It seems the radiant system is not turning on or is turning off due to condensation risk. 1) check that the radiant equipment has the higher priority in the equipmentlist object. 2) check that the setpoint schedule for the radiant cooling equipment is lower than that of the zone cooling setpoint, i.e. that of the fancoil. 3) set the chilled water temperature to the radiant system somewhere between 18 to 20 deg C and report the output variable which shows if and when the radiant system is turning off due to condensation risk. Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity) i. A. Jean Marais b.i.g. bechtold Tel. +49 30 6706662-23
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.