1) Yes and yes. Yes. The "Rated" R-Vales must be calculated correctly using the film values in that section if you are modelling as per Appx G. It is also sometimes required to de-rate some layers (eg. Framing/insulation layers) to account for the thermal breaks as the standard dictates. Yes. Rated values are different as they are rated by different norms in different countries. You can and should hand calculate the rated values as per the required norm. But don't compare the rated value as per one norm to that value as calculated by another norm. 2) you already know which film values to apply and how, judging by your post. The bit in the middle is just the sum of the layer by layer R-values (R=thickness/conduction_coeffecient... if I remember correctly). The key is therefore to set the conduction coefficient(s). I recommend the hand calculation as excersize. Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity) i. A. Jean Marais b.i.g. bechtold Tel. +49 30 6706662-23
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.