The problem has some progress but still some strange things going. Check everything 3 times. Attached *.rdd. Whats going on?
RVI:
ASP1308-C-SYS-CENTR.eso
ASP1308-C-SYS-CENTR_SHOPS.csv
Site Outdoor Air Drybulb Temperature
SHOPS,Zone Mean Air Temperature
SHOPS,Zone Thermostat Air Temperature
SHOPS,Zone Thermostat Heating Setpoint Temperature
SHOPS,Zone Thermostat Cooling Setpoint Temperature
SHOPS,Zone Cooling Setpoint Not Met Time
SHOPS,Zone Heating Setpoint Not Met Time
Baseboard Total Heating Rate
SHOPS Heating Coil,Heating Coil Heating Rate
SHOPS DOAS Heating Coil,Heating Coil Heating Rate
SHOPS Cooling Coil,Cooling Coil Total Cooling Rate
SHOPS DOAS Cooling Coil,Cooling Coil Total Cooling Rate
SHOPS DOAS,Air System Outdoor Air Flow Fraction
SHOPS DOAS,Air System Outdoor Air Minimum Flow Fraction
SHOPS DOAS,Air System Outdoor Air Mass Flow Rate
SHOPS DOAS,Air System Mixed Air Mass Flow Rate
SHOPS DOAS Heat Recovery,Heat Exchanger Total Heating Rate
SHOPS DOAS Heat Recovery,Heat Exchanger Total Cooling Rate
SHOPS Supply Fan Inlet,System Node Temperature
SHOPS Cooling Coil Outlet,System Node Temperature
SHOPS Supply Inlet,System Node Temperature
SHOPS DOAS Mixed Air Outlet,System Node Temperature
SHOPS DOAS Cooling Coil Outlet,System Node Temperature
SHOPS DOAS Heating Coil Outlet,System Node Temperature
0
readvars.audit:
ReadVarsESO
processing:ASP1308-C-SYS-CENTR.rvi
input file:ASP1308-C-SYS-CENTR.eso
output file:ASP1308-C-SYS-CENTR_SHOPS.csv
number variables requested for output= 15
found/finding:
1 Site Outdoor Air Drybulb Temperature
1 SHOPS:Zone Mean Air Temperature
0 SHOPS:Zone Thermostat Air Temperature
1 SHOPS:Zone Thermostat Heating Setpoint Temperature
1 SHOPS:Zone Thermostat Cooling Setpoint Temperature
1 SHOPS:Zone Cooling Setpoint Not Met Time
0 SHOPS:Zone Heating Setpoint Not Met Time
2 Baseboard Total Heating Rate
1 SHOPS Heating Coil:Heating Coil Heating Rate
1 SHOPS DOAS Heating Coil:Heating Coil Heating Rate
1 SHOPS Cooling Coil:Cooling Coil Total Cooling Rate
1 SHOPS DOAS Cooling Coil:Cooling Coil Total Cooling Rate
1 SHOPS DOAS:Air System Outdoor Air Flow Fraction
1 SHOPS DOAS:Air System Outdoor Air Minimum Flow Fraction
1 SHOPS DOAS:Air System Outdoor Air Mass Flow Rate
1 SHOPS DOAS:Air System Mixed Air Mass Flow Rate
0 SHOPS DOAS Heat Recovery:Heat Exchanger Total Heating Rate
0 SHOPS DOAS Heat Recovery:Heat Exchanger Total Cooling Rate
0 System Node Temperature
0 SHOPS Cooling Coil Outlet:System Node Temperature
0 SHOPS Supply Inlet:System Node Temperature
0 SHOPS DOAS Mixed Air Outlet:System Node Temperature
0 SHOPS DOAS Cooling Coil Outlet:System Node Temperature
0 SHOPS DOAS Heating Coil Outlet:System Node Temperature
ReadVars Run Time=00hr 00min 0.09sec
ReadVarsESO program completed successfully.
BR,
Artem Zhukov
HVAC Consultant/Building Simulation Engineer

Mob.: +420 774 081 898
SKYPE: zhukov_artem
View profile
Web Cal
BE RESPONSIBLE. THINK ABOUT THE ENVIRONMENT BEFORE PRINTING THIS E-MAIL OR ITS ATTACHMENTS
Oh, or "variable name"
Input File eplusout.eso
Output File eplusout.csv
Site Outdoor Drybulb Temperature
Zone Air Temperature
Zone Air Humidity Ratio
Zone Air System Sensible Cooling Rate
Zone Air System Sensible Heating Rate
Zone Total Internal Latent Gain Rate
On Mon, Sep 16, 2013 at 7:29 AM, Edwin Lee <leeed2001@xxxxxxxxx> wrote:
Don't put input file or output file in the eso.
eplusout.eso
eplusout.csv
Variable Name Site Outdoor Drybulb Temperature
Variable Name Zone Air Temperature
Variable Name Zone Air Humidity Ratio
Variable Name Zone Air System Sensible Cooling Rate
Variable Name Zone Air System Sensible Heating Rate
Variable Name Zone Total Internal Latent Gain Rate
On Mon, Sep 16, 2013 at 1:06 AM, Artem Zhukov <artem.zhukov@xxxxxxxxxxx> wrote:
Here is my input:
Input File eplusout.eso
Output File eplusout.csv
Variable Name Site Outdoor Drybulb Temperature
Variable Name Zone Air Temperature
Variable Name Zone Air Humidity Ratio
Variable Name Zone Air System Sensible Cooling Rate
Variable Name Zone Air System Sensible Heating Rate
Variable Name Zone Total Internal Latent Gain Rate
BR,
Artem Zhukov
HVAC Consultant/Building Simulation Engineer

Mob.: +420 774 081 898
SKYPE: zhukov_artem
View profile
Web Cal
BE RESPONSIBLE. THINK ABOUT THE ENVIRONMENT BEFORE PRINTING THIS E-MAIL OR ITS ATTACHMENTS
What are the contents of your my.rvi file?
Good day I want to use ReadVarsESO.exe program to generate csv. But met the problem that the program wont recognize the input file, nevertheless the file eplusout.eso exist in the same folder.

BR,
Artem Zhukov
HVAC Consultant/Building Simulation Engineer
![logo]()
Mob.: +420 774 081 898
SKYPE: zhukov_artem
View profile
Web Cal
BE RESPONSIBLE. THINK ABOUT THE ENVIRONMENT BEFORE PRINTING THIS E-MAIL OR ITS ATTACHMENTS
--