minimum Temperature=1.0 {C}
> ** ~~~ ** PlantLoop Maximum Temperature=98.0 {C}
> ** ~~~ ** PlantLoop Flow Request (SupplySide)=0.0 {kg/s}
> ** ~~~ ** PlantLoop Flow Request (DemandSide)=0.1 {kg/s}
> ** ~~~ ** PlantLoop Node (SupplySide) "CHW LOOP SUPPLY SIDE OUTLET" has mass flow rate =0.1 {kg/s}
> ** ~~~ ** PlantLoop PumpHeat (SupplySide)=3.4 {W}
> ** ~~~ ** PlantLoop PumpHeat (DemandSide)=0.0 {W}
> ** ~~~ ** PlantLoop Cooling Demand=218.9 {W}
> ** ~~~ ** PlantLoop Heating Demand=0.0 {W}
> ** ~~~ ** PlantLoop Demand not Dispatched=0.0 {W}
> ** ~~~ ** PlantLoop Unmet Demand=62323.8 {W}
> ** ~~~ ** PlantLoop Capacity=120000.0 {W}
> ** ~~~ ** PlantLoop Capacity (SupplySide)=120000.0 {W}
> ** ~~~ ** PlantLoop Capacity (DemandSide)=0.0 {W}
> ** ~~~ ** PlantLoop Operation Scheme=CHW LOOP OPERAZIONE
> ** ~~~ ** PlantLoop Operation Dispatched Load = 218.9 {W}
> ** ~~~ ** PlantLoop Operation Dispatched Load (SupplySide)= 218.9 {W}
> ** ~~~ ** PlantLoop Operation Dispatched Load (DemandSide)= 0.0 {W}
> ** ~~~ ** Branches on the Loop.
>
>
> I've tried to check the GSHPSimple-GLHE in the ExampleFile and get some changes but it doesn't work... Any ideas????
> Maria
>




-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 50 Years


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___