Hi,
I have attached the idf
file, the following errors are displayed:
** Severe ** Sizing: Coil:Cooling:DX:SingleSpeed "OS:COIL:COOLING:DX:SINGLESPEED 1": Rated air volume flow rate per watt of rated total cooling capacity is out of range.
** ~~~ ** Min Rated Vol Flow Per Watt=[4.027E-005], Rated Vol Flow Per Watt=[3.074E-005], Max Rated Vol Flow Per Watt=[6.041E-005]. See Input-Output Reference Manual for valid
range.
** Severe ** For object = Coil:Cooling:DX:SingleSpeed, name = "OS:COIL:COOLING:DX:SINGLESPEED 1"
** ~~~ ** Calculated outlet air relative humidity greater than 1. The combination of
** ~~~ ** rated air volume flow rate, total cooling capacity and sensible heat ratio yields coil exiting
** ~~~ ** air conditions
above the saturation curve. Possible fixes are to reduce the rated total cooling
** ~~~ ** capacity, increase the rated air volume flow rate, or reduce the rated sensible heat ratio for this coil.
** ~~~ ** If autosizing, it is recommended that all three of these values be autosized.
** ~~~ ** ...Inputs used for calculating cooling coil bypass factor.
** ~~~ ** ...Inlet Air Temperature = 26.67 C
** ~~~ ** ...Outlet Air Temperature = 4.31 C
** ~~~ ** ...Inlet Air Humidity Ratio = 1.125000E-002 kgWater/kgDryAir
** ~~~ ** ...Outlet Air Humidity Ratio = 6.976137E-003 kgWater/kgDryAir
** ~~~ ** ...Total Cooling Capacity used in calculation = 24000.00 W
** ~~~ ** ...Air Mass Flow Rate used in calculation = 0.713176 kg/s
** ~~~ ** ...Air Volume Flow Rate used in calculation = 0.737977 m3/s
** ~~~ ** ...Air Volume Flow Rate per Watt of Rated Cooling Capacity is also out of bounds at = 3.0749021E-005 m3/s/W
** ~~~ ** During Warmup, Environment=MEDELLÃ?N, at Simulation time=03/21 00:00 - 00:15
** Fatal ** Check and revise the input data for this coil before rerunning the simulation.
...Summary of Errors that led to program termination:
How can I change the "Rated air volume flow rate per watt" without change the "Rated Total Cooling Capacity"?
Thanks
Jaime Zuluaga
M
From: Jason Kirkpatrick <jason.alan.kirkpatrick@xxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Thursday, 22 August 2013, 17:06
Subject: Re: [EnergyPlus_Support] Zone Cooling Design Supply Air
Temperature
Jaime,
while the field that you were asking about (Cooling SAT) will not change with changes to the DDY file, the system size will, which is likely why you're seeing a change in the flow per power metric. You may have hard sized the power consumption of the unit, but now are changing the size of the unit by editing the outdoor air conditions used for sizing. (my best guess)
You might get a better answer by posting your file however.
Jason