[EnergyPlus_Support] Re: Heating Coil and Cooling Coil are running simultaneously!?!?



Thank you very much for this reply,
I have been using: 
1. HVACTemplate:System:VAV object to adjust setpoints, for heating setpoint was put to 24[C] and cooling setpoint was put to 18[C],
 
2. HVACtemplate:Zone:VAV objects use 11[C] Temp. difference adjusted for both zone heating and zone cooling.
 
3. Thermostat setpoints are 20[C] for heating and 22[C] for cooling.

Please advise.

Hisham


--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "jeannieboef@..." <jeannieboef@...> wrote:
>
> You place a setpoint usually on the outlet node of the AHU. Depending  
> on which setpointmanager you use to place the setpoint, the setpoint  
> could dynamically change to best meet the load in the zone. Often both  
> coils look at this same setpoint together with their relative entering  
> air temperatures: based on this information each independant coil  
> controller will actuate to best try and achieve the air setpoint that  
> you placed on the AHU outlet (which may change dynamically the value  
> to achieve).
> 
> Therefore if the setpoint the AHU outlet (at a timestep) was 13 deg C  
> (because the zone needed cooling, because some equipment has turned  
> on), the heating coil entering air temperature was 10 deg C from cold  
> outside air, and the cooling coil entering air is 16 deg C (for any  
> number of reasons), then both coils will operate.
> 
> Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity)
> 
> i. A.
> Jean Marais
> b.i.g. bechtold
> Tel.   +49 30 6706662-23
> 
> On 18.12.2013, at 11:16, "hisham.rashrash" <hisham.rashrash@...>  
> wrote:
> 
> > Dear all,
> > Regarding this warning 'In HVACTemplate:System:VAV "VAV" the Heating  
> > Coil Design Setpoint is greater than the Cooling Coil Design  
> > Setpoint. This may cause the heating coil and cooling coil to  
> > operate simultaneously. Check results carefully and adjust controls  
> > if needed.'
> >
> > Please, can anyone explain how this HVACTemplate:System:VAV works? I  
> > feel lost in questions, like:
> > Should heating and cooling coils run independently of each others  
> > and only depend on thermal zones thermostats? Then, what if two  
> > thermostats provided contradicting signals: a request for heating  
> > and another for cooling?
> > And in case there are no contradicting signals, why there is a  
> > possibility both coils are running together when heating coil  
> > setpoint is higher than cooling coil setpoint? Is there some  
> > 'invisible' thermostat E+ object between these two coils?
> >
> > Maybe my questions are too basic, but I really need help here.
> >
> > Thank you very much.
> >
> > Hisham
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "hisham.rashrash"  
> > <hisham.rashrash@> wrote:
> > >
> > > Dear all,
> > >
> > > I got this warning:
> > >
> > > Program Version,EnergyPlus-Windows-64 8.1.0.008, YMD=2013.12.17  
> > 17:18,IDD_Version 8.1.0.008
> > > ** Warning ** Output:PreprocessorMessage="ExpandObjects" has the  
> > following Warning conditions:
> > > ** ~~~ ** Warning: In HVACTemplate:System:VAV "VAV" the Heating  
> > Coil Design Setpoint
> > > ** ~~~ ** is greater than the Cooling Coil Design Setpoint. This  
> > may cause the
> > > ** ~~~ ** heating coil and cooling coil to operate simultaneously.  
> > Check results
> > > ** ~~~ ** carefully and adjust controls if needed.
> > >
> > > It seems like EnergyPlus puts a thermostat between coils? why  
> > should they run at the same time?
> > >
> > > Please advise.
> > >
> >
> >
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo Groups is subject to:
    http://info.yahoo.com/legal/us/yahoo/utos/terms/