Santiago, Perhaps you should use one setpoint manager, plus a PlantEquipmentOperation: object to define the range of operation for each chiller. James V Dirkes II, PE, BEMP, LEED AP From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Santiago Velez Dear forum, I'm having some trouble controlling a Chilled water loop with two air cooled chillers in series. I would appreciate some comments on the approach. I setted a 'schedule setpoint manager' at the outlet node of each of the chillers and a 'scheduled setpoint manager' for the CHW Loop Supply Side Outlet. The goal is to have a water temperature drop of 5 C on each. And
Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.