Re: [EnergyPlus_Support] humidity ratio = -999





That's a default value -- I think there was something wrong with this setpoint manager, but not sure this is  applicable.  That is an initial set value and either is never reset or something is off and that value is the fall back position.

At 07:22 AM 12/6/2013, fpasserini.tn@xxxxxxxxx wrote:


In the output as "System Node Setpoint Humidity Ratio" I get -999 kgWater/kgDryAir (constantly) in all the nodes. What can be the reason of this error?
There are AHUs for the dehumidification and I imposed

SetpointManager:MultiZone:Humidity:Maximum,
    SM 0terra mag_uff_sud2,  !- Name
    Air Loop 0terra mag_uff_sud2,  !- HVAC Air Loop Name
    0.005,                   !- Minimum Setpoint Humidity Ratio {kgWater/kgDryAir}
    0.012,                   !- Maximum Setpoint Humidity Ratio {kgWater/kgDryAir}
    Air Loop 0terra mag_uff_sud2 AHU/1 Cooling Coil Air Outlet Node;  !- Setpoint Node or NodeList Name

The values of "Site Outdoor Air Humidity Ratio Environment" are normal (between 0.006 and 0.019 kgWater/kgDryAir).


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___