Thank you Mahabir, Joe and Jean, If I understood, this Zone Component Load Summary provide a similar rapport than DOE-2 LS-B with some differences listed by Joe. The first difference is the user-input design days but If we choose SizingPeriod:WeatherFileDays” instead “SizingPeriod:DesignDay” the peak days would be the same that LS-B report, will not be? Anyway, we have to add a fictitious system to work. In my specific and actual case, I have to output the zones air temperatures to analyze the performances of a passive building. I don’t create any fictitious system so I can’t see the components loads. However, I can get a hourly report with the variable “Zone Air Temperature”. How energy plus calculates theses temperatures without calculate heat transfers by the walls and by the others zone surfaces? I didn’t set any indoor temperature setpoint to the building. Thanks again Rodrigo De : EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] De la part de Joe Huang Mahabir, Joe Huang White Box Technologies, Inc. 346 Rheem Blvd., Suite 108D Moraga CA 94556 yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx http://weather.whiteboxtechnologies.com for simulation-ready weather data (o) (925)388-0265 (c) (510)928-2683 "building energy simulations at your fingertips"
EnergyPlus (ver 8.0 onwards) does provide the similar report : Zone Component Load Summary, using decay curve methodology. The summary is only available for sizing run. For more details: E+ Engineering Reference document (1394-1399). Also available at: http://bigladdersoftware.com/epx/docs/8-0/engineering-reference/page-122.html Mahabir ��……��������……………��������………………������� �…………��������……………��������………………������� �…………������.. Mahabir Bhandari, Ph.D.|Oak Ridge National Laboratory| office:865-574-0989 | cell:865-356-0140 From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of jeannieboef@xxxxxxxxx I wish I could think as clearly and bring it so concisely to paper. Great answer. I'm going to rample my less concise thoughts a further step. The use of the componant loads report was to get an idea where the "weak spots" were, so that you could think about "strengthening those componants. Perhaps some were too good, and you could apply those construction costs better elsewhere. So how can you do the same analysis in e+? There exists a new report called Sensible Heat Gain and Sensible Heat Gain at Peak Heating (or similar...I'm not sure of the exact name). So basically you can see in this report where energy flows in and out of a zone. Not by componant, but by type, e.g. Infiltration gain, infiltration loss, hvac air gain/loss, active radiative surface gain/loss, solar gain/loss...basically the whole zone energy balance including through zone total componants. It's not the same, but it is a good start to understanding the energy flows in relation of magnitudes (more wall insulation is not helping much when you have an 80% WWR, just decrease the WWR by 5% for double the effect of increased insulation). As Joe suggested, the zone loads calcs with purchased air is also a good tool. If you have the zone loads and the rated U-Values and areas of the zone's componants, you could back calculate the componant loads at the rated U-value rated conditions as they include the airfilm resistance based on appropriate convection coefficients, right? It's too early to think this hard! Jean
Aucun virus trouvé dans ce message. __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |