[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

RE: Re: [EnergyPlus_Support] EMS actuator causing fatal error in V8.1





Dear Jean,

Thank you for your reply.


The edd file was the first thing I checked but found no trace of the "Zone Temperature Control" actuator. I've double checked the variable names and they are all matching.


The strange thing is that the edd file shows the calculated value during warmup for the SET statement containing this actuator/variable in the line traces.


To make sure that this is a problem with the V8.1 version only, I checked the edd file for V8.0 of the idf file (the one I updated to V8.1) and indeed found the following two actuators available:


EnergyManagementSystem:Actuator Available,PDEC,Zone Temperature Control,Heating Setpoint,[C]

EnergyManagementSystem:Actuator Available,PDEC,Zone Temperature Control,Cooling Setpoint,[C]


Any Idea why this is happening?


Omar Ibraheem



---In EnergyPlus_Support@xxxxxxxxxxxxxxx, <energyplus_support@xxxxxxxxxxxxxxx> wrote:

Check the edd file to see if that variable name is still correct. If you don't have an edd file you need to still code in the "verbose" statements into your code.

Mit freundlichen GrüÃ?en- Sent from my iPhone (excuse the brevity)

i. A.
Jean Marais
b.i.g. bechtold
Tel.   +49 30 6706662-23

On 05.11.2013, at 04:29, <laxoayi@...> wrote:

 

Hi all,


Using release V7.0, I setup a "Zone Temperature Control" actuator with "Cooling Setpoint" as its control type to control the setpoints of a zone with an ILAS (my setpoints change with every timestep and these in turn depend on values in a Schedule:File in case you're wondering why I'm using this actuator in the first place). There were no severe errors or warnings in the results. I've been converting the exact same idf file to work with every new release ever since including V8.0 and was having no problems. However, when converting to V8.1 I got the following fatal error:


   ** Severe  ** Invalid Actuated Component Type =ZONE TEMPERATURE CONTROL
   **   ~~~   ** Entered in EnergyManagementSystem:Actuator=PDEC_ZN_SP
   **   ~~~   ** Component Type not found
   **   ~~~   ** Review .edd file for valid component types.
   ** Severe  ** Invalid Actuated Component Unique Name =PDEC
   **   ~~~   ** Entered in EnergyManagementSystem:Actuator=PDEC_ZN_SP
   **   ~~~   ** Component Unique key name not found
   **   ~~~   ** Review edd file for valid component names.
   ** Severe  ** Invalid Actuated Component Control Type =COOLING SETPOINT
   **   ~~~   ** Entered in EnergyManagementSystem:Actuator=PDEC_ZN_SP
   **   ~~~   ** Control Type not found
   **   ~~~   ** Review edd file for valid component control types.
   **  Fatal  ** Errors found in processing Energy Management System input. Preceding condition causes termination.
   ...Summary of Errors that led to program termination:
   ..... Reference severe error count=3
   ..... Last severe error=Invalid Actuated Component Control Type =COOLING SETPOINT
   ************* Warning:  Node connection errors not checked - most system input has not been read (see previous warning).
   ************* Fatal error -- final processing.  Program exited before simulations began.  See previous error messages.
   ************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
   ************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
   ************* EnergyPlus Terminated--Fatal Error Detected. 0 Warning; 3 Severe Errors; Elapsed Time=00hr 00min  1.48sec

I've checked the "Addressed Issues" of release V8.1 to see whether this actuator has been renamed or replaced but found neither to be the case.

Is this a Bug in V8.1 or am I missing something here?

Your help is much appreciated.

Omar Ibraheem


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___