RE: [EnergyPlus_Support] Re: Controller function error
Hello James,
I will check the setpoints. Thank you very much for your suggestions.
----------------------------------------
Best Regards
Ying Yan
Graduate Student
Electrical & Computer Engineering
School of Engineering
University of Connecticut
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [EnergyPlus_Support@xxxxxxxxxxxxxxx] on behalf of Jim Dirkes [jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx]
Sent: Tuesday, October 29, 2013 3:18 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: RE: [EnergyPlus_Support] Re: Controller function error
Occasionally the "Controller function is inconsistent…” error is due to setpoints that are inappropriate – e.g., heating setpoint higher than cooling setpoint. E+ doesn’t handle that very well. (Neither does a real control system!)
James V Dirkes II, PE, BEMP, LEED AP
<http://www.buildingperformanceteam.com/>www.buildingperformanceteam.com
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of jeannieboef@xxxxxxxxx
Sent: Tuesday, October 29, 2013 3:10 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Cc: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Re: Controller function error
Could you post the exact error copy paste?
Mit freundlichen Grüßen- Sent from my iPhone (excuse the brevity)
i. A.
Jean Marais
b.i.g. bechtold
Tel. +49 30 6706662-23
On 29.10.2013, at 15:40, "Yan, Ying" <<mailto:yiy11005@xxxxxxxxxxxxxx>yiy11005@xxxxxxxxxxxxxx> wrote:
>
> Hello Jill,
>
> Thank you so much for your answer. Actually I used the IDFVersionUpdater.exe to update the IDF file obtained from DesignBuilder to 8.0.0. There is no warning message. I do not know whether the error that the "Controller function is inconsistent with user specified control action = Normal action" is caused by any other reasons or not. Can you give me some suggestions?
>
> ----------------------------------------
> Best Regards
>
> Ying Yan
>
> Graduate Student
> Electrical & Computer Engineering
> School of Engineering
> University of Connecticut
> From: <mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>EnergyPlus_Support@xxxxxxxxxxxxxxx [EnergyPlus_Support@xxxxxxxxxxxxxxx] on behalf of Jill Dalglish [jill.dalglish@xxxxxxxxxxxxxxxxxxxxx]
> Sent: Tuesday, October 29, 2013 9:51 AM
> To: <mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Re: Controller function error
>
> Hello Ying Yan,
> A few things that may help if you haven't figured this out already.
> 1. If the EPLaunch version doesn't match the IDF file version, there is usually a warning saying so.
> 2. There is a "Version" object in your IDF file. If that doesn't match, you will usually get this warning.
> 3. You can try to trick the program into getting rid of this warning by just changing the version in the IDF file in a text editor, but this is merely cosmetic.
> 4. If you know your IDF version is 8.0 or the latest version, I would just download and install the latest version of EnergyPlus, then they should match.
> Good luck,
> Jill
__._,_.___
Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov
The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=30465/stime=1383081711>
Your email settings: Individual Email|Traditional
<http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJmMTViN3E1BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzEzODMwODE3MTE->Change settings via the Web (Yahoo! ID required)
Change settings via email: <mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=Email Delivery: Digest>Switch delivery to Daily Digest | Switch to Fully Featured
<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJkbmxuanZiBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMzgzMDgxNzEx>Visit Your Group | <http://info.yahoo.com/legal/us/yahoo/utos/terms/> Yahoo! Groups Terms of Use | <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> Unsubscribe
__,_._,___