Re: [EnergyPlus_Support] Inability to output data for days other than Design Day





Not sure if it was called this in v7, but looking at v8, you need to tell EnergyPlus to run the simulation for weather file run periods.. that's in the SimulationControl object.
 
Often, it will look like this:
 
SimulationControl,
    Yes,                     !- Do Zone Sizing Calculation
    Yes,                     !- Do System Sizing Calculation
    Yes,                     !- Do Plant Sizing Calculation
    Yes,                     !- Run Simulation for Sizing Periods
    No;                      !- Run Simulation for Weather File Run Periods
 
In that case, you'll get sizing calcs and simulation results for ONLY the sizing periods. If you just want simulation results for the run period (and autosized equipment), you'll need to change it to:
 
SimulationControl,
    Yes,                     !- Do Zone Sizing Calculation
    Yes,                     !- Do System Sizing Calculation
    Yes,                     !- Do Plant Sizing Calculation
    No,                      !- Run Simulation for Sizing Periods
    Yes;                     !- Run Simulation for Weather File Run Periods
 


On Sat, Oct 26, 2013 at 7:55 PM, <davidwagland@xxxxxxxxxxx> wrote:
 

Hi there,


I'm very new to EnergyPlus and am trying to do a very basic model of a one-zone house for the months of February and July, profiled four times an hour, with outputs such as temperature, sensible heating/cooling etc. For some reason, however, I can only get the program to produce hourly data for my two designated Design Days in February and July (rather than for both whole months).

I am using Version 7.0 of EnergyPlus. I have defined the Timestep to be 4, the RunPeriod to be for the months of February and July and I have also designed two Design Days as 21 February and 21 July.

I just can't figure out why it will only produce data for the Design Days. Is there anywhere else I need to tell the program that it should be profiling for the RunPeriod? I'm also not really sure why I need the Design Days designated, but the program won't run without these definitions.

If anyone has any ideas to help me, I would really appreciate it!

Thanks very much,
Dave




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___