Hi Bily,



1. Good question, one I asked myself. You are right, it is the water flowrate...makes sence when you puzzle over it for long enough. Also, ASHRAE 90.1 2010 spells it out far better.


2. Another good question. Many of the same types are repeated in the Tables A, B and D making it a bit confusing...also meaning that sometimes it doesn't matter which table you use because the same equipment is meant. That being said: System Type 1,2 are listed in Table 6.8.1 D. and differentiate themselves in that the HP or AC sits on the Termanal (before or in the zone). Choosing between A and B is anything but straight forward.


Table 6.8.1. A conserns itself with units where the same working fluid is not also used for reverse function, i.e. both heating and cooling. Heating is done by gas furnace or electric.

Table 6.8.1 B conserns itself with units where the same working fluid is also used for reverse function, i.e. both heating and cooling (reversable), but may also include a electric or other reheater in cooling mode.


Anyone else like to chime in?


Jean



---In EnergyPlus_Support@xxxxxxxxxxxxxxx, <energyplus_support@xxxxxxxxxxxxxxx> wrote:

Hello dear forum, 
I have two specific questions about mechanical equipment performance requirements (addressed in the tables 6.8.1 of ASHRAE 90.1-2007). 

1. From 6.8.1G: For axial fan cooling towers, the performance required is >= 3.23 L/s.kW. Below this table, it says this: ''Cooli

__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___