[EnergyPlus_Support] RE: Football Stadium Modeling





I wrote a short ems to do this for freeze protection trace heating on piping... you can adjust it for pitch heating.


!!!External equipment
  Exterior:FuelEquipment,
    PipeFrostProtection,
    Electricity,
    FrostFreeSch,
    5850,  !26 W/m @ 225 m =
    PipeFrostProtection;  
  Schedule:Compact,
    FrostFreeSch,            !- Name
    Any Number,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00,0;          !- Field 3
!!!!!FROST FREE EMS!!!!!!!!!!!!!!!!!!!!!    
!ODA dry-bulb temperature sensor
EnergyManagementSystem:Sensor,
ODA_T, ! Sensor Name...reporting schedule properties
Environment, ! Output:Variable or Output:Meter Index Key Name Zone/Sys Thermostat Cooling Setpoint  Output:Variable,*,Zone/Sys Thermostat Cooling Setpoint,hourly; !- Zone Average [C]
Site Outdoor Air Drybulb Temperature; ! Output:Variable or Output:Meter Name
EnergyManagementSystem:Actuator,
FrostFreeOn, !- Name
FrostFreeSch,  !- Actuated Component Unique Name...in this case !-EnergyManagementSystem:Actuator Available,COOLING SP SCH,Schedule:Compact,Schedule Value,[ ]
Schedule:Compact, !- Actuated Component Type
Schedule Value ; !- Actuated Component Control Type
!***Program Calling Proceedure***
EnergyManagementSystem:ProgramCallingManager,
FrostFreeCM, ! Name
AfterPredictorAfterHVACManagers, ! EnergyPlus Model Calling Point
FrostFree; ! Program 1 Name
!
!***Main Program***
!******************
EnergyManagementSystem:Program,
FrostFree, ! Program 1 Name
!
IF (ODA_T < 4),
SET  FrostFreeOn = 1,
ELSE,
SET  FrostFreeOn = Null,
ENDIF;



---In EnergyPlus_Support@xxxxxxxxxxxxxxx, <energyplus_support@xxxxxxxxxxxxxxx> wrote:

Dear all,
I have a project for a football stadium which has underground heating for the playing pitch area. The stadium is open to the outdoors. The question is: Can such stadium pitch heating be modeled in EnergyPlus? if yes, how? and also how to account for the impact on outdoor environment factors effects (like wind or rain) caused by seating and exterior walls (which are shaped as displaced high columns around seating with open spaces between them), also there is the open structure above

__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.