It seems the radiant system is not turning on or is turning off due to condensation risk.
1) check that the radiant equipment has the higher priority in the equipmentlist object.
2) check that the setpoint schedule for the radiant cooling equipment is lower than that of the zone cooling setpoint, i.e. that of the fancoil.
3) set the chilled water temperature to the radiant system somewhere between 18 to 20 deg C and report the output variable which shows if and when the radiant system is turning off due to condensation risk.
Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity)
i. A.
Jean Marais
b.i.g. bechtold
Tel. +49 30 6706662-23
Sir
I did the modeling of radiant cooling system with fan coil unit and i faced some problem as
I want that all the cooling load of zone is handled by radiant system and remaining load mostly latent load is handled by fan coil unit but load on fan coil unit is almost constant and not varying with occupancy change.
Condensation problem is continuous occurring when i increase the leaving chilled water temperature of the chiller which is equipped with fan coil unit
i am using variable flow radiant system but the flow is constant and only return temperature of chilled water of chiller( equipped with radiant system ) is varying according to the
load