[EnergyPlus_Support] Re: Football Stadium Modeling
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] Re: Football Stadium Modeling
- From: "hisham.rashrash" <hisham.rashrash@xxxxxxxxx>
- Date: Tue, 22 Oct 2013 11:08:41 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Tue, 22 Oct 2013 05:08:47 -0600
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=echoe; t=1382440124; bh=ZnXzls2u35zhRYMdVi+rANipYEmbg9Zu5uIXxACNVgc=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:In-Reply-To:User-Agent:X-Mailer:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=i6fo7+Byx6o5oFz7/O4ZpWgTN+x6P7uIcEeLO+0z3fKGzDxr/V1avTFnSjAoy5aMTLRhdtePyzGhJkJnBlFruvQRda6DeXCGlxnNOAEXa26+W4AAZUUICeGLBfuK/gn4TmMGw0SjlTi1R4GuncViDnuD+/V+n9w1eTcbM6YRAdk=
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=echoe; d=yahoogroups.com; b=y4gjb3S1BDGfTLt3w3RSTm/DBSY/BJhG7n6JUnvogJyZOWOHUEIz7GNXDX9LLz28AHHvfXOOSGlgyrB2KhvjF+mgRkELBcfvWYWoNes9JhPHKLKcEWDf8MP9WUb1e4Q7bcXHAGcF61GxF+p2ZmUv9dWY4JieAzSYO+Vl9EuNUb8=;
- Envelope-to: linda@xxxxxxxxxxxxxx
- In-reply-to: <l45ffh+sfhbik@YahooGroups.com>
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
Many thanks for your help, but please, can you make the EMS input a little more clearer, I haven't used EMS before. This would be very kind of you.
Thank you very much.
Best regards,
Hisham
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, <jeannieboef@...> wrote:
>
> I wrote a short ems to do this for freeze protection trace heating on piping... you can adjust it for pitch heating.
>
>
> !!!External equipment
> Exterior:FuelEquipment,
> PipeFrostProtection,
> Electricity,
> FrostFreeSch,
> 5850, !26 W/m @ 225 m =
> PipeFrostProtection;
> Schedule:Compact,
> FrostFreeSch, !- Name
> Any Number, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 24:00,0; !- Field 3
> !!!!!FROST FREE EMS!!!!!!!!!!!!!!!!!!!!!
> !ODA dry-bulb temperature sensor
> EnergyManagementSystem:Sensor,
> ODA_T, ! Sensor Name...reporting schedule properties
> Environment, ! Output:Variable or Output:Meter Index Key Name Zone/Sys Thermostat Cooling Setpoint Output:Variable,*,Zone/Sys Thermostat Cooling Setpoint,hourly; !- Zone Average [C]
> Site Outdoor Air Drybulb Temperature; ! Output:Variable or Output:Meter Name
> EnergyManagementSystem:Actuator,
> FrostFreeOn, !- Name
> FrostFreeSch, !- Actuated Component Unique Name...in this case !-EnergyManagementSystem:Actuator Available,COOLING SP SCH,Schedule:Compact,Schedule Value,[ ]
> Schedule:Compact, !- Actuated Component Type
> Schedule Value ; !- Actuated Component Control Type
> !***Program Calling Proceedure***
> EnergyManagementSystem:ProgramCallingManager,
> FrostFreeCM, ! Name
> AfterPredictorAfterHVACManagers, ! EnergyPlus Model Calling Point
> FrostFree; ! Program 1 Name
> !
> !***Main Program***
> !******************
> EnergyManagementSystem:Program,
> FrostFree, ! Program 1 Name
> !
> IF (ODA_T < 4),
> SET FrostFreeOn = 1,
> ELSE,
> SET FrostFreeOn = Null,
> ENDIF;
>
>
>
>
> ---In EnergyPlus_Support@xxxxxxxxxxxxxxx, <energyplus_support@xxxxxxxxxxxxxxx> wrote:
>
> Dear all,
> I have a project for a football stadium which has underground heating for the playing pitch area. The stadium is open to the outdoors. The question is: Can such stadium pitch heating be modeled in EnergyPlus? if yes, how? and also how to account for the impact on outdoor environment factors effects (like wind or rain) caused by seating and exterior walls (which are shaped as displaced high columns around seating with open spaces between them), also there is the open structure above that resembles the roof.
>
>
> Please, see the stadium image refered by this link:
> http://img198.imageshack.us/img198/6113/y3dz.jpg http://img198.imageshack.us/img198/6113/y3dz.jpg
>
>
> Thank you very much.
>
>
> Hisham.
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://info.yahoo.com/legal/us/yahoo/utos/terms/