To simulate the wood burning, you are going to have to construct a detailed pattern of heat output from the wood device. Some of the heat will be radiant and
some will be convective. Recommended cast iron stove temperature is 400F to 500F maximum. You may be able to start a fire, but have limited control over adjusting the heat output (my airtight stove does have a draft regulator that responds to the stove temperature),
so the space may be over or under heated depending on exterior conditions and fire status. An important consideration can be heat storage in mass masonry elements and radiation from stove pipes in the occupied space. For an open fireplace, you will need
to have infiltration sufficient to satisfy the chimney draft, but some stoves fireplaces include combustion air connections to outside. I suggest that you research wood heat sources more before attempting a model. Many manufacturers have detailed information about heat output from their products.
You will likely need EMS logic or a highly detailed schedule to complete your analysis…. Ned Lyon, P.E. (MA, WV) SIMPSON GUMPERTZ & HEGER
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
On Behalf Of Oscar Hernandez Hi Pascalis I simulated one time a wood boiler as a radiant system. In practice is the same. The results that I had were not so bad compared with another software. My advise is try to simulate as a radiant system. Take only count the radiant distribution over the walls. Good luck Oscar __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |