That is a difficalt question. Software validation like BestTest and ASHRAE 140, validates software, but models are specific. The best thing would be for an independant other engineer to remodel the project using a different software. I wouldn't expect even close match (this excersize has been done for LEED vs BREEAM projects and the same project energy usage would deviate by up to 20%! Ironically, perhaps correctly, the savings against the respective baselines was a far better match). Another option of quality control is using the PRM outlined in Appendix G of ASHRAE 90.1. I find it a fantastic QA program. Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity) i. A. Jean Marais b.i.g. bechtold Tel. +49 30 6706662-23
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.