Hisham, I think that the templates are intended for somewhat common HVAC systems. The dry cooler with run around heat recovery is not one of those, so you will need to build something on your own. In the E+ world, you probably want a “FluidCooler:….” For the dry cooler. The FluidCooler.idf example file will show use of a fluid cooler. For the run-around loop, assuming that you are trying to recover energy from one air loop to another using a water loop, you will need to add a water coil in each air loop and pump water between them – this shouldn’t be too difficult! James V Dirkes II, PE, BEMP, LEED AP From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of hisham.rashrash Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.